Default Fire Separation in Garage

Noted this in today's inspection. It looks like a portion of the garage to attic ceiling has been removed to make storage. From above it opens to the entire attic. Any suggestions on wording for fire separation? Thanks
Attached Thumbnails
fire-separation-garage-fire-wall.jpg  



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #2  
Old 5/7/08, 9:26 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,841
Default Re: Fire Separation in Garage

Quote:
Originally Posted by rnewland
Noted this in today's inspection. It looks like a portion of the garage to attic ceiling has been removed to make storage. From above it opens to the entire attic. Any suggestions on wording for fire separation? Thanks
The fire separation wall between the garage and living area is missing and a safety hazard...recommend repair as needed for safety.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 5/7/08, 10:08 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,511
Default Re: Fire Separation in Garage

That's pretty much what I have... short and sweet Thanks



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #4  
Old 5/14/08, 10:05 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,731
Default Re: Fire Separation in Garage

I know this is an old post, but i thought i would speak my .02 cents.
In my state, (MI) 1/2 hour "burn time" is mandatory. This means 5/8" drywall covers the garage side of any shared wall between house and garage. This also includes shared attic spaces as seen in your picture. (covering the ceiling with 5/8" drywall would work)
Reply With Quote
  #5  
Old 5/14/08, 12:48 PM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 3,396
Default Re: Fire Separation in Garage

Quote:
Originally Posted by rnewland
That's pretty much what I have... short and sweet Thanks
Short and sweet can be good but you would better serve your client if you would explain why this is important.

The walls / ceilings between the attached garage and interior living spaces had gaps / holes / missing or substandard surface materials. These surfaces are intended to prevent vehicle fumes from entering living spaces, and to slow the spread of fire from the garage to living spaces. A qualified contractor should evaluate and make repairs as necessary so the attached garage wall and ceiling surfaces that adjoin living spaces are tightly sealed and fire rated as per standard building practices. Typically these surfaces require a one-hour fire rating.



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010

Reply With Quote
  #6  
Old 5/14/08, 1:55 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: Fire Separation in Garage

Quote:
Originally Posted by rnewland
Noted this in today's inspection. It looks like a portion of the garage to attic ceiling has been removed to make storage. From above it opens to the entire attic. Any suggestions on wording for fire separation? Thanks
2006 International Residential Code for One & Two family Dwellings
Chapter 3

SECTION R309
GARAGES AND CARPORTS
R309.1 Opening protection.
Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than 13/8 inches (35 mm) in thickness, solid or honeycomb core steel doors not less than 13/8 inches (35 mm) thick, or 20-minute fire-rated doors.

R309.1.1 Duct penetration.
Ducts in the garage and ducts penetrating the walls or ceilings separating the dwelling from the garage shall be constructed of a minimum No. 26 gage (0.48 mm) sheet steel or other approved material and shall have no openings into the garage.

R309.1.2 Other penetrations.
Penetrations through the separation required in Section R309.2 shall be protected by filling the opening around the penetrating item with approved material to resist the free passage of flame and products of combustion.

R309.2 Separation required.
The garage shall be separated from the residence and its attic area by not less than ½-inch (12.7 mm) gypsum board applied to the garage side.

Garages beneath habitable rooms shall be separated from all habitable rooms above by not less than 5/8-inch (15.9 mm) Type X gypsum board or equivalent.

Where the separation is a floor-ceiling assembly, the structure supporting the separation shall also be protected by not less than 1/2-inch (12.7 mm) gypsum board or equivalent.

Garages located less than 3 feet (914 mm) from a dwelling unit on the same lot shall be protected with not less than ½-inch (12.7 mm) gypsum board applied to the interior side of exterior walls that are within this area.

Openings in these walls shall be regulated by Section R309.1.
This provision does not apply to garage walls that are perpendicular to the adjacent dwelling unit wall.



I hope that this has been of some help.



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #7  
Old 5/14/08, 4:30 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,511
Default Re: Fire Separation in Garage

Frank and Frank, Good stuff, Much appreciated!



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #8  
Old 5/2/09, 9:54 AM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Fire Separation in Garage

This means that as long as the ceiling as drywall , 1/2 in., that should be ok?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #9  
Old 5/2/09, 10:58 AM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,486
Send a message via Yahoo to bboerner
Default Re: Fire Separation in Garage

Frank,

Is this the latest IRC version (2006)? Good stuff. Just goes to show we all really do need to become ICC certified.



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
  #10  
Old 5/2/09, 9:57 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Fire Separation in Garage

Quote:
Originally Posted by bboerner View Post
Frank,

Is this the latest IRC version (2006)? Good stuff. Just goes to show we all really do need to become ICC certified.


What are you talking about Willis??????

Buy a code book.
Reply With Quote
  #11  
Old 5/2/09, 10:16 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,768
Default Re: Fire Separation in Garage

Quote:
Originally Posted by bkelly2 View Post
[/b]

What are you talking about Willis??????

Buy a code book.
Brian, you think we could convince Contractors to buy one too?
Sure would make our jobs easier wouldn't it?
Reply With Quote
  #12  
Old 5/2/09, 10:18 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Fire Separation in Garage

Good One Marcel.
Reply With Quote
  #13  
Old 5/3/09, 5:45 PM
Steven C. Meyer Steven C. Meyer is offline
Active Poster
 
Join Date: Jan 2008
Location: California/Washington
Posts: 533
Please Note: Steven C. Meyer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fire Separation in Garage

Quote:
Originally Posted by mcyr View Post
Brian, you think we could convince Contractors to buy one too?
Sure would make our jobs easier wouldn't it?
You are assuming they can READ and COMPREHEND it.

If they could, then all houses would be "perfect", and would not require an inspection!!! If it wern't for bad builders, we would have nothing to report on.

Bless those marginal builders and remodelers AND the weekend fixer upper home owners. Makes the inspection treasure hunt more challenging and fun! It takes the "I can'r belive this" out of inspecting.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Garage fire rated wall jlybolt Interior Inspections 3 6/18/06 6:21 PM


All times are GMT -4. The time now is 4:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts