Inspection today had a interesting electrical panel, How many defects do you see. I was told they upgraded from fuses and from the exterior service I expected a 100 amp panel.
This what I got. I wish I had taken more pictures, there was also water lines above and beside it and no clearance in front. www.tristatehomeinspections.org www.tristateenergyinspections.com If you always do what you always did you will always get what you always got. |
|
#2
|
|||
|
|||
|
Please Note:
jguillen is a non-member guest and is in no way affiliated with InterNACHI or its members.
DOUBLE TAPPING OF NEUTRALS IS A CODE VIOLATION A HAZARDOUS Situation see nec 408.41 each neutral needs to be individually in its terminal also see article 110 each terminal is intended for 1 wire only and the service wires feeding panel are detiorated and the lower voltage wires coming down with feeders is un acceptable to me it is a noncompliance write -up i will call it a failed inspection from JOSE A. GUILLEN ICC
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Coming to Schaumburg, Ill - Electrical Training with The Electrical Guru | ksitzes | Inspection Education & Training | 12 | 3/17/10 4:19 PM |
| Download the videos here all about physics and electricity | jtedesco1 | Electrical Inspections | 5 | 9/14/08 3:58 PM |
| Electrical Safety Foundation International Links | jtedesco1 | Electrical Inspections | 5 | 12/8/07 3:10 PM |
| Electrical Safety Information | jtedesco1 | Electrical Inspections | 0 | 2/19/06 1:48 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |