Any limit to the number of splices inside a sevice?

Originally Posted By: kshepard
This post was automatically imported from our archived forum.



A number of defects here including wires abandoned outside the box, spliced ground, stranded aluminum wires from connection for backup generator (reason for the splices), and about 30 splices. Splices look hokey but are they defects? -Kent





Originally Posted By: jwilliams4
This post was automatically imported from our archived forum.



312.8 Enclosures for Switches or Over-current Devices.


Enclosures for switches or over-current devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other over-current devices, unless adequate space for this purpose is provided.


The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.


Originally Posted By: jhagarty
This post was automatically imported from our archived forum.



Federal Pacific Stab-Lok Panel


Recommend replacement.


Originally Posted By: kshepard
This post was automatically imported from our archived forum.



Thanks Jae. -Kent


Originally Posted By: dfackler
This post was automatically imported from our archived forum.



My two Certified Electricians and Joe from Square One all say abanded wiring is not allowed by the NEC. In a bow or in the attic/crawl space.


Am I miss-understanding this?
Zoe


Originally Posted By: jhagarty
This post was automatically imported from our archived forum.



jhagarty wrote:
Federal Pacific Stab-Lok Panel

Recommend replacement.


This should give you enough links...

http://www.inspect-ny.com/fpe/fpepanel.htm


Originally Posted By: pabernathy
This post was automatically imported from our archived forum.



Dennis,


Your electricians are partly right....

Art. 725, 760, 770, 800, 820, and 830. Abandoned cables are defined as cables that are not terminated at equipment and not identified for future use with tag. The removal requirement is not exactly the same in every article but is similar to, "the accessible portion of abandoned cables shall not be permitted to remain."

But these more or less pertain to cable and TV and low voltage installations and not really for 120/240V ( nominal ) installations.

While it is best to always remove unused wires, atleast disconnected from both ends and capped off is the best choice, never cap a live wire in an area and leave it......always try to remove the power from the circuit to be abandonded. Also all wires should terminate in a junction box of some sort anyway...

However I would look for a change down the way in 2008 regarding abandoned electrical lines....but unless their is something I am not aware of ( which is possible ) I do not believe the 2002 NEC addresses this other than in articles listed above for low voltage and data communication wiring.


--
Paul W. Abernathy- NACHI Certified
Electrical Service Specialists
Licensed Master Electrician
Electrical Contractor
President of NACHI Central Virginia Chapter
NEC Instructor
Moderator @ Doityourself.com
Visit our website- www.electrical-ess.com

Originally Posted By: mcyr
This post was automatically imported from our archived forum.



icon_smile.gif icon_smile.gif


Hi. Jae;

While I read these posts. and abviously these wire nut splices are overboard in by book for no known code, and only because it doesn't look right.
What is it you said in laymens' terms? I am not quite familiar with the codes of the NEC on this one, other than the fact I would have strongly recommended an Licensed Electrical Contractor to look at.

Thanks in advance.

Marcel


Originally Posted By: bbadger
This post was automatically imported from our archived forum.



As far as the NEC is concerned you can fill any cross section of the panel up to 75% with splices.


This effectively means you will never see a panel with more splices than allowed by the NEC.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: kshepard
This post was automatically imported from our archived forum.



The wires you see spliced in the service panel are not abandoned, they are part of the method used to connect wires from the backup generator system. The abondoned wires don’t even enter the box and are barely visible at the top.


Does anyone really calculate 75% of the box? How would you do that? Sounds like a stand back and squint thing.


My first recommendation was to replace the Federal Pacific panel.


Second was have a qualified electrician do the work, correct abandoned wires and evaluate generator connections.


Kent


Originally Posted By: jwilliams4
This post was automatically imported from our archived forum.



Hey, Marcel–waddup?


In laymens terms it's O.K. to have splices (properly done) in the

panel box--just don't overdo it. If it looks like too many splices,

it is probably true. Recommend electrician.

![icon_biggrin.gif](upload://iKNGSw3qcRIEmXySa8gItY6Gczg.gif) ![icon_biggrin.gif](upload://iKNGSw3qcRIEmXySa8gItY6Gczg.gif)


Originally Posted By: jwilliams4
This post was automatically imported from our archived forum.



Good heavens!! Why am I posting in “ELECTRICAL” when


Bob B. and Paul A. are watching over us??? ![icon_eek.gif](upload://yuxgmvDDEGIQPAyP9sRnK0D0CCY.gif) ![icon_eek.gif](upload://yuxgmvDDEGIQPAyP9sRnK0D0CCY.gif) ![icon_eek.gif](upload://yuxgmvDDEGIQPAyP9sRnK0D0CCY.gif)




Originally Posted By: kshepard
This post was automatically imported from our archived forum.



I’ll tell you why Jae,


Nobody's rung the bell yet.

There was only one overcurrent device, so your first post didn't answer the question. The next several were off-subject...

Maybe the fault is mine for not asking the question clearly...

1. Is there a limit to the number of splices that are allowed within a main service panel and is there an NEC number that addresses this limit?

2. In connecting a backup generator electical system to the home is it ever permissable for electrical connections to be made using stranded aluminum cable?

Kent


Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



Quote:
1. Is there a limit to the number of splices that are allowed within a main service panel and is there an NEC number that addresses this limit?


There is nothing about splices in a panel at all. The 75% Bob referred to is really just talking about extra wires passing through the cabinet. You don't have a fill deduction for a splice.

Quote:
2. In connecting a backup generator electical system to the home is it ever permissable for electrical connections to be made using stranded aluminum cable?


By "stranded aluminum" I assume you mean larger than #10. I am not sure that was ever a concern.


Originally Posted By: jwilliams4
This post was automatically imported from our archived forum.





O.K. breakers/fuses are in the service panel...

Question? Is there a limit to splices in a service panel?

NEC 312.8 Sure, if there's room. Don't over fill the area.

![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif) ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif) ![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



You folks are still ignoring the words “for conductors feeding through or tapping off to other over-current devices”.


If these splices are in conductors serving the O/C devices in the panel in question they are not addressed at all in 312.8.


1 Like