Default Hot water heater question

I inspected a relatively new condo with the hot water tpr valve drain pipe routed up through the ceiling?!? Is this a new exception to the code in Georgia?
Attached Thumbnails
hot-water-heater-question-tpv-valve-drain-routed-upwards0001.jpg  
Reply With Quote
  #2  
Old 6/5/06, 12:21 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,747
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Hot water heater question

Quote:
Originally Posted by mgeddie
I inspected a relatively new condo with the hot water tpr valve drain pipe routed up through the ceiling?!? Is this a new exception to the code in Georgia?
No it's just plain old wrong

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 6/5/06, 12:33 PM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,394
Default Re: Hot water heater question

As Gerry said, it's wrong. However, it it cannot be easily plumbed to the exterior and within six-inches of grade, it should be removed and a Watts 210 gas shut-off valve installed, which serves the same purpose. If this is done, the plumber should confirm that there is a pressure relief valve elsewhere on the system. PS That's my understanding, but I'm not a plumber.
Reply With Quote
  #4  
Old 6/5/06, 3:16 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Hot water heater question

Keith,

If I am not mistaken arn't the Watts 210 Value for Gas Water Heaters?

The one shown is Electric...is it not?

P2803.6.1 ( quoting only the last portion ) The discharge pipe shall be installed so as to drain by gravity flow and shall terminate atmospherically not more than 6 inches above the floor.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 6/5/06 at 3:24 PM..
Reply With Quote
  #5  
Old 6/6/06, 9:21 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Hot water heater question

Quote:
Originally Posted by kswift
it should be removed and a Watts 210 gas shut-off valve installed, which serves the same purpose. If this is done, the plumber should confirm that there is a pressure relief valve elsewhere on the system.
Yes.
And no.
The Watts 210 gas shut-off valve does not serve the same purpose as the TPR valve, which is why, as you did note, a pressure relief valve still needs to be installed. However, a temperature relief valve also needs to be installed, so why not just make it a TPR valve?

Unfortunately, every time I find a W210, I find that there is no TPR valve. I quite often have to print out the W210 instructions from the Watts site to give to my Clients to give to the plumber who says that only a W210 is needed.

All the W210 does is shut off the gas, with the theory being that if there is no gas, then there can be no flame to make the temperature go higher and higher, so the water will start cooling down. However, it does not cool down instantaneously, which is why the TPR valve is also needed.

There's a reason why one is called a "shut-off" valve and the other is called a "relief" or "release" valve. They are inherently different and need to be married in order to work together.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 6/6/06, 9:37 AM
jbowman's Avatar
jbowman jbowman is offline
Active Poster
 
Join Date: Dec 2003
Location: ROME, PA
Posts: 2,270
Please Note: jbowman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water heater question

Quote:
Hot water heater question
Why would you heat hot water?



http://hisearch.org has over 1,000 hits per month and climbing. Currently ranked #1 in many search engines for determing the age of HVAC equipment. Check it out at http://hisearch.org/hvac.aspx Feel free to bookmark and use our site at any time.

List your business in our Home Inspector Registry with a link exchange. Check out your state now at http://hisearch.org/homeinspectorregistry.aspx Are you listed???
Reply With Quote
  #7  
Old 6/6/06, 9:50 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Hot water heater question

Quote:
Originally Posted by jbowman
Why would you heat hot water?
Because it is inherently more efficient.

For example, cold water comes into my place at about 68°F. When it hits my hot water heater, it causes the thermostat to come on and heat the cold water to about 120°F.

However, if the temperature of the water in my tank hot water heater falls below 115°F, then the thermostat comes on and heats that 115°F hot water back up to 120°F. So you are, indeed, heating hot water quite often. In fact, you'd find that you heat hot water far more often than you heat cold water.

I can use a mere one gallon of hot water at the kitchen sink and cause the hot water heater to start up. This is why hot water heaters with tanks are so inefficient and why tankless water heaters are making significant inroads into the hot water heating industry. Once everyone has been converted to tankless water heaters, then we truly won't have hot water heaters anymore, just water heaters. Until then, either "water heater" or "hot water heater" is correct.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #8  
Old 6/6/06, 11:39 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Hot water heater question

Actually Russ, in areas where the Watts 210 valve is allowed, a pressure relief valve (not a TPR valve) is required in conjunction with the Watts 210.

Paul, you are correct. The Watts 210 works on the gas supply only, and they are not made for electric water heaters.

The picture above is just wrong, plain and simple.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 6/6/06, 12:14 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Hot water heater question

Quote:
Originally Posted by jpope
Actually Russ, in areas where the Watts 210 valve is allowed, a pressure relief valve (not a TPR valve) is required in conjunction with the Watts 210.
True. Thanks for clarifying my post.

I should have stated that the temperature of the water can still continue rising some after the gas has been shut off due to the heat of the metal, so common sense would seem to say that a temperature relief valve should be installed along with the pressure release valve. Therefore, why not just install a TPR valve?



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 6/6/06, 2:48 PM
cradan cradan is offline
Active Poster
 
Join Date: Aug 2003
Location: Minooka, IL
Posts: 239
Please Note: cradan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot water heater question

You guys are killing me. Here in Illinois, items which in your opinion are "unsafe" or "not functioning" are required to be reported-on using the phrase, "SIGNIFICANTLY DEFICIENT." I'm thinking about going to our State's Home Inspector Advisory Board to suggest that we replace that language in our reports with "JUST PLAIN WRONG."

I'm actually not kidding...consider what we come-across in the field. Many times, we find items that are...strange...questionable...could be done better...marginal, etc. On occasion, we obviously find totally unsafe or other obviously fubared items. For such occasions, don't you think "JUST PLAIN WRONG" carries more impact than "Significantly Deficient?"

Reply With Quote
  #11  
Old 6/6/06, 3:25 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Hot water heater question

There could be a whole new set of categories:

Just plain wrong.
Just plain dumb. Dumb, dumb, dumb.
A fire waiting to happen.
Ingenious but unsafe.




  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #12  
Old 6/7/06, 1:34 AM
rarmstrong1 rarmstrong1 is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Sandy Springs, GA
Posts: 33
Default Re: Hot water heater question

Actually, in GA the TPR drain can go up. A thermal expansion device must be installed on the cold water side and there must be a provision for a low point drain to drain the trapped portion of the discharge pipe.
Ga St Amendment to the SPC 504
Reply With Quote
  #13  
Old 6/7/06, 1:45 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Hot water heater question

Quote:
Originally Posted by rarmstrong1
Actually, in GA the TPR drain can go up.
I would like to see how that is worded. Can you quote the reference here?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #14  
Old 6/7/06, 9:24 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Hot water heater question

Robert,

I do not believe that a "TRAP" is ever allowed in the TPR drain line as listed clearly by the IRC.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 6/7/06, 1:35 PM
Matt Geddie Matt Geddie is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Acworth, GA
Posts: 4
Default Re: Hot water heater question

Well, I found the amendment. I guess I need to get up to speed on Georgia's amendments:


SECTION 504


SAFETY DEVICES


*Delete Section 504.6.1 and substitute the following:


504.6.1 Discharge.
The relief valve shall discharge full size to a safe place of disposal such as a concrete floor, outside the building, an indirect waste receptor, or other approved location. The discharge shall terminate in a manner that does not cause injury to occupants in the immediate area or structural damage to the building. The discharge pipe shall not be trapped. When the relief valve discharge piping goes upward a thermal expansion control device shall be installed on the cold water distribution or service pipe in accordance with Section 607.3.2 (GA.


Ga Standard Plumbing Code (International Plumbing Code) Amendments 2002


Amendments). Provisions shall be made at the low point to drain the trapped portion of the discharge pipe.
(Effective January 1, 2002)

Learning more every day.

Matt
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solar water heating + electric water heater Todd M. Soper Plumbing 20 5/30/07 7:31 AM
Hot Water Heater djohnson6 Plumbing 12 12/28/06 10:18 PM
Venting an oil-fired water heater mh718 HVAC 3 11/16/06 10:36 AM
Hot water heater question carolinainspector Plumbing 9 6/19/06 2:59 PM


All times are GMT -4. The time now is 1:49 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts