Question Knob and Tube Wiring

Recently a house was inspected here in Maine. It was noted that there was knob and tube wiring in some places of the wiring system. Most of the wiring has been upgraded.

We had a licensed electrician inspect the wiring and judged it to be satisfactory.

The prospective owner has taken issue with the old wiring, and want it replaced because they attempted to get insurance and were denied after the buyers told the insurance company that this knob and tube wiring was there.

Does anyone know the about the acceptance of thid kind of wiring?

Thanks.

Last edited by Gary Brearley; 11/1/08 at 11:52 AM.. Reason: Just read many of the threads.
Reply With Quote
  #2  
Old 11/1/08, 11:39 AM
Greg Bell's Avatar
Greg Bell Greg Bell is offline
InterNACHI Member
 
Join Date: Oct 2002
Location: Titusville, FL
Posts: 4,155
Default Re: Knob and Tube Wiring

I don't know of any insurance company that will issue a policy on a home with knob and tube.

Who hired the electrician?

Did he issue his findings in writing?



Greg Bell
Titusville, Fl
02111507

Serving Central Florida
Reply With Quote
  #3  
Old 11/1/08, 12:08 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and Tube Wiring

Here is a good article on knob & tube.
http://www.bradyinspects.com/files/knob_tube_DH.pdf

Some electricians (here at least) have said that knob and tube is safer (when in good condition) due to the space between the wires. We also have a very temperate climate, with no extreme temperatures, so that helps keep it in good condition.

Here in Eureka, CA I see it fairly regularly and I'm sure that there must be someone insuring these properties. We have a lot of pier and post foundation houses here too, and I know that not all insurance companies will cover those, but there are plenty that will.

State farm, for one, I think is pretty particular. Try some other companies.
Reply With Quote
  #4  
Old 11/1/08, 12:22 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and Tube Wiring

A written statement from the electrician may be accepted by some insurance companys in my area. From the buyer's perspective though, they get their mortgage but it does not mean they are covered if there is a fire! The best insurance is new wiring, IMO.

John Kogel
www.allsafehome.ca
Reply With Quote
  #5  
Old 11/1/08, 7:44 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,316
Send a message via Yahoo to jfunderburk
Default Re: Knob and Tube Wiring

Have the electrician put that statement on his letterhead and sign it. He'd be a fool to do so. If you are involved with the electrician in any way, I'd form a new relationship with someone else.

If you referred it to an electrician and the buyer hired one who said it's OK, the monkey is off your back. But if I was the buyer, I'd get a second opinion.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 11/1/08, 7:48 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,316
Send a message via Yahoo to jfunderburk
Default Re: Knob and Tube Wiring

P.S.

When you refer something like that out, refer it to a licensed "and competent" contractor. Just because you got your electrician license 40 years ago, doesn't mean you are competent. I'm sure we've all seen instances of morons who have a contractors license.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 11/1/08, 8:53 PM
rshuey rshuey is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Mar 2007
Posts: 198
Please Note: rshuey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and Tube Wiring

The state of PA, with exception to a few cities, is really scary. There is no contractor certification. If you have a magnet on your truck that says you are an electrician, you are an electrician...scary indeed.


I am working on a program in my jurisdiction to have a very basic and simple contractor registry program. Basically, this program will just check insurances and stuff.
Reply With Quote
  #8  
Old 11/1/08, 8:56 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Knob and Tube Wiring

To me it seems to be a negotiating issue and the electricians opinions are moot.

A) Insurance company won't insure.
B) Buyers want it fixed so they can insure it.
C) Sellers either have it fixed or don't
D) Buyers buy it or don't.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #9  
Old 11/2/08, 8:52 AM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is online now
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,541
Default Re: Knob and Tube Wiring

Most likely the seller has the home insured, what company did he use?



"A state of war only serves as an excuse for domestic tyranny." ~ Alexander Solzhenitsyn



Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"
Reply With Quote
  #10  
Old 11/3/08, 5:29 PM
jvogan's Avatar
jvogan jvogan is offline
Active Poster
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Please Note: jvogan is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and Tube Wiring

I see knob and tube wiring here all the time. I always call it out, and my software states that SOME insurance companies wont insure a home with K & T, so they should check with their insurance company prior to close of escrow.
Reply With Quote
  #11  
Old 11/3/08, 6:33 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Knob and Tube Wiring

Quote:
Originally Posted by jburkeson1 View Post
Most likely the seller has the home insured, what company did he use?
That's becoming less and less of an avenue lately, as even some people who have faithfully paid their premiums for decades are now faced with new insurance company requirements to just renew their policy. I hear these woeful tales on a regular basis.
Reply With Quote
  #12  
Old 11/12/08, 5:16 PM
Ron S. De Mott Ron S. De Mott is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: northern N.J.
Posts: 62
Default Re: Knob and Tube Wiring

You covered yourself by suggesting a electrician look at it. In N.J. I see alot of it and this weather dries and cracks the insulation. I never follow up to see what happens, I always state the entire dwelling needs to be evaluated by a qualified electrician Much K&T is not visible and it is always incorrectly spliced in many places. Also if insulation is installed in walls or the attic that covers the wire it becomes a real fire hazard..Always cover yourself. I believe that G F C I outlets or possibly AFCI's can be installed to make them just a little safer. Replacement is the safest option.
Reply With Quote
  #13  
Old 11/12/08, 6:10 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,316
Send a message via Yahoo to jfunderburk
Default Re: Knob and Tube Wiring

I heard a guy tell me once, "The only safe thing to plug into knob-and-tube wiring is a smoke alarm".



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
K&T splice. egarcia1 Electrical Inspections 13 2/3/07 6:36 AM
Knob and tube wblakey Electrical Inspections 17 11/14/06 7:41 PM
Knob and tube: heat's the main problem? kshepard Electrical Inspections 25 6/27/06 9:51 AM


All times are GMT -4. The time now is 12:56 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts