I heard today that this is becoming a common problem:

Dryer vents clogging up quickly due to condensation inside the uninsulated duct. The clog is occurring up near the roof termination point.

I guess this could occur on ones that run horizontal to a wall too.

I'm going to start recommending these ducts be insulated starting with a predrywall I did today.

Also,
I have started seeing more insulated condensate drain pipes in attics too (new homes). With the larger homes and owners that run the A/C a lot, there can be a lot of dripping condensation off these pipes into the attic insulation/sheetrock.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
Find an InterNACHI certified Florida Home Inspector (and anywhere else in North America)
  #2  
Old 6/16/09, 7:59 PM
Ian A. Niquette's Avatar
Ian A. Niquette Ian A. Niquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,193
Send a message via ICQ to iniquette
Default Re: dryer vents through the roof

How long is the run that these are clogging up on Bruce?



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network



What we've got here is......failure......to communicate.....
Reply With Quote
  #3  
Old 6/16/09, 7:59 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,826
Send a message via Yahoo to jfunderburk
Default Re: dryer vents through the roof

Insulating a dryer vent seems extreme to me. What do you have to base that recommendation on? (You're going to make your Realtor friends mad!)

I just say this: "The dryer vents vertically. The lint trap must be kept clean, because trapped lint can rapidly turn into a fire hazard. Inspection of the vent every 6 to 12 months is recommended to ensure it is not clogged."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 6/16/09, 8:06 PM
Keith Runquist Keith Runquist is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Rapid City, SD
Posts: 212
Send a message via AIM to krunquist
Default Re: dryer vents through the roof

Pretty common in dry south west locations and W. Texas but it doesn't get very cold and the dew point tends to be very low. I would guess that a big part of the problem is that no one ever cleans the lint out of the exit point since it's up on the roof.
Reply With Quote
  #5  
Old 6/16/09, 8:11 PM
Gary L. Farnsworth, CMI Gary L. Farnsworth, CMI is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 968
Default Re: dryer vents through the roof

I see some here in KC. I always have a concern about snow covering the vent.
Reply With Quote
  #6  
Old 6/16/09, 8:20 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,216
Default Re: dryer vents through the roof

Quote:
Originally Posted by jfunderburk View Post
Insulating a dryer vent seems extreme to me. What do you have to base that recommendation on? (You're going to make your Realtor friends mad!)

I just say this: "The dryer vents vertically. The lint trap must be kept clean, because trapped lint can rapidly turn into a fire hazard. Inspection of the vent every 6 to 12 months is recommended to ensure it is not clogged."

Realtor friends? ha! You know better than that!

A maintenance guy for a homebuilder told a friend about this, he said its becoming a major issue for them. Not sure if he is working for the builder or working on the side but that does not matter.

The typical roof run is probably 20-30 feet depending on the pitch, ceiling height etc. I agree with keith, the problem could be less if these outlets got cleaned once in a while, its just bad design to assume homeowners will do any maintenance.

Nothing wrong with recommending upgrades as long as they are stated as such.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #7  
Old 6/16/09, 8:26 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,581
Default Re: dryer vents through the roof

http://www.nachi.org/dryer-vent-safety.htm



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #8  
Old 6/18/09, 2:57 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 152
Default Re: dryer vents through the roof

Thanks for the post Nick. I am always looking for good safety and informational links for my website.



Robert Sole



407-637-7288


Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #9  
Old 8/23/09, 8:06 PM
John M. Murray John M. Murray is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Fayetteville, OH
Posts: 72
Default Re: dryer vents through the roof

Quote:
Originally Posted by gromicko View Post
Good info that cuts through the reality correct propaganda.






Cincinnati Ohio Home Inspection Services



Cincinnati Ohio Home Inspection
http://ohiocertifiedhomeinspections.us
Reply With Quote
  #10  
Old 8/26/09, 12:30 AM
Ryan Selwood Ryan Selwood is offline
InterNACHI Member
 
Join Date: Aug 2009
Posts: 2
Default Re: dryer vents through the roof

I just recently came across a dryer vent that entered the crawl space before exiting through the wall. The ribbed flex vinyl was completely torn apart and judging by the pounds of lint strown all over the crawlspace, it has been for quite some time. It gets worse too. Although the residence was currently empty(including the dryer), and there were gas and hydro hook-ups available, I could tell by the teflon paste apparent on the gas fitting that it was likely gas exhaust pumping straight into the three bedrooms immediately over that portion of the crawlspace. Those flexible ribbed vents should always be listed a defect.
Reply With Quote
  #11  
Old 8/26/09, 1:32 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,728
Default Re: dryer vents through the roof

Attached Thumbnails
dryer-vents-through-roof-1757-e-carson-8-8-09-028.jpg   dryer-vents-through-roof-1757-e-carson-8-8-09-030.jpg  



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #12  
Old 8/26/09, 1:58 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,681
Default Re: dryer vents through the roof

Quote:
Originally Posted by bkelly2 View Post
Beat ya--




Reply With Quote
  #13  
Old 8/26/09, 2:03 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 6,681
Default Re: dryer vents through the roof

Or through a Garage Cabinet terminated in a Cabinet.

Reply With Quote
Find an InterNACHI certified Florida Home Inspector (and anywhere else in North America)
  #14  
Old 8/26/09, 7:47 AM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: dryer vents through the roof

I had one yesterday that was venting over a lower roof. The shingles (below) were full of lint.
Reply With Quote
  #15  
Old 8/26/09, 10:45 AM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 801
Default Re: dryer vents through the roof

Quote:
Originally Posted by gromicko View Post
Good article.

A dryer vent booster fan should be installed if the run exceeds 25'. This is determined after taking into acct. the 90 degree turn reduces it by 5' and the 45 degree turns reduce it by 2.5'.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A little on the Commercial side of things. mcyr General Inspection Discussion 457 8/1/09 11:50 AM
Building Science- research from respected sources Brian A. MacNeish Ancillary Services & Additional Topics 12 2/13/08 12:33 PM
Chimney flashing photo's needed: brick and stone done correctly kshepard Exterior 6 10/13/07 9:10 AM
Roof Repair? Maybe NO jhagarty Exterior 9 2/15/07 2:19 AM


All times are GMT -4. The time now is 9:30 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts