Default Garage/house fire door

When a homeowner puts a Pet door in a garage to house fire door, would this not render nthe door nineffective? What best way to report this?
Reply With Quote
  #2  
Old 2/3/08, 3:15 PM
Mike D. Hazelwood's Avatar
Mike D. Hazelwood Mike D. Hazelwood is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Bakersfield, Ca
Posts: 358
Default Re: Garage/house fire door

Fire resistant door breached with a pet door. Noted at the house to garage door. Recommend to remove and replace with a 1 hour rated fire resistant door. You could recommend that the hole be covered with 3/4" plywood or 26 guage sheet metal. However I do not since it is something that could be removed and be unsightly. IMHO




Mike Hazelwood
Bakersfield, California
cal-proinspections@sbcglobal.net
www.calproinspections.com

Last edited by mhazelwood; 2/3/08 at 3:22 PM..
Reply With Quote
  #3  
Old 2/4/08, 11:44 AM
Adam Veitenheimer Adam Veitenheimer is offline
Active Poster
 
Join Date: Dec 2007
Location: Philadelphia
Posts: 210
Please Note: Adam Veitenheimer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage/house fire door

yea i agree, it completly changes the rating and effectivness of the door
Reply With Quote
  #4  
Old 2/4/08, 11:52 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: Garage/house fire door

Same problem with most pull down ladders in the garage celling

rlb
Reply With Quote
  #5  
Old 2/4/08, 11:58 AM
Ed Figueroa Ed Figueroa is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Bartlett, TN
Posts: 34
Default Re: Garage/house fire door

Actually, depends where you are at. I had the same situation with window garage doors. I spoke to county code enforcers and they told me that they allow it. It was not a safety issue. I had the same hard ache, but I can't put it as a discrepancy. Most new constructions are built with glass window doors here. Check first with your local code enforcement agency!



Ed Figueroa
Spotlight Home Inspection Service, LLC
Bartlett, TN
(901) 569-4997
Reply With Quote
  #6  
Old 2/4/08, 12:10 PM
Captain Beefheart Captain Beefheart is offline
New User
 
Join Date: Nov 2007
Location: Space
Posts: 31
Please Note: Captain Beefheart is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage/house fire door


Check your facts; garage to house door needs to be 1 3/8 inch solid wood, 1 3/8 inch steel or 20-minute fire-rated. Glass is permitted as long as it meets the fire rating; IE, large pieces of glass (unless fire rated) is unacceptable.

Beef
Reply With Quote
  #7  
Old 2/4/08, 12:24 PM
Ed Figueroa Ed Figueroa is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Bartlett, TN
Posts: 34
Default Re: Garage/house fire door

Actually, I did check with the code enforcement office. The said they don't even check to see if so. I don't doubt that it should be fire rated. The fact I'm saying is that they don't check and don't care here in my county. I called twice and spoke to 2 of the code inspectors.



Ed Figueroa
Spotlight Home Inspection Service, LLC
Bartlett, TN
(901) 569-4997
Reply With Quote
  #8  
Old 2/4/08, 1:26 PM
Captain Beefheart Captain Beefheart is offline
New User
 
Join Date: Nov 2007
Location: Space
Posts: 31
Please Note: Captain Beefheart is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage/house fire door

Ed,

Wasn't talking about your facts; talking about a 1 hour fire door.

Beef
Reply With Quote
  #9  
Old 2/4/08, 6:28 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,349
Default Re: Garage/house fire door

Quote:
Originally Posted by Steven C. Meyer
When a homeowner puts a Pet door in a garage to house fire door, would this not render nthe door nineffective? What best way to report this?

A cat door has been installed in the door between the attached garage and the house.

This negates the fire resistant rating of the door and breaches the fire resistant rating between the house and garage.

This is a safety hazard and needs to be repaired.

I am not the best with words, but that should work.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #10  
Old 2/4/08, 7:23 PM
T.J. Christopher T.J. Christopher is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Torrington, WY
Posts: 187
Default Re: Garage/house fire door

Don't garage/house walk doors on attached garages have to have an auto-closer on them to keep any combustible fumes out also?
Reply With Quote
  #11  
Old 2/4/08, 7:34 PM
Captain Beefheart Captain Beefheart is offline
New User
 
Join Date: Nov 2007
Location: Space
Posts: 31
Please Note: Captain Beefheart is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage/house fire door

Quote:
Originally Posted by tchristopher
Don't garage/house walk doors on attached garages have to have an auto-closer on them to keep any combustible fumes out also?
No requirement in the IRC.


Beef
Reply With Quote
  #12  
Old 2/4/08, 7:34 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,349
Default Re: Garage/house fire door

Highly recommended by NFPA and the IBC, check with local jurisdiction if required in your area.

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #13  
Old 2/4/08, 8:12 PM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 3,968
Default Re: Garage/house fire door

Quote:
Originally Posted by Steven C. Meyer
When a homeowner puts a Pet door in a garage to house fire door, would this not render nthe door nineffective? What best way to report this?
Your state has adopted the ICC codes.

Therefore this is not only considered a "safety hazard" but is also considered a code violation.

Since this door poses a "Safety Hazard" it should be removed and replaced with a solid door.

2006 International Residential Code for One and Two-Family Dwellings
Part III - Building Planning and Construction
Chapter 3, Building Planning
Section R309 Garages and Carports
SECTION R309
GARAGES AND CARPORTS

R309.1 Opening protection.
Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Other openings between the garage and residence shall be equipped with solid wood doors not less than 13/8 inches (35 mm) in thickness, solid orhoneycomb core steel doors not less than 13/8 inches (35 mm) thick, or 20-minute fire-rated doors.

2006 International Building Code
Chapter 4, Special Detailed Requirements Based on the Use and Occupancy
Section 406 Motor Vehicle Related Occupancies
406.1 Private Garages and Carports.

406.1.4 Separation
1. The private garage shall be separated from the dwelling unit and its attic area by means of a minimum ˝-inch (12.7 mm) gypsum board applied to the garage side.

Garages beneath habitable rooms shall be separated from all habitable rooms above by not less than a 5/8-inch Type X gypsum board or equivalent.

Door openings between a private garage and the dwelling unit shall be equipped with either solid wood doors or solid or honeycomb core steel doors not less than 13/8 inches (34.9 mm) thick, or doors in compliance with Section 715.4.3.
Openings from a private garage directly into a room used for sleeping purposes shall not be permitted. Doors shall be self-closing and self-latching.



ICC makes every effort to provide current, accurate code adoption information, but in some cases jurisdictions do not notify ICC of adoptions, amendments or changes to their codes. To ensure you have accurate information, please contact the jurisdiction directly.

Click here to print Adoption List"Washington Statewide


2006 International Building Code
2006 International Fire Code
International Fuel Gas Code
2006 International Mechanical Code
2006 International Residential Code
Washington Jurisdictions


Arlington
2003 International Building Code
2003 International Energy Conservation Code
2003 International Existing Building Code
2003 International Fire Code
2003 International Fuel Gas Code
2003 International Mechanical Code
2003 ICC Performance Code
2003 International Property Maintenance Code
2003 International Residential Code
Battle Ground
2003 International Building Code
2003 International Energy Conservation Code
2003 International Existing Building Code
2003 International Fire Code
2003 International Fuel Gas Code
2003 International Mechanical Code
2003 International Property Maintenance Code
2003 International Residential Code
Bellingham
2003 International Building Code
2003 International Existing Building Code
2003 International Fire Code
2003 International Fuel Gas Code
2003 International Mechanical Code
2003 International Residential Code
Cheney
2003 International Building Code
2003 International Existing Building Code
2003 International Fire Code
2003 International Fuel Gas Code
2003 International Mechanical Code
2003 International Property Maintenance Code
2003 International Residential Code
Edgewood
2003 International Building Code
2003 International Fire Code
2003 International Mechanical Code
2003 International Property Maintenance Code
2003 International Residential Code
Federal Way
2003 International Building Code
2003 International Existing Building Code
2003 International Fire Code
2003 International Fuel Gas Code
2003 International Mechanical Code
2003 International Property Maintenance Code
2003 International Residential Code
Issaquah
2003 International Building Code
2003 International Fire Code
2003 International Fuel Gas Code
2003 International Mechanical Code
2003 International Residential Code
Kennewick
2003 International Building Code
2003 International Fire Code
2003 International Fuel Gas Code
2003 International Mechanical Code
2003 International Residential Code
Lacey
International Building Code
International Existing Building Code
International Fire Code
International Fuel Gas Code
International Mechanical Code
International Residential Code
Lynnwood
2003 International Building Code
2003 International Fire Code
2003 International Fuel Gas Code
2003 International Mechanical Code
Montlake Terrace
2003 International Building Code
2003 International Existing Building Code
2003 International Fire Code
2003 International Mechanical Code
2003 International Performance Code Code
2003 International Property Maintenance Code
2003 International Residential Code
Orting
2003 International Energy Conservation Code
2003 International Existing Building Code
2003 International Fuel Gas Code
2003 International Plumbing Code
2003 International Private Sewage Disposal Code
2003 International Property Maintenance Code
Selah
2003 International Energy Conservation Code
2003 International Existing Building Code
2003 International Property Maintenance Code
Yakima County
International Urban-Wildland Interface Code



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member

Last edited by fcarrio; 2/4/08 at 8:16 PM..
Reply With Quote
  #14  
Old 2/4/08, 11:33 PM
Mike D. Hazelwood's Avatar
Mike D. Hazelwood Mike D. Hazelwood is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Bakersfield, Ca
Posts: 358
Default Re: Garage/house fire door

Quote:
Originally Posted by Captain Beefheart
Wasn't talking about your facts; talking about a 1 hour fire door.

Beef


Beef
A 20 Minute door is a minimum standard. I prefer to recommend the 1 Hr rated door when a fire door needs to be replaced. In fact 75% of the fire doors here in my area are a 1 hr. door and when you see a 20 minute door it kind of suprises you.




Mike Hazelwood
Bakersfield, California
cal-proinspections@sbcglobal.net
www.calproinspections.com
Reply With Quote
  #15  
Old 2/5/08, 7:13 AM
Captain Beefheart Captain Beefheart is offline
New User
 
Join Date: Nov 2007
Location: Space
Posts: 31
Please Note: Captain Beefheart is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage/house fire door

If that’s he case, I hope your reports reads something like----

‘Although only a 20 minute rated door is required, I personally recommend a 1 hour rated door. This extra fire rating will protect your family far greater the minimum required.’

When you recommend replacement of the roof shingles, do you also recommend the seller install Timberline 35 year shingles?


Beef
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Escape, Fire & Smoke Alarms badair Interior 14 1/28/08 8:21 AM
Service door Fire Rating jmichael Interior 2 8/13/07 11:45 PM


All times are GMT -4. The time now is 9:30 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts