Default Unusual Sub-Panel Wiring

Gents,

I saw an unusual method of wiring a sub-panel yesterday. The feed from the main panel is wired to the terminals of the 50 amp breaker in the sub-panel and not the normal Bus terminal lugs.

I assume that this is an attempt to create a "main" in a panel that does not have a main breaker attachment. The circuit is also protected by a 50 amp breaker in the Main Panel.

Is this acceptable?

Note: I am reporting the open knockouts.
Attached Images
File Type: jpg IMG7.JPG (36.9 KB, 135 views)
Reply With Quote
  #2  
Old 1/5/06, 10:16 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: Unusual Sub-Panel Wiring

The panel is being "back-fed" through the breaker. Not uncommon. . .



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #3  
Old 1/5/06, 10:42 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 412
brian winkle has had a little positive feedback
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unusual Sub-Panel Wiring

The backfed breaker should be fastened in place. 384-16 (g)
Reply With Quote
  #4  
Old 1/5/06, 10:47 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
jtedesco1 is considered disreputable jtedesco1 is considered disreputable jtedesco1 is considered disreputable
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Unusual Sub-Panel Wiring

In addition:

Markings on panelboards that employ plug-on units require the use of a hold-down kit when the units are back-fed and the field installed supply conductors are terminated on the plug-on unit. The marking indicates: “Back-fed _____ requires hold-down kit Cat. No._____ “ or the equivalent.

An identification of the applicable back-fed unit is specified in the first
blank-for example, circuit breaker, fused switch, or terminal kit; and the catalog number of the required hold-down kit is specified in the second blank.






Reference: UL Panelboard Marking Guide and Industry Standards




Back-Fed Devices



Plug-in-type overcurrent protection devices or plug-in type main lug assemblies that are back-fed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.



I don't see this "kit" in the picture?

This rule has been in the industry standards for at least 10 years, because of an electrocution..
Reply With Quote
  #5  
Old 1/5/06, 8:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,933
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unusual Sub-Panel Wiring

Ok...Timothy...I am going to ask one question here not related to what has been posted.

Q: What size was the conductor that FED the panel shown here?

I will tell you why when you reply....Now i know what should be installed for the 50A breaker...and we all know the conductor can be larger...I just would like to know what size the wire was to this panel.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #6  
Old 1/5/06, 9:10 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 841
Jason A. Sieg, CMI .
Default Re: Unusual Sub-Panel Wiring

Paul, you realy have me wondering what your going to say. I'm posting to track this thread in my email.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #7  
Old 1/5/06, 9:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,933
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unusual Sub-Panel Wiring

lol.....well it really depends on what Timothy tells me here...lol

Besides.....I may have nothing as pictures are sometimes not great for thinking you see things....so I just want to know for piece of mind but I will wait for Timothy to let me know.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.

Last edited by pabernathy; 1/5/06 at 10:00 PM.
Reply With Quote
  #8  
Old 1/6/06, 2:58 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 261
Timothy J. Gardner is generally well trusted
Default Re: Unusual Sub-Panel Wiring

Paul,

#6 copper THHN in plastic? (at least going in the ground and out of the ground) conduit buried - 4 leads - 50' from the main Panel.

The panel is mounted in a storage shed on a dock.

tg
Reply With Quote
  #9  
Old 1/6/06, 3:03 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,933
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unusual Sub-Panel Wiring

Thanks Timothy......Next Question...

Is that GREEN TAPE wrapped around the Ground Wire?



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #10  
Old 1/6/06, 3:16 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 261
Timothy J. Gardner is generally well trusted
Default Re: Unusual Sub-Panel Wiring

Paul,

No, it is pvc insulation.

tg
Reply With Quote
  #11  
Old 1/6/06, 3:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,933
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Unusual Sub-Panel Wiring

Cool........thats why I did not want to post anything and wanted to ask the question because pictures sometimes dont tell the story...with the BRIGHT color of that cable....I have only seen it that bright when it was wrapped with Green Tape......which in the NEC would not be allowed on 6AWG and smaller cables....The risk of that is someone later can come along later and remove the tape and screw something up.

Anyway......I have learned...asking the questions is better than just posting since I could not zoom in on the picture....looked like tape sticking up on the end about 1 inch before it goes into the terminal block.

Anyway.......Just wanted to check....



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
  #12  
Old 1/6/06, 3:37 PM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 261
Timothy J. Gardner is generally well trusted
Default Re: Unusual Sub-Panel Wiring

Thanks for the info. Joe & Brian, I KNEW that something didn't look right. Thanks for the reminder.

Around here, a back-fed breaker is usually a DIY emergency generator connection point.

Thanks again, TG
Reply With Quote
  #13  
Old 1/10/06, 2:05 AM
Joseph B. Kormos's Avatar
Joseph B. Kormos Joseph B. Kormos is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Medinah, IL
Posts: 640
Joseph B. Kormos .
Default Re: Unusual Sub-Panel Wiring

It also looks as if a knock out is missing from the top of the box, and the copper pipe should also be capped just in case it is just attached to a shut off valve, and if the valve leaks...

Joe
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 4:10 PM
Sub Panel Wiring tmartens Electrical 4 2/27/07 11:56 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:46 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics