Default garage heating supply vent

Hello fellow Innernachians
I was just wondering what you would say about these two items in the garage aprox. 3 feet from each other. A gas fired furnace supply heat vent in the garage and a man made hole in the water heater flue.
garage-heating-supply-vent-img00027-20091106-1216.jpg

garage-heating-supply-vent-img00026-20091106-1216.jpg





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
Find an InterNACHI certified Texas Home Inspector (and anywhere else in North America)
  #2  
Old 11/8/09, 9:51 AM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,585
Default Re: garage heating supply vent

Cap the end of flue in second picture.
Reply With Quote
  #3  
Old 11/8/09, 10:13 AM
mlopezi mlopezi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Lafayette, Co
Posts: 242
Please Note: mlopezi is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage heating supply vent

Here if a furance is in a garage it must be installed 18" above the Floor.
Reply With Quote
  #4  
Old 11/8/09, 10:21 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,468
Default Re: garage heating supply vent

Quote:
Originally Posted by mlopezi View Post
Here if a furance is in a garage it must be installed 18" above the Floor.
I believe ony the source of ignition needs to be 18" above the floor.


Is that furnace a downflow?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 11/8/09, 2:21 PM
mnicholet's Avatar
mnicholet mnicholet is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 542
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage heating supply vent

Recommend a qualified HVAC technician for further investigation and or repair including installation of combustible fuel appliance(s) 18" above the floor in a garage and repair/replacement of the vent connector.

How old is the furnace? looks a little rusty. How does the burners/heat exchanger look? The register installed in the house air fan housing may reduce the air flow to the other registers through out the home.
Reply With Quote
  #6  
Old 11/8/09, 2:39 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,486
Default Re: garage heating supply vent

I know of no requirements for a furnace to be on an 18" stand in a garage. I think someone is confusing the water heater requirement with the furnace. There must be 18" from the floor to the ignition source, however.

The ductwork is a different issue. You cannot have openings to the ductwork system in the garage and the ductwork, itself, needs to have "mechanical protection" from vehicles.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #7  
Old 11/8/09, 3:54 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: garage heating supply vent

Thanks John that was what i was looking for. The other problem that i see is that since the water heater flue has two openings and there is a supply duct in the garage that it could possibly postive pressure the flue and cause back drafting on the water heater flue at the draft hood.
And also that you cannot have a supply duct in a garage for safety reasons.
the house was a 2005 age and the water heater and the furnace were installed high enough to be above the 18 inch rule. Any ignition source should be up above 18" inches in the garage. the furnace is a downdraft unit.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #8  
Old 11/8/09, 10:19 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,585
Default Re: garage heating supply vent

Gases will not vent correctly if you have two openings.
Reply With Quote
  #9  
Old 11/9/09, 12:19 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 1,893
Default Re: garage heating supply vent

Furnace lowest potential source of ignition needs to be 18 inches above the floor, which it appears to be (same rule for water heaters). Ducts inside or leading to the garage need to be metal, at least 26 ga. Not sure what you have there???

Positive pressure does not cause back drafting of appliances, negative pressure does. I believe that the opening on the water heater vent should be capped (but not positive).



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #10  
Old 11/9/09, 12:23 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: garage heating supply vent

Quote:
Originally Posted by jbushart View Post
The ductwork is a different issue. You cannot have openings to the ductwork system in the garage.
This is true. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 11/9/09, 12:43 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 1,893
Default Re: garage heating supply vent

Quote:
Originally Posted by jpope View Post
This is true. . .
Agreed. Should be blocked off.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #12  
Old 11/9/09, 1:18 AM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: garage heating supply vent

thanks for the feedback guys.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #13  
Old 11/10/09, 9:43 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,363
Default Re: garage heating supply vent

Quote:
Originally Posted by mnorthrup View Post
Hello fellow Innernachians
I was just wondering what you would say about these two items in the garage aprox. 3 feet from each other. A gas fired furnace supply heat vent in the garage and a man made hole in the water heater flue.
Attachment 33160

Attachment 33161
Mark,
I hope the following information can be of some help to you.

2009 International Residential Code
M1601.6 Independent garage HVAC systems.
Furnaces and air-handling systems that supply air to living spaces shall not supply air to or return air from a garage.

2009 International Residential Code
Part V.-Mechanical
Chapter 16 Duct Systems


SECTION M1602
RETURN AIR

M1602.1 Return air.
Return air shall be taken from inside the dwelling . Dilution of return air with outdoor air shall be permitted.

M1602.2 Prohibited sources.
Outdoor and return air for a forced-air heating or cooling system shall not be taken from the following locations:

1. Closer than 10 feet (3048 mm) to an appliance vent outlet, a vent opening from a plumbing drainage system or the discharge outlet of an exhaust fan, unless the outlet is 3 feet (914 mm) above the outside air inlet.

2. Where flammable vapors are present; or where located less than 10 feet (3048 mm) above the surface of any abutting public way or driveway; or where located at grade level by a sidewalk, street, alley or driveway.

3. A room or space, the volume of which is less than 25 percent of the entire volume served by the system. Where connected by a permanent opening having an area sized in accordance with ACCA Manual D, adjoining rooms or spaces shall be considered as a single room or space for the purpose of determining the volume of the rooms or spaces.

Exception: The minimum volume requirement shall not apply where the amount of return air taken from a room or space is less than or equal to the amount of supply air delivered to the room or space.

4. A closet, bathroom, toilet room, kitchen, garage, mechanical room, boiler room, furnace room, unconditioned attic or other dwelling unit .

5. A room or space containing a fuel-burning appliance where such room or space serves as the sole source of return air.

Needless to say that the "man made hole" in the water heater flue is discharging poisonous fumes into the garage and this is a dangerous situation/safety hazard that should be called out immediately!





Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096

Last edited by fcarrio; 11/10/09 at 9:47 AM..
Reply With Quote
Find an InterNACHI certified Texas Home Inspector (and anywhere else in North America)
  #14  
Old 11/11/09, 1:11 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 473
Default Re: garage heating supply vent

Quote:
Originally Posted by fcarrio View Post
Mark,
I hope the following information can be of some help to you.

2009 International Residential Code
M1601.6 Independent garage HVAC systems.
Furnaces and air-handling systems that supply air to living spaces shall not supply air to or return air from a garage.

2009 International Residential Code
Part V.-Mechanical
Chapter 16 Duct Systems


SECTION M1602
RETURN AIR

M1602.1 Return air.
Return air shall be taken from inside the dwelling . Dilution of return air with outdoor air shall be permitted.

M1602.2 Prohibited sources.
Outdoor and return air for a forced-air heating or cooling system shall not be taken from the following locations:

1. Closer than 10 feet (3048 mm) to an appliance vent outlet, a vent opening from a plumbing drainage system or the discharge outlet of an exhaust fan, unless the outlet is 3 feet (914 mm) above the outside air inlet.

2. Where flammable vapors are present; or where located less than 10 feet (3048 mm) above the surface of any abutting public way or driveway; or where located at grade level by a sidewalk, street, alley or driveway.

3. A room or space, the volume of which is less than 25 percent of the entire volume served by the system. Where connected by a permanent opening having an area sized in accordance with ACCA Manual D, adjoining rooms or spaces shall be considered as a single room or space for the purpose of determining the volume of the rooms or spaces.

Exception: The minimum volume requirement shall not apply where the amount of return air taken from a room or space is less than or equal to the amount of supply air delivered to the room or space.

4. A closet, bathroom, toilet room, kitchen, garage, mechanical room, boiler room, furnace room, unconditioned attic or other dwelling unit .

5. A room or space containing a fuel-burning appliance where such room or space serves as the sole source of return air.

Needless to say that the "man made hole" in the water heater flue is discharging poisonous fumes into the garage and this is a dangerous situation/safety hazard that should be called out immediately!


Thanks Frank I did call it out as a major concern and the realitor thanked me. Thanks for the info i will add it to my book of backups. So if challenged i have backup as to why i wrote it up.
Cheers.





House 2 Home LLC
503-602-1420
HomePros@House2HomeLLC.ORG
Protecting Peace of Mind One House at a Time
IAC2 Certified
IR Certified
A favorite place on Google Maps
Reply With Quote
  #15  
Old 11/11/09, 1:14 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,486
Default Re: garage heating supply vent

Quote:
Originally Posted by mnorthrup View Post
Thanks Frank I did call it out as a major concern and the realitor thanked me. Thanks for the info i will add it to my book of backups. So if challenged i have backup as to why i wrote it up.
Cheers.
Be sure your jurisdiction has adopted the 2009 IRC before you quote from it.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage door inspection procedure bgromicko General Inspection Discussion 5 8/7/09 1:47 PM
HELP! What do you call a 3 prong male plug with a cord. gromicko Electrical Inspections 5 1/9/09 1:33 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM


All times are GMT -4. The time now is 1:10 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts