Default Kitchen Range Down Draft Vent

What type duct material is typically used for a stove/ range down draft vent? I recently had one that was connected to a plastic dryer vent duct material in the crawlspace. Don't think that's right Thanks.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #2  
Old 2/27/09, 8:29 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Kitchen Range Down Draft Vent

What I have seen is a metal close-accordianed type that can be bent to the different angles needed. The big box catalog calls it 'semi-rigid aluminum vent duct'.

The plastic dryer vent type wouldn't do well, at all. Course, be cheap to do spring cleaning. Just toss and replace !!
Reply With Quote
  #3  
Old 2/27/09, 9:54 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: Kitchen Range Down Draft Vent

Quote:
Originally Posted by lfoster View Post
What I have seen is a metal close-accordianed type that can be bent to the different angles needed. The big box catalog calls it 'semi-rigid aluminum vent duct'.

The plastic dryer vent type wouldn't do well, at all. Course, be cheap to do spring cleaning. Just toss and replace !!

LOL! Thx Linda!



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Home Inspection Reports Powered by:
HomeGauge eServices

Reply With Quote
  #4  
Old 2/27/09, 10:18 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Kitchen Range Down Draft Vent

IRC SECTION M1503
RANGE HOODS

M1503.1 General. Range hoods shall discharge to the outdoors
through a single-wall duct. The duct serving the hood
shall have a smooth interior surface, shall be air tight and shall
be equipped with a backdraft damper. Ducts serving range
hoods shall not terminate in an attic or crawl space or areas
inside the building.

Exception: Where installed in accordance with the manufacturer’s
installation instructions, and where mechanical or
natural ventilation is otherwise provided, listed and labeled
ductless range hoods shall not be required to discharge to
the outdoors.

M1503.2 Duct material. Single-wall ducts serving range
hoods shall be constructed of galvanized steel, stainless steel or
copper
.

Exception: Ducts for domestic kitchen cooking appliances
equipped with down-draft exhaust systems shall be permitted
to be constructed of schedule 40 PVC pipe provided that
the installation complies with all of the following:
1. The duct shall be installed under a concrete slab
poured on grade; and
2. The underfloor trench in which the duct is installed
shall be completely backfilledwith sand or gravel; and
3. The PVC duct shall extend not more than 1 inch (25
mm) above the indoor concrete floor surface; and
4. The PVC duct shall extend not more than 1 inch (25
mm) above grade outside of the building; and
5. The PVC ducts shall be solvent cemented.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pellet stove help chellickson General Inspection Discussion 23 8/19/10 1:23 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Draft fan & gravity vent rbrady Inspecting HVAC Systems 7 1/4/08 8:19 PM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM


All times are GMT -4. The time now is 5:19 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts