Default Chimney height on roof

I always thought a chimney needs to be at least 3 feet above a roof. But in looking closer at the Inspection Graphics it states a minimum of 2 feet for gas vent or type L vent. The chimney in the pixs is from the oil furnace and is 2 feet high. Is this OK or should it be three feet?
Attached Thumbnails
chimney-height-roof-058.jpg   chimney-height-roof-059.jpg   chimney-height-roof-chimney-less-than-10-ft-pitched.jpg  



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout on LinkedIn
Follow David O'Keefe on Twitter
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/17/10, 10:47 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,401
Default Re: Chimney height on roof

I measured it from the low side, but on the ridge side it is probably only a foot and a half tall. Should it be 2 feet at the ridge side?



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout on LinkedIn
Follow David O'Keefe on Twitter
Reply With Quote
  #3  
Old 8/17/10, 10:53 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,571
Default Re: Chimney height on roof

Strictly speaking of the projection of the chimney. . .

3 ft. tall min - measured from the tallest side.
2 ft. higher than any wall/ridge within 10 ft.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 8/17/10 at 10:56 PM..
Reply With Quote
  #4  
Old 8/17/10, 11:20 PM
Larry Kage, CMI Larry Kage, CMI is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: NW, MI
Posts: 11,684
Default Re: Chimney height on roof

Quote:
Originally Posted by dokeefe View Post
Should it be 2 feet at the ridge side?
Yes, minimum...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/
____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
whis11 @ charter.net
The above post represents my personal opinion.
Reply With Quote
  #5  
Old 8/17/10, 11:20 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,401
Default Re: Chimney height on roof

Quote:
Originally Posted by jpope View Post
Strictly speaking of the projection of the chimney. . .

3 ft. tall min - measured from the tallest side.
2 ft. higher than any wall/ridge within 10 ft.
So, it's too short on both sides. No difference from gas, oil, wood chimneys?



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout on LinkedIn
Follow David O'Keefe on Twitter
Reply With Quote
  #6  
Old 8/18/10, 12:34 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,571
Default Re: Chimney height on roof

If it's a "chimney," those are the requirements. If it's a "vent" (gas-fired, oil-fired), these requirements do not apply.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 8/18/10, 1:14 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 32,068
Default Re: Chimney height on roof

Quote:
Originally Posted by jpope View Post
If it's a "chimney," those are the requirements. If it's a "vent" (gas-fired, oil-fired), these requirements do not apply.
This is a metal chase surrounding a vent.
What say you?
Reply With Quote
  #8  
Old 8/18/10, 4:33 PM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,571
Default Re: Chimney height on roof

Depends on the slope of the roof and the appliance it serves, but generally speaking for what is pictured. . .

2 ft. minimum projection from the roof and 2 ft. above a wall or similar obstruction within 10 ft. of the termination.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 8/18/10, 5:13 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 32,068
Default Re: Chimney height on roof

Quote:
Originally Posted by jpope View Post
Depends on the slope of the roof and the appliance it serves, but generally speaking for what is pictured. . .

2 ft. minimum projection from the roof and 2 ft. above a wall or similar obstruction within 10 ft. of the termination.
OK ,from the earlier response I thought you were viewing it as a wood burning fireplace chimney.

I think many are not clear on the difference and bet seeing the fake brick(metal) chase would put them in 10/3/2 mode.
Reply With Quote
  #10  
Old 8/18/10, 6:09 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,401
Default Re: Chimney height on roof

Quote:
Originally Posted by belliott View Post
This is a metal chase surrounding a vent.
What say you?
Here is another pix. It is a vent from an oil fired furnace made to look like a brick chimney. So the 2/10/3 rule doesn't apply? But it still needs to be at least 2 feet above the ridge.
Attached Thumbnails
chimney-height-roof-060.jpg  



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout on LinkedIn
Follow David O'Keefe on Twitter
Reply With Quote
  #11  
Old 8/18/10, 6:16 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 32,068
Default Re: Chimney height on roof

Quote:
Originally Posted by dokeefe View Post
Here is another pix. It is a vent from an oil fired furnace made to look like a brick chimney. So the 2/10/3 rule doesn't apply? But it still needs to be at least 2 feet above the ridge.
That is pretty much what I was saying.
Reply With Quote
  #12  
Old 8/18/10, 6:33 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,401
Default Re: Chimney height on roof

OK, anyone., what is the difference between these two. A block chimney with a tile flue from a gas furnace and this metal flue from an oil furnace. Why are the requirements not the same? One is required to be three feet high but the other one only 2 feet high? Am I missing something?
Attached Thumbnails
chimney-height-roof-054.jpg   chimney-height-roof-059.jpg  



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout on LinkedIn
Follow David O'Keefe on Twitter
Reply With Quote
  #13  
Old 8/18/10, 6:36 PM
ROBERT YOUNG, CMI's Avatar
ROBERT YOUNG, CMI ROBERT YOUNG, CMI is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: H4B2R8
Posts: 9,951
Send a message via Yahoo to ryoung7
Default Re: Chimney height on roof

for O'Keeffe about false chimney.
Its a chase enclosure and there are plenty of them in western part of Montreal Quebec Canada.They can be for wood,an oil furnaces.Cheaper then doing a brick double width and single width Terra cotta lined chimneys.
You see them mostly on double cladded facade exterior homes.Lower part brick about first 8 to 10 feet and upper part siding.I rarely see this on fully brick clad homes but I have seen a few and far between.Maybe after thought.
For O'Keeffe on brick and block chimney.
Even the ridge vent is so close to the spark arrester from the chimney ,no crown to control rain dripping , and drafting ,stop spillage and if there is back drafting all that startup and shut down smoke goes right into the home along with Co's from burning..
From the pictures I see its a real hazard.
Just my opinion.
Now to answer you question its fire hazard that is caused from wood burning fireboxes and fire places and the sparks on the roof from chimneys built to close to the roof that is why they have a hight restriction and should have spark arresters on top of the crown or cap as some people call it.The hight regulation is for smoke and spark that has to draft properly over a roof and not drift into windows and roof vents.As for oil stoves the heat is not as hazards and no sparks but there is Co's that have to be carried away by drafting so hight requirements are in place.
If you google chimney hight requirements you should be OK and InterNACH has in depth building code on this.
Hight restrictions for oil and wood burning fireplaces.
1 : brick chimneys must be higher because of outlet is larger '' FLUE'' for spark and fire concerns
2 : oil chases lower because outlet is smaller ''flue'', no chance of spark fires.
I hope this helped you.
I am a mason and build chimneys and if you need more help email me and if I have the time I would be glad to answer you question but everything is on internachi .
Sorry if my explanation is all over the place .I am tired.

Last edited by ryoung7; 8/18/10 at 7:26 PM.. Reason: adding
Reply With Quote
Need a home inspection in Iowa? Check out InterNACHI's listing of Iowa certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 8/18/10, 6:39 PM
David OKeefe's Avatar
David OKeefe David OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar, NY ★ New York's Capital Region
Posts: 1,401
Default Re: Chimney height on roof

I am asking why are the height requirements different, or am I misinterpreting/misunderstanding something?



David

InterNACHI Certified Home Inspector #08051301
NYS Licensed Home Inspector #16000038229
NYS DEC Certified Pest Technician # T4865884
518-505-8305
HouseAbout Home Inspections, LLC
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI
Connect on LinkedIn
Follow HouseAbout on LinkedIn
Follow David O'Keefe on Twitter
Reply With Quote
  #15  
Old 8/18/10, 6:39 PM
ROBERT YOUNG, CMI's Avatar
ROBERT YOUNG, CMI ROBERT YOUNG, CMI is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: H4B2R8
Posts: 9,951
Send a message via Yahoo to ryoung7
Default Re: Chimney height on roof

Both of these would be breaking code in Montreal Canada.Read hight and clearance regulations for chimneys.No more block chimneys in Montreal thats for most of the areas I have looked into anyway and the clearance is off spec that for sure.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Foam Insulation Requires roof Ventilation dvalley Thermal Imaging, Infrared Cameras & Energy Audits 30 9/4/10 2:43 AM
Roof Height? nbhi Exterior Inspections 22 10/1/09 5:37 PM
Before You Start Repairing or Replacing Roof Finishes from CMHC mkyriacou Canadian Inspectors 0 9/17/09 12:52 PM
What's Inside A Chimney mcyr Inspecting HVAC Systems 14 9/17/08 6:11 PM
Moss growing on roof ecox1 Exterior Inspections 45 1/19/06 9:57 PM

All times are GMT -4. The time now is 5:14 PM.
no new posts