Default Any rough framers have a 2009 IRC? I have a question.

My question has to do with figure R602.3(2) on page 152.

Don't the ends of the window sill need jack studs under them (not just along side them)?



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 5/24/11 at 11:50 PM..
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/25/11, 12:19 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,905
Default Re: Any rough framers have a 2009 IRC? I have a question.

any-rough-framers-have-2009-international-residential-code-have-question-jack-stud-under-sill..jpg
Just so we can all follow.
Reply With Quote
  #3  
Old 5/25/11, 12:20 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: Any rough framers have a 2009 IRC? I have a question.

That's not figure R602.3(2).



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #4  
Old 5/25/11, 12:31 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: Any rough framers have a 2009 IRC? I have a question.

Here is figure R602.3(2) from the 2009 IRC. See anything wrong with their drawing?
Attached Thumbnails
any-rough-framers-have-2009-international-residential-code-have-question-wallframingsection.jpg  



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #5  
Old 5/25/11, 12:32 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Any rough framers have a 2009 IRC? I have a question.

Nope. The jack studs are for the load bearing header, not for the window frame out.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #6  
Old 5/25/11, 12:33 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: Any rough framers have a 2009 IRC? I have a question.

Doesn't the window sill need jack studs like Bob's image depicts?



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #7  
Old 5/25/11, 12:35 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Any rough framers have a 2009 IRC? I have a question.

Personally I would not call it out. The sill is non load bearing. Just there to frame out the window. In Bobs picture, they are using those as a jack stud all the way through the sill to the header.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #8  
Old 5/25/11, 12:46 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: Any rough framers have a 2009 IRC? I have a question.

Nails only hold wood together, they are not meant to be used to carry a load (even if the load is only a window) like the horizontal nails holding up the ends of the window sill are doing in the IRC's figure R602.3(2).
Attached Thumbnails
any-rough-framers-have-2009-international-residential-code-have-question-wallframingsection.jpg  



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 5/25/11 at 12:49 AM..
Reply With Quote
  #9  
Old 5/25/11, 12:49 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Any rough framers have a 2009 IRC? I have a question.

I know the diagram you speak of Nick.. it shows the sill to be what would appear toe-nailed to the jack with cripples under it. The only thing that I would say is correct in *that* diagram is that the Jack is not intersected. I'm in CA, and haven't ever nailed at least one full trimmer or jack stud under a beam.. period, and tightly to boot.

I have however seen many times in practice where the sill is simply face nailed to a cripple below it that is *nailed directly to the jack*, meaning no sandwich as in Bob's illustration.

There are requirements for openings over 60" and having double trimmers and a single king.. but again, at least one full length jack/trimmer under the beam. When we used a second Jack as shown in Bob's diagram, and sandwich a sill between the pieced Jack, we'd call it a sub-sill and nail another sill on top of it. Lotta wood, eh?

I think the Sill and Sub Sill methods tie into the trades of years past as the top Sill would be SLOPED... remember the 2 x 6 and 8 sloped sill window opening's?



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #10  
Old 5/25/11, 12:51 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: Any rough framers have a 2009 IRC? I have a question.

Interesting take on it. Thanks.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #11  
Old 5/25/11, 12:53 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Any rough framers have a 2009 IRC? I have a question.

And just as I replied.. there's that illustration..

I'd agree that it's correct in CODE, but incorrect in practice. The only time that I would see a sill framed like the one pictured, is right before I nailed a piece of framing next to each jack and under the sill. IMO, it's more incomplete than incorrect.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #12  
Old 5/25/11, 1:05 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: Any rough framers have a 2009 IRC? I have a question.

One of the reasons I noticed it was because the dead load of a wall is calculated by including the additional load of any windows (about 8psf) which would mean the horizontal nails holding up the ends of the sill plate are carrying some load, albeit not very much.

Thanks for your insight.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #13  
Old 5/25/11, 1:55 PM
Jim Hime Jim Hime is offline
InterNACHI Member
 
Join Date: Feb 2008
Location: Dickinson, Tx
Posts: 103
Default Re: Any rough framers have a 2009 IRC? I have a question.

The IRC R301.2.1.1 Design Criteria via the American Forest and Paper Association (AF&PA) - Wood Frame Construction Manual for One-Two Family Dwellings (WFCM) also shows wall framing without a jack stud at the sill ends.

The perimeter of a window is fastened to the framed opening. In my area we add the jack studs as common practice and habit. A wall is built on the foundation and then stood up. The extra jack stud generally aids in keeping the window opening from torquing from the frame (depending on the amount of labor onsite). The lack of the jack studs at the sill ends has no real value to the load-bearing of the wall. The lack of these jack studs can increase wall insulation and decreases thermal bridging. (Green Building)
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/25/11, 9:48 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any rough framers have a 2009 IRC? I have a question.

[quote=jhime;786811]The IRC R301.2.1.1 Design Criteria via the American Forest and Paper Association (AF&PA) - Wood Frame Construction Manual for One-Two Family Dwellings (WFCM) also shows wall framing without a jack stud at the sill ends.

The perimeter of a window is fastened to the framed opening. In my area we add the jack studs as common practice and habit. A wall is built on the foundation and then stood up. The extra jack stud generally aids in keeping the window opening from torquing from the frame (depending on the amount of labor onsite). The lack of the jack studs at the sill ends has no real value to the load-bearing of the wall. The lack of these jack studs can increase wall insulation and decreases thermal bridging. (Green Building)[/quote]

Optimum Value Engineered (OVE) framing saves labour/materials up front and allows for more efficient walls with less low R-value framing and more lower cost but better R-value insulation; the average overall R value of the wall goes up. The OVE concept has been around for 25-30 years now.
Reply With Quote
  #15  
Old 5/26/11, 12:49 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: Any rough framers have a 2009 IRC? I have a question.

Quote:
In my area we add the jack studs as common practice and habit.
Same here in my area.

Many windows require that you install shims between the bottom of the window and the ends of the sill, which would mean shimming against a framing member that is nothing but end nailed if the jacks studs were missing.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Next Energy Audit Class - May 15, 2009 jmckenna1 Thermal Imaging, Infrared Cameras & Energy Audits 3 5/12/09 1:47 PM
Law and Disorder - DALLAS, TX - January 28, 2009 jferry1 Inspection Education & Training 0 1/19/09 4:14 PM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 3:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts