Default Is this a bad idea?

As the picture shows, the AC is damaged and I will report that. But, what about the overall idea of running the plumbing and electrical through the cabinet? Any issues with this besides the obvious of losing cabinet space? Safety concerns with electrical in a cabinet where you can reach your hand?
Attached Thumbnails
bad-idea-p6120014.jpg  



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 6/12/09, 8:50 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,641
Default Re: Is this a bad idea?

is there any open wires?
Reply With Quote
  #3  
Old 6/12/09, 8:52 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 757
Default Re: Is this a bad idea?

Quote:
Originally Posted by wwilson3 View Post
is there any open wires?
Yes the AC cable is damaged, But after it is repaired, is there still an issue?
Attached Thumbnails
bad-idea-p6120013.jpg  



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #4  
Old 6/12/09, 8:54 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 951
Default Re: Is this a bad idea?

That wiring should be protected. Run in conduit in that cabinet.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #5  
Old 6/12/09, 8:56 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 951
Default Re: Is this a bad idea?

Extend that bx through the cabinet.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #6  
Old 6/12/09, 9:00 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 757
Default Re: Is this a bad idea?

Quote:
Originally Posted by dokeefe View Post
That wiring should be protected. Run in conduit in that cabinet.
AC is not good enough protection?



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #7  
Old 6/12/09, 9:08 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,917
Default Re: Is this a bad idea?

It is a storage cabinet, and the Armored Cable has pulled apart from its connector meaning that it has already received some abuse, therefore, the EMT should continue through the cabinet closer to where the AC needs to connect to.

Note what you see and recommend repairs by a qualified licensed Electrician.
Reply With Quote
  #8  
Old 6/13/09, 12:11 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,115
Default Re: Is this a bad idea?

In addition to correcting the Greenfield/AC, maybe suggest a building a removable back to the cabinet. You can pretty much guarrantee that the cabinet will be used for storage and thay will rest objects on top of the copper, EMT and flex.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #9  
Old 6/13/09, 10:52 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a bad idea?

Quote:
Originally Posted by jwicklander View Post
In addition to correcting the Greenfield/AC, maybe suggest a building a removable back to the cabinet. You can pretty much guarrantee that the cabinet will be used for storage and thay will rest objects on top of the copper, EMT and flex.

Jeff
Along those same lines, it looks like there's maybe 6" or so from the cabinet door to the copper, etc.

Perhaps recommend not to use that for storage at all.
Reply With Quote
  #10  
Old 6/13/09, 11:19 AM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,829
Default Re: Is this a bad idea?

nuthin like pisspoor building techniques.
Most cabinets I've seen, have a toe kick area at their base,(which happens to be hollow)
I think they should have gone through the hollow open space BELOW the cabinet.
But Nooooo, we gotta go in a straight line and destroy the whole cabinet...sheesh



Steven Waskewicz
Rest Assured Inspection Services, LLC.
719-510-7703 mobile all the time
719-495-7166 Fax.
s_waskewicz@msn.com
HVAC Lic. #10722
EPA cert.544143239730

www.restassuredinspection.com
NACHIiid=NACHI06032370





Reply With Quote
  #11  
Old 6/13/09, 11:24 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a bad idea?

What kind of room was this in? Seems someone went through a lot of effort to thread those materials through the holes (after the room was painted).
Reply With Quote
  #12  
Old 6/13/09, 1:47 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 757
Default Re: Is this a bad idea?

Quote:
Originally Posted by rmaday View Post
What kind of room was this in? Seems someone went through a lot of effort to thread those materials through the holes (after the room was painted).
Rick, this is in a condo, kitchen. The site of the old Lexington hotel, Al Capone's old hang out. Yeah it seems the client will lose this storage space, but maybe can use it for small objects. I thought it was a bad place to put the plumbing.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #13  
Old 6/13/09, 2:30 PM
dbolduc dbolduc is offline
Active Poster
 
Join Date: Jan 2009
Location: Freedom, NH
Posts: 130
Please Note: dbolduc is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a bad idea?

Rumor has it that place is haunted.
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #14  
Old 6/13/09, 3:40 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 757
Default Re: Is this a bad idea?

I don't know if it is haunted, but I have heard that rumor. They demo'd the old building and rebuilt, so maybe the ghosts will leave now.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Marketing Idea For Nick wwilson3 Miscellaneous Discussion for Inspectors 5 3/15/09 9:54 PM
Good Idea jmckenna1 Miscellaneous Discussion for Inspectors 1 10/7/06 2:31 AM


All times are GMT -4. The time now is 11:52 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts