Change requires an equipotential bonding grid be installed to reduce voltage gradients in and around permanently installed pools, outdoor spas, and outdoor hot tubs.
INDENT Bonded Parts. The following parts of a permanently installed pool, outdoor spa, and outdoor hot tub must be bonded to a equipotential bonding grid of the type specified in 680.26©.
Author’s Comment: See 680.42(B) for the bonding methods permitted for outdoor spas and hot tubs.
(1) Metallic Parts of Structure. All metallic parts of the water structure, including the reinforcing metal of the permanently installed pool, outdoor spa, and outdoor hot tub shell and deck, must be bonded to the equipotential grid. The usual steel tie wires are considered suitable for bonding the reinforcing steel together for this purpose. Welding or special clamping is not required, but the tie wires must be made tight. Figure 680-4
Where the reinforcing steel of the permanently installed pool, outdoor spa, and outdoor hot tub shell and deck are encapsulated with a nonconductive compound or if it’s not available, an equipotential grid constructed in accordance with 680.26© must be installed to mask stray voltage gradients.
(2) Underwater Lighting. All metal forming shells for underwater permanently installed pool, outdoor spa, and outdoor hot tub luminaires and speakers.
(3) Metal Fittings. Metal fittings within or attached to the permanently installed pool, outdoor spa, and outdoor hot tub structure, such as ladders and handrails.
(4) Electrical Equipment. Metal parts of electrical equipment associated with the permanently installed pool, outdoor spa, and outdoor hot tub water circulating system, such as water heaters and pump motors. Accessible metal parts of listed equipment incorporating a system of double insulation and providing a means for grounding internal metal parts are not required to be directly bonded to the equipotential grid.
(5) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways, metal piping, and all fixed metal parts, as well as metallic surfaces of electrical equipment, must be bonded to the equipotential grid if located:
(1) Within 5 ft horizontally of the inside walls of the permanently installed pool, outdoor spa, and outdoor hot tub, and
(2) Within 12 ft measured vertically above the maximum water level of the permanently installed pool, outdoor spa, and outdoor hot tub, or any observation stands, towers, or platforms or any diving structures.
[/INDENT]
http://www.mikeholt.com/onlinetraining/page_images/6_63_169_7_2.gif
(A) Receptacles
(5) GFCI Protection. All 125V receptacles located within 20 ft. of the inside walls of a pool or fountain must be protected by a ground-fault circuit interrupter. Receptacles supplying pool pump motors rated 15 or 20A, single-phase, 120V through 240V must be provided with GFCI protection. Figure 680-5
Intent: The revised text is intended to clarify that GFCI protection is required for all 15 or 20A, 120V through 240V,240V circuits that supply single-phase receptacles for pool pump motors.
Courtest of Mike Holt Enterprises- Can you tell I am a huge fan of Mr. Holt…