Default Fire Doors / tags

Looking for information on Fire Rating tags on service doors...
Reply With Quote
  #2  
Old 8/13/07, 8:48 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Fire Doors / tags

James, start with this and see if it helps, if not let me know so I can assist.

http://www.steeldoor.org/pdfs/118.pdf


Marcel
Reply With Quote
  #3  
Old 8/16/07, 5:50 PM
Wilfred O. Hellner Wilfred O. Hellner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Longwood, FL
Posts: 121
Send a message via AIM to whellner
Default Re: Fire Doors / tags

I am a member of NFPA . what exactly are you looking for? the tag itself? or what rating the firedoor should have in that fire wall or smoke wall?



Will Hellner Florida Licence # HI103
Reply With Quote
  #4  
Old 8/16/07, 7:33 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 18,918
Default Re: Fire Doors / tags



Notes on Fire Door Requirements
  1. Fire rated door assemblies require a labeled door, a labeled frame, a listed lock device, listed closing device, and steel bearing hinges. Non-steel bearing hinges are acceptable as tested on listed assemblies.
  2. In general, the required hourly rating of the door assembly is 3/4 of the hourly rating of the wall it is being installed into.

  3. The minimum rating of any component in the assembly determines the achieved rating as the assembly: a 1 1/2 hour door installed into a 20-minute frame results in a 20-minute assembly.

  4. Subdivision of non-rated components or devices in the door assembly can only result in a reduction in or a voiding of the overall fire protection rating.

  5. Most fire door installations are governed by NFPA 80- Fire Doors and Windows.
http://www.benchmarkdoors.com/Buildi...ireCodes.shtml

Marcel
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Escape, Fire & Smoke Alarms badair Interior Inspections 14 1/28/08 8:21 AM
Good man rcooke Canadian Inspectors 3 12/4/06 11:38 AM
The Fire Guy ccrooker Canadian Inspectors 0 3/8/06 12:11 AM


All times are GMT -4. The time now is 2:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts