Default Clearance to combustibles?

I recently did an inspection of a house that had a flue pipe for a wood burning stove running up the exterior side of the house and through the soffit and roof above. Siding is T-111 and untreated wood shakes. The flue comes within 6" of the siding. I could not find any documentation for the fireplace and am not sure what the current building requirements are. Can you all give me some advice on this?

Terry
Attached Thumbnails
clearance-combustibles-flue.jpg  
Reply With Quote
  #2  
Old 6/8/08, 7:04 PM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,093
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Clearance to combustibles?

6" spacing would apply to single wall. That picture shows at least a double wall and possible triple wall. It may actually be "Zero" clearance acceptable. OEM safety info should have been stamped into the material.

Good Luck!
Reply With Quote
  #3  
Old 6/8/08, 7:04 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Clearance to combustibles?

Not sure what type of flue that is. There should be mfrs. markings on the flue pipe.

It it's type HT it needs to be 2" minimum to combustibles.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #4  
Old 6/8/08, 7:10 PM
tlorenz's Avatar
tlorenz tlorenz is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Bozeman, MT
Posts: 26
Default Re: Clearance to combustibles?

Thanks guys!

appreciate it.

Terry
Reply With Quote
  #5  
Old 6/8/08, 7:17 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Clearance to combustibles?

Quote:
Originally Posted by whandley
6" spacing would apply to single wall. That picture shows at least a double wall and possible triple wall. It may actually be "Zero" clearance acceptable. OEM safety info should have been stamped into the material.

Good Luck!
Will, I think you may have missed that he was talking about a wood burning stove. I know of no single wall pipe for wood burning that can be within 6" of combustibles...single wall for gas, yes.

Quote:
Originally Posted by tlorenz
I recently did an inspection of a house that had a flue pipe for a wood burning stove running up the exterior side of the house and through the soffit and roof above. Siding is T-111 and untreated wood shakes. The flue comes within 6" of the siding. I could not find any documentation for the fireplace and am not sure what the current building requirements are. Can you all give me some advice on this?

Terry
Metalbestos brand requires 2" to combustibles also. I believe what is shown in the picture is too close to combustibles because it is touching siding at the wall.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 6/8/08 at 7:20 PM..
Reply With Quote
  #6  
Old 6/8/08, 7:31 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Clearance to combustibles?

Quote:
Originally Posted by lkage
I know of no single wall pipe for wood burning that can be within 6" of combustibles...single wall for gas, yes.
I do.
It's triple wall and 1" clearance to combustibles is OK for vertical runs.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #7  
Old 6/8/08, 7:34 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Clearance to combustibles?

Quote:
Originally Posted by mlarson
I do.
It's triple wall and 1" clearance to combustibles is OK for vertical runs.
You know of a single wall pipe that is called triple wall?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #8  
Old 6/8/08, 7:40 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Clearance to combustibles?

Quote:
Originally Posted by lkage
You know of a single wall pipe that is called triple wall?
Well now were both in error. Sorry. Read too fast.

Will never said single wall was OK for zero clearance.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #9  
Old 6/8/08, 7:44 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Clearance to combustibles?

Quote:
Originally Posted by mlarson
Well now were both in error. Sorry. Read too fast.

Will never said single wall was OK for zero clearance.
I said he did?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #10  
Old 6/8/08, 7:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Clearance to combustibles?

Quote:
Originally Posted by lkage
I said he did?
We all agree that the photo appears problematic.

You claimed Will "missed" something. What did he miss?

No harm no foul Larry. I apologize again for my hastily composed and erroneous post.

I have only seen "zero clearance" refer to the fire box portion of manufactured wood burning fireplaces and those usually have some type of stand off built into or attached to the outer shell.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #11  
Old 6/8/08, 8:09 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Clearance to combustibles?

Quote:
Originally Posted by mlarson
You claimed Will "missed" something. What did he miss?
That it was a wood burning stove...


Quote:
Originally Posted by lkage
Will, I think you may have missed that he was talking about a wood burning stove. I know of no single wall pipe for wood burning that can be within 6" of combustibles...single wall for gas, yes.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #12  
Old 6/8/08, 8:13 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Clearance to combustibles?

Larry have a nice evening.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Clearance Testing tfarmer Ancillary Inspection Services & Additional Topics 15 2/26/08 6:41 PM
chearance to combustibles Leanne Jowers General Inspection Discussion 5 5/14/07 11:49 AM
Range Clearance dsmith6 Interior Inspections 18 1/7/07 10:55 PM
Siding to Ground Clearance tneumann Exterior Inspections 14 2/9/06 12:48 AM


All times are GMT -4. The time now is 6:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts