InterNACHI member Steve Beverlin brought to our attention typo in our "25 Standards" course, which we have corrected, but after Ben and Nick looked up the details in the 2009 IRC, we're somewhat perplexed and need your input. We could be looking at an IRC typo, for which I'm pretty sure you don't get any free books...

Here's the confusing section in Chapter 13 (p.447):
Section M1305: Appliance Access
M1305.1.3. Attics containing appliances shall be provided with an opening and a clear and unobstructed passageway large enough to allow removal of the largest appliance, but not less than 30 inches high and 22 inches wide, and not more than 20 feet long measured along the centerline of the passageway from the opening to the appliance. The passageway shall have continuous solid flooring in accordance with Chapter 5 not less than 24 inches wide. A level service space at least 30 inches deep and 30 inches wide shall be present along all sides of the appliance where access is required. The clear access opening dimensions shall be a minimum of 20 inches by 30 inches, and large enough to allow removal of the largest appliance.

We've decided to throw the debate open to our members. Do you think the IRC's description is a typo? Do the two bolded passages contradict each other?

Thanks for playing our game!



Cheers,
Kate
Crimea River
Editor-in-Chief

kate@internachi.org
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/12/10, 6:31 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,946
Default Re: Is the IRC wrong?

As I read it, one dimension is regarding the path to the appliance while the other regards the opening in the ceiling.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.
Reply With Quote
  #3  
Old 11/12/10, 6:50 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,171
Default Re: Is the IRC wrong?

Quote:
Originally Posted by jbushart View Post
As I read it, one dimension is regarding the path to the appliance while the other regards the opening in the ceiling.
I read it the same way. 30" x 22" for the pathway, 30" x 20" for the (ceiling) opening.
Reply With Quote
  #4  
Old 11/12/10, 6:59 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,012
Default Re: Is the IRC wrong?

Should not the dimensions be the same?
Attics containing appliances shall be provided with an opening 30 by 22
. The clear access opening dimensions shall be a minimum of 20 inches by 30 inches
That is how I read it.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #5  
Old 11/12/10, 7:01 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,612
Default Re: Is the IRC wrong?

I sent Steve the books for helping regardless.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #6  
Old 11/12/10, 7:04 PM
Kate Tarasenko's Avatar
Kate Tarasenko Kate Tarasenko is offline
InterNACHI Member
 
Join Date: Jul 2009
Posts: 145
Default Re: Is the IRC wrong?

OK -- I see what you're saying, although I would have added the bolded bits for clarity:

Attics containing appliances shall be provided with an opening and a clear and unobstructed passageway, with the passageway large enough to allow removal of the largest appliance, but not less than 30 inches high and 22 inches wide, and not more than 20 feet long measured along the centerline of the passageway from the opening to the appliance.

It looks like I need to change our numbers in the course back, then.

Thanks for your input!



Cheers,
Kate
Crimea River
Editor-in-Chief

kate@internachi.org
Reply With Quote
  #7  
Old 11/12/10, 7:15 PM
Kate Tarasenko's Avatar
Kate Tarasenko Kate Tarasenko is offline
InterNACHI Member
 
Join Date: Jul 2009
Posts: 145
Default Re: Is the IRC wrong?

Robert Young wrote:

Should not the dimensions be the same?
Attics containing appliances shall be provided with an opening 30 by 22. The clear access opening dimensions shall be a minimum of 20 inches by 30 inches
That is how I read it.

That's how Steve (and we) read it, too, but I do see now that the first set of dimensions given is related to the passageway, while the second set specifically mentions the attic access itself.

Again, were I the editor for the IRC, that passage would have been written more clearly, but I don't think I'd be interested in that job....

P.S. Apologies to Robert and all Canucks for deleting the metric measurements from the quoted IRC passage. Just trying to be brief. Anyway, you guys'll come around to our standard system eventually...



Cheers,
Kate
Crimea River
Editor-in-Chief

kate@internachi.org

Last edited by ktarasenko; 11/12/10 at 7:19 PM..
Reply With Quote
  #8  
Old 11/12/10, 7:22 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,946
Default Re: Is the IRC wrong?

Quote:
Originally Posted by ktarasenko View Post
Robert Young wrote:

Should not the dimensions be the same?
Attics containing appliances shall be provided with an opening 30 by 22. The clear access opening dimensions shall be a minimum of 20 inches by 30 inches
That is how I read it.

That's how Steve (and we) read it, too, but I do see now that the first set of dimensions given is related to the passageway, while the second set specifically mentions the attic access itself.

Again, were I the editor for the IRC, that passage would have been written more clearly, but I don't think I'd be interested in that job....

P.S. Apologies to Robert and all Canucks for deleting the metric measurements from the quoted IRC passage. Just trying to be brief. Anyway, you guys'll come around to our standard system eventually...

They can certainly use you and your skills at the International Code Council, Kate. Sadly, in the majority of jurisdictions in my state you could hide the remains of Jimmy Hoffa in a code book and they would continue to remain undiscovered.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.
Reply With Quote
  #9  
Old 11/12/10, 8:29 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Is the IRC wrong?

Quote:
Originally Posted by ktarasenko View Post
Robert Young wrote:

Should not the dimensions be the same?
Attics containing appliances shall be provided with an opening 30 by 22. The clear access opening dimensions shall be a minimum of 20 inches by 30 inches
That is how I read it.

That's how Steve (and we) read it, too, but I do see now that the first set of dimensions given is related to the passageway, while the second set specifically mentions the attic access itself.

Again, were I the editor for the IRC, that passage would have been written more clearly, but I don't think I'd be interested in that job....

P.S. Apologies to Robert and all Canucks for deleting the metric measurements from the quoted IRC passage. Just trying to be brief. Anyway, you guys'll come around to our standard system eventually...
There are three separate things being defined in this standard: 1.) the passageway (HxW); 2.) the floor of the passageway (W); 3.) the opening to the passageway (LxW).

The passageway must be have minimum clear dimensions (inches) of 30Hx22W (you should be able to move a rectangular box of 30Hx20W along the passageway with an inch to spare on each side clear of any obstructions). The floor of this passageway must be at least 24W. The opening to the passageway must be clear at least 30Lx20W (no hinges, trim, brackets, etc. encroaching). These minimum dimensions must be adjusted upward to accommodate the largest appliance if it won't fit through these dimensions.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 11/12/10 at 8:34 PM..
Reply With Quote
  #10  
Old 11/12/10, 9:12 PM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,012
Default Re: Is the IRC wrong?

Thank you Kate.
Thank you for thinking of metric conversion.
I myself sill use standard mesuerments and only do conversions when needed.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #11  
Old 11/12/10, 11:13 PM
Steve Beverlin Steve Beverlin is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Houston, TX
Posts: 7
Default Re: Is the IRC wrong?

I don't think the IRC is wrong, but it is ambiguous in section M1305.1.3

In one case they are referring to access to the attic. In the other case they are referring to accessibility to appliances while within the attic.

IRC Section R807.1 "Attic Access" clearly states:
"The rough framed opening shall not be less than 22 inches by 30 inches and shall be located in the hallway or other readily accessible location. A 30 inch minimum unobstructed headroom in the attic space shall also be provided at some point above the access opening."

IRC M1305.1.3 deals with "Appliances in the Attic", and the dimensions for their subsequent removal if necessary. It specifies 30" X 22" wide and not more than 20 feet in length along the centerline of the passageway from the opening to the appliance. Again, they are referring to the dimensions when in the attic itself. (not access to the attic). Later in the same paragraph it specifies a "clear access opening dimensions shall be a minimum of 20 inches by 30 inches where such dimensions are large enough to allow removal of the largest appliance."

I don't think there is any ambiguity regarding the clarity of IRC 807.1 . and its dimensions for "attic access". (30" X 22")

However IRC M1305.1.3 is ambiguous, in my opinion, regarding the attic passageway access (not attic access) by offering two different dimensions in the context of the same paragraph.

By the way, the Uniform Building Code 1505.1, is consistent with the IRC,
in specifying a 30" X 22" attic access.
Reply With Quote
  #12  
Old 11/13/10, 12:00 AM
Kate Tarasenko's Avatar
Kate Tarasenko Kate Tarasenko is offline
InterNACHI Member
 
Join Date: Jul 2009
Posts: 145
Default Re: Is the IRC wrong?

Quote:
Originally Posted by jbushart View Post
They can certainly use you and your skills at the International Code Council, Kate. Sadly, in the majority of jurisdictions in my state you could hide the remains of Jimmy Hoffa in a code book and they would continue to remain undiscovered.
Thanks for the shout-out, Jim! My experience says that if a bureaucracy isn't obfuscating, they're just not trying hard enough!

I went back into the "25 Standards" course (the slide is called "Attic Access") and I slightly rewrote the info covering this so that it's clear and unambiguous (and no code was quoted originally, and I think it's best left that way).

Thanks again to everyone for their help with this. And to all the guys working on their "Molson muscles" up North, Happy Remembrance Day Plus One!



Cheers,
Kate
Crimea River
Editor-in-Chief

kate@internachi.org
Reply With Quote
  #13  
Old 11/13/10, 12:06 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Is the IRC wrong?

A Home Inspection
is not a Code Inspection...

If a client
is going to sue
over 2 inches of attic access
lol


From the words of Joe Myers
"Too Funny...."



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
Need a home inspection in New Mexico? Check out InterNACHI's listing of New Mexico certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/13/10, 12:08 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,946
Default Re: Is the IRC wrong?

I think this was in reference to the accuracy of information being provided in a training program...not a liability issue.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.
Reply With Quote
  #15  
Old 11/13/10, 12:28 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Is the IRC wrong?

Quote:
Originally Posted by jbushart View Post
I think this was in reference to the accuracy of information being provided in a training program...not a liability issue.
Code is not absolute
It is always about
individual (state, county, municipal, provincial)
interpretation
....
no absolutes that I am aware of...



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Free Books And Articles For Electrical jtedesco1 Electrical Inspections 14 1/6/08 6:45 PM
Whats wrong in this pic cbottger Inspecting HVAC Systems 11 3/11/07 6:16 PM


All times are GMT -4. The time now is 4:31 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts