Default "Allowable" Gas Leakage

I routinely use a TIF 8800 combustible gas detector to check for leaks in gas supply lines and some appliance components. On a recent inspection I reported that the natural gas-fueled water heater's thermostat valve had a leak. I could smell it, and verified that it was there (multiple times) with my gas detector. So, they had a heating and cooling guy come out and he confirmed that it was leaking, but that it was leaking at an "Allowable" rate. My client forwaded me some documents (see attached) he was provided relating to this, and sure enough, Rheem and Ruud say the allowable rate for leakage is 200 cubic cm of natural gas per hour. I hate crying "wolf" at inspections, so the question arises, how to discern 175 cu. cm./hr vs. 250?

As an aside, other documents I found on the web state that there is NO allowable leakage for LP gas.
Attached Thumbnails
allowable-gas-leakage-waterheaterinfo.jpg  
Reply With Quote
  #2  
Old 9/18/06, 6:26 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: "Allowable" Gas Leakage

I normally don't pull out my TIFF 8800 unless my nose smells something. Then I try to locate it. But if there is a leak, enough for my nose, I report it and let the gas tech deal with it.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 9/18/06, 7:05 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: "Allowable" Gas Leakage

How was the gas tech able to measure the "leak of an allowable rate"?

Something certainly smells here.
Reply With Quote
  #4  
Old 9/18/06, 7:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: "Allowable" Gas Leakage

That's reasonable because natural gas will dissipate and not become a flash or explosion hazard if adequate ventilation is provided. However, it is far beyond us to try and determine the "volume" of the leakage, therefore, all leaks should be reported and deferred accordingly.

As for LP, this gas is heavier than air, and as such, will pool or pond in low areas, thus becoming a flash or explosion hazard.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 9/18/06, 7:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: "Allowable" Gas Leakage

Well said Jeff. Measurements of this accuracy are well beyond the scope of work for a home inspection.
Reply With Quote
  #6  
Old 9/18/06, 7:23 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: "Allowable" Gas Leakage

Jeff is corrected in the LPG leaks pooling due to heavier than air. I use LPG more so than not in temporary heating during the Winter months and if you can sniff it, you better take care of it quick and I mean no delays. On a construction site this would be extremely hazardous.

Marcel
</IMG></IMG>
Reply With Quote
  #7  
Old 9/18/06, 7:31 PM
sspradling sspradling is offline
Active Poster
 
Join Date: Jan 2004
Location: Columbia, MO
Posts: 227
Please Note: sspradling is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: "Allowable" Gas Leakage

Jim,
You made the right call. Keep doing what you're doing. A gas leak is a bad thing. They don't heal themselves. You pointed it out, recommended a repair by a qualified contractor, and they had someone come out and check it. Now the qualified contractor, an "expert in that field", has looked at it and signed off on it. You did your job.
Stu
Reply With Quote
  #8  
Old 9/18/06, 8:06 PM
John J. Passailaigue, Jr.'s Avatar
John J. Passailaigue, Jr. John J. Passailaigue, Jr. is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Auburn, AL
Posts: 402
Send a message via AIM to jpassailaigue
Default Re: "Allowable" Gas Leakage

Jim,
Had the same thing happen to me my first year of doing inspections. The local gas company came to the home and stated that the gas leak was allowable an in tolerance of the local building code. The home owner called me and asked if I would pay the $55.00 service call and I did with no hesitation. I got four referrals from this past client. He was happy, I was happy, and apparently the gas water heater was happy. i think you did your job and have done it very well. Keep up the good work.



John J. Passailaigue Jr.
NACHI05062580
Auburn Home Inspection
Auburn, Alabama
WAR EAGLE!
Reply With Quote
  #9  
Old 9/18/06, 9:21 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,899
Default Re: "Allowable" Gas Leakage

I happened to be driving past a motel when it exploded, I didn't know what the hell happened, all I saw was pink insulation flying in the air like a blizzard, two people were killed and the cause, LP leak, obviously substantial, explosion touched of by one of the victims when they came back to their room and turned the light switch on.
Reply With Quote
  #10  
Old 9/18/06, 9:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: "Allowable" Gas Leakage

That's why there is no tolerance for LPG leaks. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 9/18/06, 9:53 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,850
Default Re: "Allowable" Gas Leakage

Everything leaks kids. Even LPG piping and valves. Now you may not be able to detect any leaks using soapy water, pressure decay testing, or thermal conductivity meters on an LPG system, but that is far different from saying it does not leak. There were no detectable leaks might be a more accurate description.
</IMG></IMG>
Reply With Quote
  #12  
Old 9/19/06, 2:30 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: "Allowable" Gas Leakage

One of the FAQs on the SDG&E site used to say something similar to this:

Q: How do I know if I have a gas leak and where it is?
A: If you can smell it, you have a gas leak. Don't worry about where it is. Turn the gas off at the gas meter and call us immediately at xxx-xxx-xxxx. Don't light anything like cigarettes or candles. Turn all lights and appliances off and don't turn anything on. Open all windows.

I think their words of warning were more extensive than what I wrote right there, but the gist of the message was, "Call us immediately."

That was good enough for me.



NACHI 2005 U.S. Member of the Year

Last edited by rray; 9/19/06 at 4:28 AM..
Reply With Quote
  #13  
Old 9/19/06, 4:09 AM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,093
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: "Allowable" Gas Leakage

We're fortunate here in California, most public utility gas service companies will respond to gas leaks for no service charge to the owner.
Reply With Quote
  #14  
Old 9/19/06, 5:44 AM
rmoore5's Avatar
rmoore5 rmoore5 is offline
Active Poster
 
Join Date: Oct 2005
Location: Powder Springs, GA
Posts: 106
Please Note: rmoore5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: "Allowable" Gas Leakage

I also use the tif 8800, its a great tool........i use it on all inspections where gas is being used in the home.........If it sniffs any gas i put in the report....
and recommend a professional to come out and look at it.... I have not had any complaints....most clients say thank you, but if it came down to saftey, and i was wrong... i will pay the tech to come out and check it. Last thing i would want is a new home owner, moving in and his house blows up.... if that happens who do you think they will blame. ........

Just my $ .02
maybe this helps...

Thanks RM
www.prohomechek.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Article on Commercial and Residential Inspections and Assessment mcyr Commercial Inspections 2 8/6/07 2:26 AM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 3 1/22/07 11:24 AM


All times are GMT -4. The time now is 9:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts