Default how to call this out????

From today's inspection not sure if this is of any concern the pic is of propane tanks located close to a dryer vent. I don't think it is of concern because the vent really isn't considered an ignition source, but you thoughts and comments are welcome.
Attached Thumbnails
call-out-propane-tank-and-vent.jpg  
Reply With Quote
  #2  
Old 2/13/08, 10:10 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,649
Default Re: how to call this out????

The vent is broken and needs replaced.
Reply With Quote
  #3  
Old 2/13/08, 10:20 PM
rgrizzle's Avatar
rgrizzle rgrizzle is offline
Active Poster
 
Join Date: May 2007
Location: Little Torch Key, Fl
Posts: 358
Please Note: rgrizzle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: how to call this out????

called out the vent, and the tanks service the dryer and stove
Reply With Quote
  #4  
Old 2/13/08, 11:18 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: how to call this out????

Tanks are small for that appication and at a minimum should be secured in place.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 2/14/08, 12:26 AM
T.J. Christopher T.J. Christopher is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Torrington, WY
Posts: 187
Default Re: how to call this out????

Propane tanks are supposed to be min 25 ft from dwellings & with ends directed away from house. Big tanks anyway. Looks like some kind of redneck retrofit project...
Reply With Quote
  #6  
Old 2/14/08, 12:58 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: how to call this out????

If that's a window to the left out of frame the location is unacceptable

The piping should be protected from impact and secured to the structure, imo

I note that for safety reasons the peramanant installed appliances should have a properly installed gas supply.




badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #7  
Old 2/14/08, 6:47 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: how to call this out????

Another thing that is of concern is the wall where the supply line passes through stucco (cement product with metal lath)
I'd think a sleeve should be in place so no direct contact with the copper piping occurs, potentially causing corrosion or dielectric failure at that junction.



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #8  
Old 2/14/08, 7:50 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,378
Default Re: how to call this out????


The tanks in the post is obviously make shift set-up by the owner so they can exchange tanks at will.
A propane supplier would not fill those on site with this set-up.
Those are what we call 20# tanks.


Usually this would be the set up, with one or two tanks, determined by the usage.
These are 120 gallon tanks.


ABOVE-GROUND TANKS
200 gallon30" diameter x 79" long Holds 160 gallon
250 gallon 30" diameter x 94" long Holds 200 gallon
320 gallon 30" diameter x 119" long Holds 256 gallon
500 gallon37" diameter x 119" long Holds 400 gallon
1000 gallon41" diameter x 193" long Holds 800 gallon

The Law requires these tanks to be placed upon a solid masonry footing or foundation. Sometimes a contractor will pour a pad to place the tank upon.

The propane tank must be more than ten (10) feet from a building and more than ten (10) feet from a source of ignition or combustible materials and property line.
* Tanks greater than 500 gallon capacity require greater distances. All propane tanks should be painted with light-colored, reflecting paint.




Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #9  
Old 2/14/08, 2:04 PM
T.J. Christopher T.J. Christopher is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Torrington, WY
Posts: 187
Default Re: how to call this out????

They look like tanks off a BBQ grill...
Reply With Quote
  #10  
Old 2/14/08, 2:20 PM
rgrizzle's Avatar
rgrizzle rgrizzle is offline
Active Poster
 
Join Date: May 2007
Location: Little Torch Key, Fl
Posts: 358
Please Note: rgrizzle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: how to call this out????

Quote:
Originally Posted by tchristopher
They look like tanks off a BBQ grill...
They are. this is common down here to see this. we don't have natural gas, here is everything is propane/LP. Most homes here don't even have heat in them and the only use for propane is for cooking, hot water or for a clothes dryer. So it is cheaper for people that have an electric water heater to have this setup, then to have something that is more of a head ache to schedule someone to come out and fill it once in a blue moon and pay a big bill.

I have a 100 gallon tank that is filled once every three months. We don't use a whole lot of propane.
Reply With Quote
  #11  
Old 2/14/08, 3:53 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: how to call this out????

Quote:
Originally Posted by mcyr
The tanks in the post is obviously make shift set-up by the owner so they can exchange tanks at will.
A propane supplier would not fill those on site with this set-up.
Those are what we call 20# tanks.


Usually this would be the set up, with one or two tanks, determined by the usage.
These are 120 gallon tanks.


ABOVE-GROUND TANKS
200 gallon30" diameter x 79" long Holds 160 gallon
250 gallon 30" diameter x 94" long Holds 200 gallon
320 gallon 30" diameter x 119" long Holds 256 gallon
500 gallon37" diameter x 119" long Holds 400 gallon
1000 gallon41" diameter x 193" long Holds 800 gallon

The Law requires these tanks to be placed upon a solid masonry footing or foundation. Sometimes a contractor will pour a pad to place the tank upon.

The propane tank must be more than ten (10) feet from a building and more than ten (10) feet from a source of ignition or combustible materials and property line.
* Tanks greater than 500 gallon capacity require greater distances. All propane tanks should be painted with light-colored, reflecting paint.




Marcel
Marcel:

Propane tanks up here are installed as in the picture- right beside the building- but a couple of references have said 10' from the building. Comments??
Reply With Quote
  #12  
Old 2/14/08, 4:06 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 696
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: how to call this out????

I would verbally suggest a larger tank with a guage be properly installed and in my report "consult with a local propane supplier or certified gas technician".
Another safety issue is with trips to the refill depot with 20 pounders rolling around in the trunk.
Reply With Quote
  #13  
Old 2/14/08, 6:49 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,378
Default Re: how to call this out????

Quote:
Originally Posted by Brian A. MacNeish
Marcel:

Propane tanks up here are installed as in the picture- right beside the building- but a couple of references have said 10' from the building. Comments??
Hi. Brian;

With my experience in using propane over the years for temporary heating of structures and shelters, the limit to the ten feet around here is 500 gal. or more.

They also require a hard pipe going through the structure and you are limited to a 6 ft. section of flexible hose.

The 250' called pigs around here, which are uprights, do not matter.

Each Jurisdiction might have different set of rules, so I would check with local athorities.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #14  
Old 2/23/08, 7:56 PM
Kevin Hazelton Kevin Hazelton is offline
InterNACHI Member
 
Join Date: Dec 2007
Location: Jackson, MI
Posts: 78
Default Re: how to call this out????

Quote:
Originally Posted by jkogel
I would verbally suggest a larger tank with a guage be properly installed and in my report "consult with a local propane supplier or certified gas technician".
Another safety issue is with trips to the refill depot with 20 pounders rolling around in the trunk.
Would'n dem bombs be best in the bed o yer pick'em up?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Last Call for INSPECTVUE SOFTWARE DISCOUNT $845.00 includes Tax...... jwatts1 Hardware, Software & Publications 4 8/8/07 11:47 AM
Last call for 2006 pricing for Inspection Management Systems from TheScheduleCenter gromicko Misc. Discussion 1 12/20/06 9:22 AM


All times are GMT -4. The time now is 1:38 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts