  #16  
Old 5/29/11, 9:59 AM
Andrew Rowland Andrew Rowland is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Lexington, Ohio
Posts: 4
Default Re: Any rough framers have a 2009 IRC? I have a question.

I always frame my windows, no matter how large or small, with cripples under the ends. I checked with an inspector from the local building department to get his take. In our area (north central Ohio) they will allow no cripples at the ends on windows up to 5' wide. Anything larger they want cripples.
I just installed some Pella windows (casement) about 4.5' wide and maybe 4' high which weighed somewhere around 150lbs. Yes, there were some cripples under the center portion of the window sill, but shims were placed on each end and in the center, shifting all that weight onto three small piles of shims, two of which where on either side.
I agree with most others here - it may not be against code, but I would think it shows which builders care and pay more attention to detail. Minimum code is only a minimum. And it usually isn't good enough.
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 5/29/11, 11:11 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: Any rough framers have a 2009 IRC? I have a question.

Thank you for helping. Good post.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #18  
Old 5/29/11, 4:22 PM
Joseph W. Keresztury's Avatar
Joseph W. Keresztury Joseph W. Keresztury is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: San Antonio, Texas
Posts: 356
Default Re: Any rough framers have a 2009 IRC? I have a question.

Here's a photo from one of my recent frame inspections in the San Antonio (south Texas) area on a large national production builders home. Volume builders of course cut back on certain things for cost effectiveness, but you can see here they have the jack studs installed below window. I would write it up if they weren't installed, but never have to, at least not til this point. As far as I'm concerned they are required.
Someone made a good point on this thread, but I don't see the post anymore. They felt that it's not that the image- figure R602.3(2) is incorrect but that's it's incomplete. The reason I agree w/ that opinion is because I remembered the Rafter construction image in the 2006 IRC. We use 2006 here. In figure R802.5.1 (pg.267) The roof frame image shows ridge, rafters, joists, purlins and it's bracing but no collar ties which of course are required every other rafter (max. 4' spacing) connecting rafters under ridge. So this image I'm referring to is also incomplete. I can't get my new laptop scanning yet so I can't post that image of roof frame in IRC that I'm referring to.
Attached Thumbnails
any-rough-framers-have-2009-international-residential-code-have-question-ivan-t-frame-pics-052.jpg  



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com

Last edited by jkeresztury; 5/29/11 at 4:26 PM..
Reply With Quote
  #19  
Old 5/29/11, 7:46 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any rough framers have a 2009 IRC? I have a question.

Quote:
Originally Posted by jkeresztury View Post
Here's a photo from one of my recent frame inspections in the San Antonio (south Texas) area on a large national production builders home. Volume builders of course cut back on certain things for cost effectiveness, but you can see here they have the jack studs installed below window. I would write it up if they weren't installed, but never have to, at least not til this point. As far as I'm concerned they are required.
Someone made a good point on this thread, but I don't see the post anymore. They felt that it's not that the image- figure R602.3(2) is incorrect but that's it's incomplete. The reason I agree w/ that opinion is because I remembered the Rafter construction image in the 2006 IRC. We use 2006 here. In figure R802.5.1 (pg.267) The roof frame image shows ridge, rafters, joists, purlins and it's bracing but no collar ties which of course are required every other rafter (max. 4' spacing) connecting rafters under ridge. So this image I'm referring to is also incomplete. I can't get my new laptop scanning yet so I can't post that image of roof frame in IRC that I'm referring to.
There are metal framing brackets available to support plate ends such as in OVE framing.
Reply With Quote
  #20  
Old 6/7/11, 12:25 AM
Joseph W. Keresztury's Avatar
Joseph W. Keresztury Joseph W. Keresztury is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: San Antonio, Texas
Posts: 356
Default Re: Any rough framers have a 2009 IRC? I have a question.

Quote:
Originally Posted by Brian A. MacNeish View Post
There are metal framing brackets available to support plate ends such as in OVE framing.
There's also brackets available to support headers in lieu of jack studs
under the headers in OVE framing, etc. Brian, do you have pics of these techniques applied from all your framing inspections or did you see this on HGTV and thought it was cool along w/ futuristic. I'm curious to see if anyone has actual pics of this or, what?
OVE framing to the full extent or close to it does no exist in my area.



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com
Reply With Quote
  #21  
Old 6/7/11, 8:16 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any rough framers have a 2009 IRC? I have a question.

Quote:
Originally Posted by jkeresztury View Post
There's also brackets available to support headers in lieu of jack studs
under the headers in OVE framing, etc. Brian, do you have pics of these techniques applied from all your framing inspections or did you see this on HGTV and thought it was cool along w/ futuristic. I'm curious to see if anyone has actual pics of this or, what?
OVE framing to the full extent or close to it does no exist in my area.
Go to www.buildingscience.com and do a search for "OVE". 4-5 documents come up including one about a project in Dallas.

OVE has been in the books/periodicals for 25-30+ years but rarely gets applied......builders are a very conservative bunch!!

Last edited by Brian A. MacNeish; 6/7/11 at 6:05 PM..
Reply With Quote
  #22  
Old 6/7/11, 10:49 AM
Vern Mitchinson's Avatar
Vern Mitchinson Vern Mitchinson is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Edmonton, AB
Posts: 2,087
Default Re: Any rough framers have a 2009 IRC? I have a question.

I checked an old book "Practical house carpentry" printed 1965 and I was surprised to find that it did not show cripple studs under the ends of the sill. The older wood windows were shimmed under the jambs and this put the entire weight of the window on the ends of the sill. Go figure.
Cutting the jack stud to embed the sill is a code violation.



Vern Mitchinson_CCHI_CMI
Registar
AlbertaNACHI
International Association of Certified Home Inspectors of Canada
Reply With Quote
  #23  
Old 6/7/11, 8:20 PM
Joseph W. Keresztury's Avatar
Joseph W. Keresztury Joseph W. Keresztury is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: San Antonio, Texas
Posts: 356
Default Re: Any rough framers have a 2009 IRC? I have a question.

Quote:
Originally Posted by Brian A. MacNeish View Post
Go to www.buildingscience.com and do a search for "OVE". 4-5 documents come up including one about a project in Dallas.

OVE has been in the books/periodicals for 25-30+ years but rarely gets applied......builders are a very conservative bunch!!
Hey Brian, that's my point. I.ve never seen it. But thanx for the info, this way I won't be too caught by surprise if I ever do see it. By the way Dallas is 300 miles north of here, so I guess won't be doing that inspection.



Joe Keresztury
JWK Inspections
Home Inspections in San Antonio,
Schertz, Cibolo, New Braunfels, Boerne
and all surrounding South Texas areas
www.jwkhomeinspections.com
Reply With Quote
  #24  
Old 6/7/11, 8:44 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,783
Default Re: Any rough framers have a 2009 IRC? I have a question.

This is a scan from one of my books for Low-Cost Wood Homes for Rural America Construction Manual from the U.S. Department of Agriculture.

Although, I never framed like this, some would.

any-rough-framers-have-2009-international-residential-code-have-question-window-framing-1969.jpg

Reply With Quote
  #25  
Old 6/11/11, 4:06 PM
Marvin Maizel Marvin Maizel is offline
New User
 
Join Date: Jun 2011
Posts: 4
Please Note: Marvin Maizel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any rough framers have a 2009 IRC? I have a question.

I always used a double window sill and jack studs beside the main stud under them. It was far more solid and quicker to nail through the main stud into the sills. This method also allowed for better nailing for the apron trim. No jacks above the header and of course cripples below the sill and above the header if room.

The double sill is worthwhile and probably more than code requires. In my opinion.
Reply With Quote
  #26  
Old 6/12/11, 10:53 PM
ctasker ctasker is offline
Active Poster
 
Join Date: Nov 2010
Location: Alberta Canada
Posts: 226
Please Note: ctasker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any rough framers have a 2009 IRC? I have a question.

In Canada their would be cripple jack studs , have never seen, or framed without .
Reply With Quote
  #27  
Old 6/16/11, 8:33 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: Any rough framers have a 2009 IRC? I have a question.

Quote:
Originally Posted by gromicko View Post
Nails only hold wood together, they are not meant to be used to carry a load (even if the load is only a window) like the horizontal nails holding up the ends of the window sill are doing in the IRC's figure R602.3(2).
Nick,
You are getting tunnel vision due to your region of the county (snow load). I do understand your concern about down load support but i think that a sill that is face nailed through a jack stud and supported with a "trimmer stud" 16" away is certainly able too support a window.
Viewing the diagram from a "wind borne debris zone" it makes perfect sense in that we must account for lateral, and uplift as well as compressive loads. If the sill is let into the jack stud as in Bob's diagram it would become a hinge point (weak point) in resisting lateral and uplift loading. A strap would have to be added to connect the bottom and top of the cut jack to provide a continuous path of restraint. Even at that it would still be a hinge point and thus weakening the structure



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #28  
Old 6/16/11, 9:20 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Any rough framers have a 2009 IRC? I have a question.

Quote:
Originally Posted by gromicko View Post
Nails only hold wood together, they are not meant to be used to carry a load (even if the load is only a window) like the horizontal nails holding up the ends of the window sill are doing in the IRC's figure R602.3(2).
Most deck hangers are attached with nails that carry the load and prior to metal hangers, the joists were nailed or toe-nailed to the ledger board. Appropriate size nails have carried loads for longer than anyone here has been alive.

I can't say I have ever seen a window that was not attached in some way to the jack stud and header, in which case there would be a minimal, if any, load on the sill. If the window was not attached to the jack stud or header, the load on the sill would be limited to the weight of the window itself, since the header completely spans the opening.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Next Energy Audit Class - May 15, 2009 jmckenna1 Thermal Imaging, Infrared Cameras & Energy Audits 3 5/12/09 1:47 PM
Law and Disorder - DALLAS, TX - January 28, 2009 jferry1 Inspection Education & Training 0 1/19/09 4:14 PM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 3:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts