Originally Posted By: psmothers
This post was automatically imported from our archived forum.



This is a picture of a townhouse attic fire wall. The home was built in 1984. In the attic both firewalls ran all the way to the inside of the roof line and the rock was stamped fire rated. None of the joints were taped and floated. Was this execptable when this house was build? I know that today this would have to be taped and floated.


![](upload://pLjZuiYTQ3n74ExGhM2MM0UUDZ7.jpeg)


--
Foxe Smothers

"Its not a matter of will we rebuilt it is matter of how soon..."

"A hero is no braver than an ordinary man, but he is brave five minutes longer."
- Ralph Waldo Emerson

Originally Posted By: jhagarty
This post was automatically imported from our archived forum.



Peter:


I don't know if this is true in your particular scenario.

I have found municipalites that required a double 5/8" Fire Rock on each side of the wall. Joints are overlapped and not taped.


--
Joseph Hagarty

HouseMaster / Main Line, PA
joseph.hagarty@housemaster.com
www.householdinspector.com

Phone: 610-399-9864
Fax : 610-399-9865

HouseMaster. Home inspections. Done right.

Originally Posted By: psmothers
This post was automatically imported from our archived forum.



Ahhh! Good call. I saw a spot that I could not get within 4 feet of that I swore I could see another layer through.



Foxe Smothers


"Its not a matter of will we rebuilt it is matter of how soon..."

"A hero is no braver than an ordinary man, but he is brave five minutes longer."
- Ralph Waldo Emerson

Originally Posted By: mboyett
This post was automatically imported from our archived forum.



I had a similar situation a month or so ago. Our local fire marshal’s office indicated the drywall did not need to be taped/floated as long as the gaps were less than 1/16". He said nothing about double layers. So, that’s just my AHJ opinion.



Mike Boyett


Capital City Inspections


Austin, Tx


www.capcityinspections.com

Originally Posted By: Jay Moge
This post was automatically imported from our archived forum.



o.k michael. i’m having a brain fart. eusa_doh.gif what is AHJ?


Originally Posted By: lkage
This post was automatically imported from our archived forum.



Jay Moge wrote:
o.k michael. i'm having a brain fart. ![eusa_doh.gif](upload://has2a0g32D0AAlDjAwVcrg3HnhX.gif) what is AHJ?


Authority having jurisdiction.


--
"I have never met a man so ignorant that I couldn't learn something from him."
Galileo Galilei

Originally Posted By: Jay Moge
This post was automatically imported from our archived forum.



ooohhh yeah. thanx. icon_cool.gif


Originally Posted By: mcyr
This post was automatically imported from our archived forum.



icon_smile.gif icon_smile.gif


Most typically, 5/8" drywall up in the attic is installed to provide a smoke barrier when the area in square feet exceeds 2700 s.f., and/or to provide a fire barrier between the garage and the house.
In either case the joints should be taped over to provide the smoke barrier and/or fire rating that is necessary to meet local codes.

Marcel