Default CSST bonding

What's the deal with the bonding of the corrugated stainless steel tubing for gas appliances. I have been asked by a Real Estate agent on how and who to reply to a request of a non visible bonding wire to a gas heater with CSST. Many electricians, HVAC techs, builders and inspectors are still not in the loop on this issue. Is the electrician the one to address this issue. I looked on the internet and found this latest article-
http://www.toolbase.org/pdf/techinv/...ngconcerns.pdf

I would like to know if and how to include this in my inspections and reporting. It seems like its still up in the air. That's progress for you!

Thanks,
Ron
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/12/10, 9:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,046
Default Re: CSST bonding

Bonding is typically established by an electrician. Other tradesmen are not necessarily qualified to determine or establish proper bonding.

The "non-visible" (I'm not sure what you mean by that) bonding wire must have visible and accessible bonding connections.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 8/12/10, 9:17 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,602
Default Re: CSST bonding

Not sure what you mean by non visible bonding wire.

IMO the electrician is the one to address the issue.

The CSST must be bonded only at the end nearest the entry of the gas service into the building. If it is bonded at both ends, or at the end nearest the gas-burning appliance, the CSST may carry stray electrical currents or act as a grounding conductor, which can damage the CSST and its fittings, and cause leaks.

Here is a good discussion of the issue.

G2411.2 (310.2) Gas pipe bonding - systems that contain CSST. A gas piping system that contains any corrugated stainless steel tubing (CSST) shall be electrically continuous and shall be bonded to the electrical service grounding electrode system at the point where the gas service enters the building or structure. No portion of the gas piping system shall be used as or considered to be a grounding electrode or a grounding electrode conductor. CSST shall be installed and bonded in accordance with this section G2411.2, and the stricter of: (a) the requirements set forth in the CSST manufacturer’s installation instructions, or (b) the requirements set forth in Sections G2411.2.1, G2411.2.2, G2411.2.3, and G2415.5.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 8/12/10, 9:28 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: CSST bonding

The correct term is "additional bonding". It should already have the branch circuit ground connected to the little green wire inside the furnace compartment so that is the basic bond that was ok for quite sometime.

Most areas around here started requiring the additional bonding in late 2007 with very strict enforcement. Separate permit required by an electrician in some areas when it first became an issue. Its more expensive to add when the distance from the gas pipe to the ground electrode is long. A second ground rod is not allowed, it must be bonded to the existing ground system for equipotential.


Upgrade recommended: No grounding or bonding found for the gas piping except through the furnace equipment’s ground. This is an accepted method in many areas but recent changes have occurred to the bonding requirements in some areas and upgrades are recommended to enhance the safety level of the home.

The CSST flexible gas piping that is used throughout the house is a common item. A class action lawsuit involved this type of product. The details are available at www.CSSTsettlement.com or 800 420-2916

The product was not recalled but recommendations were made to closely follow the manufactures installation instructions. The instructions are not part of this inspection but likely involve proper bonding methods of the pipe to prevent issues with lightning damaging the thin walled pipe. I recommend having upgraded bonding installed by a licensed electrician, plumber or HVAC person that is familiar with the installation instructions. Typical methods use a #6 solid copper conductor clamped to the black iron main gas pipe at the exterior with the other end clamped to the existing electrical grounding electrode conductor (GEC) that runs to an existing ufer grounding system or the existing grounding rod imbedded in the earth. Upgrade products called gas breakers can also be added inline with the gas piping distribution for a higher safety factor since they are designed to shut off if an unusual flow of gas is present.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 8/13/10, 7:32 AM
Ronald L. Eckenroth Ronald L. Eckenroth is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Reading, PA
Posts: 3
Default Re: CSST bonding

Bruce thanks for you good reply. I understand the main bond for the gas steel pipe to the electrical system but the circuit wire to the furnace is no longer acceptable? If we do not see a #6 ground from the furnace to the steel pipe (upgrade recommended).
Reply With Quote
  #6  
Old 8/13/10, 6:45 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: CSST bonding

Quote:
Originally Posted by reckenroth View Post
Bruce thanks for you good reply. I understand the main bond for the gas steel pipe to the electrical system but the circuit wire to the furnace is no longer acceptable? If we do not see a #6 ground from the furnace to the steel pipe (upgrade recommended).

The regular equipment ground to the furnace is still needed.
The additional bonding would not typically run all the way to the furnace area, it would only go the shortest distance needed to get a clamp on the steel gas pipe. They do make some clamps that go on the CSST fitting joint but no one uses those around here.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #7  
Old 8/13/10, 8:36 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,608
Default Re: CSST bonding

Read third paragraph down in http://www.nachi.org/lightning.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
CSST Class Action jhagarty Inspecting HVAC Systems 31 1/31/12 12:15 AM
CSST bonding poll jfunderburk Electrical Inspections 17 8/12/09 4:28 PM
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM


All times are GMT -4. The time now is 7:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts