Cool First Four Point Inspection Question

Okay friends. I am new to inspecting and appreciate your help with this probably very basic question.

Today I inspected an electric service panel and found what appears to be an aluminum stranded wire connected to the neutral bus bar.

Can someone look at the attached photo top right between the red and black wires. Please tell me what you think, is this okay. Looks like aluminum?

This home was built in 1957 and also has one 30 amp fused panel in kichen.

Thanks
Attached Thumbnails
first-four-point-inspection-question-photos_071508-019-standard-e-mail-view.jpg  
Reply With Quote
  #2  
Old 7/15/08, 11:25 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: First Four Point Inspection Question

Solid Al wires on branch curcuits are the safety isssue... Al strand wires pose no safety concern. If thats what your asking.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681

Last edited by pdoane; 7/16/08 at 1:19 PM..
Reply With Quote
  #3  
Old 7/15/08, 11:33 PM
Scott Gilligan,  CMI's Avatar
Scott Gilligan, CMI Scott Gilligan,  CMI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Philadelphia, PA
Posts: 1,828
Send a message via AIM to sgilligan1 Send a message via MSN to sgilligan1 Send a message via Yahoo to sgilligan1
Default Re: First Four Point Inspection Question

Quote:
Originally Posted by jtormo
Okay friends. I am new to inspecting and appreciate your help with this probably very basic question.

Today I inspected an electric service panel and found what appears to be an aluminum stranded wire connected to the neutral bus bar.

Can someone look at the attached photo top right between the red and black wires. Please tell me what you think, is this okay. Looks like aluminum?

This home was built in 1957 and also has one 30 amp fused panel in kichen.

Thanks
You will see twisted aluminum wiring connecting the main panel to secondary distribution panels in a lot of homes built in the fifties. You find it in almost every home here in Philly. It's the branch circuit wiring that you need to watch out for. There are aluminum service entry lines, but that doesn't mean they are bad.
Reply With Quote
  #4  
Old 7/15/08, 11:46 PM
jtormo jtormo is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: Fort Lauderdale, FL
Posts: 14
Default Re: First Four Point Inspection Question

Thanks, gentelmen.

All the best!!

The new kid on the block.
Jason
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
Capital Alliance Facing Mounting Losses, Future in Question jburkeson1 Miscellaneous Discussion for Inspectors 1 2/6/07 9:59 PM
Powwer Point Question bsmith Miscellaneous Discussion for Inspectors 2 1/23/07 10:50 AM
Plumbing vent Routing Question kweiss Plumbing Inspections 7 11/1/06 9:57 PM


All times are GMT -4. The time now is 10:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts