Default Floor levelness

Anyone have a code reference for wood framed floor levelness? NAHB says 1/2 inch over 20 feet.

Last edited by kpierce; 2/9/10 at 4:24 PM..
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/10/10, 9:20 AM
Robert W. Jude's Avatar
Robert W. Jude Robert W. Jude is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Lafayette, IN
Posts: 2,074
Default Re: Floor levelness

codes are only enforced at time of construction, if you have a 100 year farmhouse with a 2" drop in the center of a 15' square room, you can call it out but i dont think you could reference a code.
Reply With Quote
  #3  
Old 2/10/10, 10:48 AM
dbelmont dbelmont is offline
Active Poster
 
Join Date: Feb 2006
Location: Barre, VT
Posts: 610
Send a message via Yahoo to dbelmont
Please Note: dbelmont is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor levelness

As HI's it shouldn't be an issue of codes. Unless you are holding yourself forth as a code inspector. I find if I don't ever reference a code then when anyone tries to use code as a defense against my opinion my argument that it is not based on code holds a lot more water.

Levelness is a subjective matter. It could be a defect depending on severity and age of the structure. A new home where you need repelling gear to cross the living room is pretty clearly a defect. Same home out 1/2 inch in 20 ft probably not unless it creates obvious situations or problems. Same thing for an old house but more leeway for slope seems reasonable.
Reply With Quote
  #4  
Old 2/10/10, 10:54 AM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Floor levelness

Some engineering guidelines allow for one inch in 20 feet. Buyers should understand that older homes settle over time. We cannot be a predictor of past or future conditions. Call it out, suggest refer, and let buyer decide.



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #5  
Old 2/10/10, 11:06 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Floor levelness

2006 IRC section and table R301.7 says deflection max is L/360 or (20x12)/360 = .67" for a 20' span.
Reply With Quote
  #6  
Old 2/10/10, 12:56 PM
Robert W. Jude's Avatar
Robert W. Jude Robert W. Jude is offline
InterNACHI Member
 
Join Date: Jul 2009
Location: Lafayette, IN
Posts: 2,074
Default Re: Floor levelness

Michael, is that for new construction?
Reply With Quote
  #7  
Old 2/10/10, 1:01 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Floor levelness

It's the IRC...it applies to any construction, new or existing, where that code has been adopted.
Reply With Quote
  #8  
Old 2/10/10, 1:29 PM
kpierce's Avatar
kpierce kpierce is offline
Active Poster
 
Join Date: Jun 2008
Location: Orting, WA
Posts: 4,609
Please Note: kpierce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor levelness

Thank you Michael. Also for not assuming I needed the information to write up a home inspection.
Reply With Quote
  #9  
Old 2/10/10, 1:37 PM
kpierce's Avatar
kpierce kpierce is offline
Active Poster
 
Join Date: Jun 2008
Location: Orting, WA
Posts: 4,609
Please Note: kpierce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor levelness

Quote:
Originally Posted by mboyett View Post
2006 IRC section and table R301.7 says deflection max is L/360 or (20x12)/360 = .67" for a 20' span.
Does the code allow for proportions? Could it also read as .335" for a 10' span and so on?
Reply With Quote
  #10  
Old 2/10/10, 2:12 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Floor levelness

Here's some snippets from the 2006 IRC. You can decipher it but, as far as I know, the answer to your question is yes.

Deflection.pdf
Reply With Quote
  #11  
Old 2/12/10, 10:03 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,466
Default Re: Floor levelness

Deflection and floor leveling are two different animals; deflection is simply the amount of deviation from a straight line when FORCE is applied..........there is no code that I am aware of that states floors have to be level and walls have to be plumb.......... matter of fact it was pointed out to me by the head of our local building department when I inspected a fast track home whose interior gable wall was out of plumb by 1 1/2 inches. I poured through the ICC code book and couldn't prove him wrong. My client was pissed at the builder and the building inspectors however he had no recourse as they both said it was within industry standards.
Reply With Quote
  #12  
Old 2/12/10, 10:09 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Floor levelness

Jeffrey...I understand and agree with your statement above, at least about deflection being different from leveling. For lack of any better direction I have used the deflection criteria before when critiquing out of level floors. Perhaps that is not an accurate thing to do.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #13  
Old 2/12/10, 10:55 AM
Jeffery L. Haynes Jeffery L. Haynes is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Concord, NC
Posts: 3,466
Default Re: Floor levelness

Here in Triad of the Carolina's the soil is so unpredictable, as a result its common to have uneven floors, especially with older homes. Unless its something out of the ordinary, I simply point out to my clients that unlevel floors can and often occur over time given the soil upon which the house was built and furthermore that they should expect that doors may need adjusting from binding and at times cracks in drywall / plaster may come and as the weather changes and / or change in the moisture content of the ground.

Because of the droughts we had here in the Carolinas for awhile followed by periods of excessive rain, I have been fortunate enough to make quite a bit of money in leveling floors the last few years......my experience shows that its often isolated to the interior piers of which many simply did not have a proper footing for the interior loads coming down on same. It can be very difficult and at times expensive to fix same. My price to go inside a crawlspace (usually a tight one at that) and attempt to jack up girders and pour additional footings runs between $2500 - $5000.00.
As you can see that can be pretty expensive and often its unnecessary unless it becomes a structural issue or a client is looking at putting in tile or slate flooring which means you have to have a stable floor system.

Most people know what they are getting however I am quick to educate first time buyers (or those new to the area) more than those who have purchased and sold multiple homes.

There is nothing wrong with exceeding the code when it comes to safety issues however the inspection industry gets a black eye when they start making recommendation for items which are outside their SOP's and safety guidelines.
If an inspector is making recommendations for a builder or seller to spend $2500 - $5000 or more in repairs..... they better be necessary.

anyway that my 2 cents.......... oopps......I see the time is getting close to my daily hot fudge sundae.... time to go......

warm regards

Jeff
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/12/10, 11:07 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Floor levelness

Quote:
Originally Posted by jhaynes View Post
There is nothing wrong with exceeding the code when it comes to safety issues however the inspection industry gets a black eye when they start making recommendation for items which are outside their SOP's and safety guidelines.
If an inspector is making recommendations for a builder or seller to spend $2500 - $5000 or more in repairs..... they better be necessary.
OK, just to be clear (I'm not sure if that is an admonishment of my previous post or inspectors in general) but when I said I used the deflection criteria when critiquing a floor levelness I meant in my mind to determine whether I should defer to a structural engineer or not. I would not and do not make any recommendations for a specific repair in such a case, that would be left to the SE. Enjoy that sundae
Reply With Quote
  #15  
Old 2/12/10, 1:53 PM
kpierce's Avatar
kpierce kpierce is offline
Active Poster
 
Join Date: Jun 2008
Location: Orting, WA
Posts: 4,609
Please Note: kpierce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Floor levelness

I wonder where the NAHB gets it's standard of 1/2 inch over 20 feet from? Thin air?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 4:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts