Default help from the pool experts please

I inspected a pool today and this was the junction box for a pool light. There should be a bonding conductor here right?
Also the pool light is centered at 18" below the water line. Is the >18" requirement to the top of the light?
Attached Thumbnails
help-pool-experts-please-cimg1858a.jpg  

Last edited by bracine; 1/7/07 at 7:11 PM..
Reply With Quote
  #2  
Old 1/7/07, 7:49 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: help from the pool experts please

No bonding wire is necessary, only the equipment grounding conductor, which is present.

18 inches to the top edge of the light - 2002 NEC 680.23(A)(5)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/7/07, 7:51 PM
Brett Racine's Avatar
Brett Racine Brett Racine is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: St. Petersburg, FL
Posts: 60
Default Re: help from the pool experts please

Thanks Jeff!
Reply With Quote
  #4  
Old 1/7/07, 8:03 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,852
Default Re: help from the pool experts please

Did the GFCI work?
Reply With Quote
  #5  
Old 1/7/07, 9:16 PM
Brett Racine's Avatar
Brett Racine Brett Racine is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: St. Petersburg, FL
Posts: 60
Default Re: help from the pool experts please

Quote:
Originally Posted by bkelly2
Did the GFCI work?
That was my next question. I saw that the light was supposed to be GFCI protected, but where will I find it to test it?
Reply With Quote
  #6  
Old 1/7/07, 9:25 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,852
Default Re: help from the pool experts please

Could be near the pool equipment or in a sub panel or panel.

If you do not trip it yourself and/or can not find where to trip the GFCI, point that out in your report.

Just guessing, but I would bet the GFCI used to be in that J-Box.
Reply With Quote
  #7  
Old 1/7/07, 9:30 PM
Brett Racine's Avatar
Brett Racine Brett Racine is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: St. Petersburg, FL
Posts: 60
Default Re: help from the pool experts please

Thanks Brian.
No sign of it near the equipment. I'll take your advice on the report.
Reply With Quote
  #8  
Old 1/7/07, 10:18 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: help from the pool experts please

BR,

You may find this useful:

http://www.mikeholt.com/files/PDF/Pooldownload.pdf

680 pool starts on page 16



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 1/7/07 at 10:21 PM..
Reply With Quote
  #9  
Old 1/8/07, 4:12 AM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 367
Default Re: help from the pool experts please

The plastic box and conduit may not require it...but what about the metal chain link fencing? if thats what it is in the picture (not clear enough)...that would require bonding, correct?



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #10  
Old 1/8/07, 6:00 AM
Brett Racine's Avatar
Brett Racine Brett Racine is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: St. Petersburg, FL
Posts: 60
Default Re: help from the pool experts please

That's a great document Barry. I had downloaded it a few days before the inspection.

No chain link fence. The pool was enclosed. Ten years old.
Reply With Quote
  #11  
Old 1/8/07, 2:37 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: help from the pool experts please

The pool cage which is aluminum would require bonding, though.

You had a 110v pool light on a house ten years old?



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #12  
Old 1/8/07, 2:46 PM
Brett Racine's Avatar
Brett Racine Brett Racine is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: St. Petersburg, FL
Posts: 60
Default Re: help from the pool experts please

Quote:
Originally Posted by bwiley
The pool cage which is aluminum would require bonding, though.

You had a 110v pool light on a house ten years old?
Correct.
You would have expected 15V at 10 years?
Reply With Quote
  #13  
Old 1/8/07, 2:58 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: help from the pool experts please

I have not seen a 110 volt pool light on a pool less than 25 years old in this area. Most are 12 or 24 volt.

I recommend replacement of 110 volt pool lights with low voltage models for safety.

But then, I'm a pain in the ....



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #14  
Old 1/8/07, 3:31 PM
Brett Racine's Avatar
Brett Racine Brett Racine is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: St. Petersburg, FL
Posts: 60
Default Re: help from the pool experts please

Quote:
Originally Posted by bwiley
I have not seen a 110 volt pool light on a pool less than 25 years old in this area. Most are 12 or 24 volt.

I recommend replacement of 110 volt pool lights with low voltage models for safety.

But then, I'm a pain in the ....
Blaine, there is no doubt based on the photo of the J-box that it's a 110V light right? Do you think they were using up old stock when they put in this pool. It's in a subdivision where all of the homes are 12 years old or less.
Reply With Quote
  #15  
Old 1/8/07, 6:55 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,852
Default Re: help from the pool experts please

Quote:
Originally Posted by bwiley
I have not seen a 110 volt pool light on a pool less than 25 years old in this area. Most are 12 or 24 volt.

I recommend replacement of 110 volt pool lights with low voltage models for safety.

But then, I'm a pain in the ....
Nice one Blaine

Pool light transformers
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pool Inspection Class jcartwright Ancillary Inspection Services & Additional Topics 1 9/24/07 2:08 PM
It's time for Professional Pool Inspections Revel L. Thom Ancillary Inspection Services & Additional Topics 13 7/26/07 11:50 AM
Pentair Water Pool Gas Heater Recall Gary Reecher Inspecting HVAC Systems 0 1/4/07 9:15 PM
Pool Inspector in Palos Hts, IL alpha1 Ancillary Inspection Services & Additional Topics 8 7/10/06 8:02 PM


All times are GMT -4. The time now is 12:26 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts