  #1  
Old 12/29/10, 12:33 PM
LeRoy D. Holm's Avatar
LeRoy D. Holm LeRoy D. Holm is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Decorah, IA
Posts: 235
Default Header replacement

I did an inspection on a home and the garage has a header that is sagging and should be replaced. The seller plans to replace the header with a new header. The buyer claims that the only fix is to have the seller install new girder truss with valley and gables to make it work.

I am getting calls from both the seller and buyer and my suggestion is call a structural engineer. I do not have the answer and would like some input I feel that the buyer is asking for more than needs to be expected from the seller. I am surprised the seller has not just cancelled the transaction.
Attached Thumbnails
header-replacement-008.jpg  
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/29/10, 12:59 PM
Robert W. Jude's Avatar
Robert W. Jude Robert W. Jude is online now
InterNACHI Member
 
Join Date: Jul 2009
Location: Lafayette, IN
Posts: 2,081
Default Re: Header replacement

You cant size the lumber for the span. only an engineer or architect can. If the seller would have done that before this came up, then he could have done anything he wanted to. how much do you think it sags if you ran a string from one side to the other?
Reply With Quote
  #3  
Old 12/30/10, 5:45 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Header replacement

LeRoy, this is just my opinion but I would just note your finding (the sagging header) take a few "Good" pictures and then recommend further evaluation by a licensed contractor or engineer and move on as you have done all you need to as the Home Inspector. There is no need for you to get to technically exhaustive as that just opens up unnecessary cans of worms for you.




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #4  
Old 12/30/10, 6:20 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,783
Default Re: Header replacement

This wood be an easy fix for me, but I agree as said, note the problem and defer to a qualified Contractor to repair.
Let the client negotiate with the seller on the monetary values.
Reply With Quote
  #5  
Old 12/30/10, 8:27 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Header replacement

Marcel, that would be a sweet little job wouldn't it.
What do you think, double 9'' LVLs ?



Russell Inspection Services
New Hampshire state license # 57
Level I Thermographer, ITC
Certified Building Science Thermographer, ITC
Certified Building Analyst, BPI
Certified Commercial Inspector, ITA
Certified Septic Evaluator, GSDI #148

www.newenglandthermalimaging.com
www.russellinspectionservices.com
www.nhsepticinspection.com
Reply With Quote
  #6  
Old 12/30/10, 8:42 PM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is online now
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,547
Default Re: Header replacement

Quote:
Originally Posted by rjude View Post
You cant size the lumber for the span. only an engineer or architect can. If the seller would have done that before this came up, then he could have done anything he wanted to. how much do you think it sags if you ran a string from one side to the other?
Wrong! The IRC has span tables that can be applied by a builder without the need of an architect or engineer as long as the dwelling is one-or-two family and under 3 stories.



"A state of war only serves as an excuse for domestic tyranny." ~ Alexander Solzhenitsyn



Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"
Reply With Quote
  #7  
Old 12/30/10, 8:50 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,783
Default Re: Header replacement

That would be more than adequate Pete for the roof load on what appears to be 8' doors.

And what is that other beam under the trusses?
Reply With Quote
  #8  
Old 12/30/10, 8:54 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,783
Default Re: Header replacement

Joe is right, you can order what you need directly from the lumber yard.
Tell them the span and voila, they will order what you need for the roof or floor loads.

LVL beam charts and lumber beam charts are also readily available to all contractors that can read them.
Reply With Quote
  #9  
Old 12/30/10, 9:08 PM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Header replacement

Quote:
Originally Posted by mcyr View Post
That would be more than adequate Pete for the roof load on what appears to be 8' doors.

And what is that other beam under the trusses?
Almost looks like it was originally framed for larger doors??



Russell Inspection Services
New Hampshire state license # 57
Level I Thermographer, ITC
Certified Building Science Thermographer, ITC
Certified Building Analyst, BPI
Certified Commercial Inspector, ITA
Certified Septic Evaluator, GSDI #148

www.newenglandthermalimaging.com
www.russellinspectionservices.com
www.nhsepticinspection.com
Reply With Quote
  #10  
Old 12/30/10, 9:19 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,783
Default Re: Header replacement

Pete, look where that beam is. It is above that sloppy hanger closer set up. I brightened up the picture a bit.

Doubled up vertically and roof trusses above, so don't know why it is there. doesn't make any sense. They should have used that for the door header.
header-replacement-008.jpg
Reply With Quote
  #11  
Old 12/30/10, 10:25 PM
LeRoy D. Holm's Avatar
LeRoy D. Holm LeRoy D. Holm is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Decorah, IA
Posts: 235
Default Re: Header replacement

Nice job guys thanks for the input,
Reply With Quote
  #12  
Old 12/31/10, 6:07 AM
Peter C. Russell's Avatar
Peter C. Russell Peter C. Russell is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Alton Bay NH
Posts: 3,998
Default Re: Header replacement

Quote:
Originally Posted by mcyr View Post
Pete, look where that beam is. It is above that sloppy hanger closer set up. I brightened up the picture a bit.

Doubled up vertically and roof trusses above, so don't know why it is there. doesn't make any sense. They should have used that for the door header.
Attachment 40936
I see it now, I don't know what they were thinking. Awful tall ceilings in that garage too.



Russell Inspection Services
New Hampshire state license # 57
Level I Thermographer, ITC
Certified Building Science Thermographer, ITC
Certified Building Analyst, BPI
Certified Commercial Inspector, ITA
Certified Septic Evaluator, GSDI #148

www.newenglandthermalimaging.com
www.russellinspectionservices.com
www.nhsepticinspection.com
Reply With Quote
  #13  
Old 12/31/10, 3:36 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,783
Default Re: Header replacement

LeRoy, can you shed some light on that beam on what it's purpose was?

And Happy New Year to you also.
Reply With Quote
Need a home inspection in Missouri? Check out InterNACHI's listing of Missouri certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/31/10, 7:42 PM
LeRoy D. Holm's Avatar
LeRoy D. Holm LeRoy D. Holm is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Decorah, IA
Posts: 235
Default Re: Header replacement

The beam is to support the roof on the front of the garage and whne it gets full of snow it sags
Reply With Quote
  #15  
Old 12/31/10, 7:47 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,783
Default Re: Header replacement

But I can see that those are roof trusses above. Trusses don't sag, they fail.
Any other explaination? Curious as hell.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
A header in a recently constructed house tpino Interior Inspections 8 9/15/10 4:21 PM
Window header trim flashing jfrederick Exterior Inspections 0 6/24/10 8:29 AM
2x4 engineered floor joists holding deck header bking Structural Inspections 1 1/27/10 9:10 PM
Possibly Overloaded Garage Door Header pdickerson Structural Inspections 25 8/3/08 2:26 AM


All times are GMT -4. The time now is 12:48 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts