I inspected a pool today and this was the junction box for a pool light. There should be a bonding conductor here right?
Also the pool light is centered at 18" below the water line. Is the >18" requirement to the top of the light? Brett Racine http://www.gulftobayinspection.com/ http://www.gulftobayinspection.com/F...ome_Inspe.html Last edited by bracine; 1/7/07 at 7:11 PM.. |
|
#2
|
||||
|
||||
|
No bonding wire is necessary, only the equipment grounding conductor, which is present.
18 inches to the top edge of the light - 2002 NEC 680.23(A)(5) IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Thanks Jeff!
|
|
#4
|
|||
|
|||
|
Did the GFCI work?
"Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#5
|
||||
|
||||
|
Quote:
|
|
#6
|
|||
|
|||
|
Could be near the pool equipment or in a sub panel or panel.
If you do not trip it yourself and/or can not find where to trip the GFCI, point that out in your report. Just guessing, but I would bet the GFCI used to be in that J-Box. "Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#7
|
||||
|
||||
|
Thanks Brian.
No sign of it near the equipment. I'll take your advice on the report. |
|
#8
|
||||
|
||||
|
BR,
You may find this useful: http://www.mikeholt.com/files/PDF/Pooldownload.pdf 680 pool starts on page 16 badair ADAIR INSPECTION 972-487-5634 Residential-Commercial-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes...accept the good Last edited by badair; 1/7/07 at 10:21 PM.. |
|
#9
|
||||
|
||||
|
The plastic box and conduit may not require it...but what about the metal chain link fencing? if thats what it is in the picture (not clear enough)...that would require bonding, correct?
Darrell Hadler CMI Five Star Home Inspections Medicine Hat, AB. Canada NACHI# 04111082 Cell phone# (403)502-3593 Inspected once . . . inspected right!
|
|
#10
|
||||
|
||||
|
That's a great document Barry. I had downloaded it a few days before the inspection.
No chain link fence. The pool was enclosed. Ten years old. |
|
#11
|
|||
|
|||
|
The pool cage which is aluminum would require bonding, though.
You had a 110v pool light on a house ten years old? |
|
#12
|
||||
|
||||
|
Quote:
You would have expected 15V at 10 years? |
|
#13
|
|||
|
|||
|
I have not seen a 110 volt pool light on a pool less than 25 years old in this area. Most are 12 or 24 volt.
I recommend replacement of 110 volt pool lights with low voltage models for safety. But then, I'm a pain in the .... |
|
#14
|
||||
|
||||
|
Quote:
|
|
#15
|
|||
|
|||
|
Quote:
Pool light transformers "Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Pool Inspection Class | jcartwright | Ancillary Services & Additional Topics | 1 | 9/24/07 2:08 PM |
| It's time for Professional Pool Inspections | Revel L. Thom | Ancillary Services & Additional Topics | 13 | 7/26/07 11:50 AM |
| Pentair Water Pool Gas Heater Recall | Gary Reecher | HVAC | 0 | 1/4/07 9:15 PM |
| Pool Inspector in Palos Hts, IL | alpha1 | Ancillary Services & Additional Topics | 8 | 7/10/06 8:02 PM |