Members,
I did an inspection today of a new home for a very nice lady. She is very knowledgable about a great many things. I noted that the main electrical panel outside the home had no main electrical circuit breaker. I made a note of it on her report saying that there was no main electrical shut-off for the main panel, but there was one for the auxillary panel. 200 amps worth. Unfortunately, if you flipped that one off, the main panel is still live. Isn't there a code stating that there has to be a main electrical shut-off? I looked through my code book and every other book I could find but nothing that comes out and says there has to be one. Help? John |
|
#2
|
||||
|
||||
|
John,
what is in the exterior panel, and what does it feed? Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#3
|
|||
|
|||
|
John
As I understand your question you must have a master cut off or six or less breakers regardless what they feed I believe that a master breaker can be external with in sight but this should be substantiated by someone that can site code rlb |
|
#4
|
||||
|
||||
|
Quote:
#2, if you did (as you say) shut down the 200 amp auxilary panel and the power remains on, and there's no other main breaker for shutting down the entire home....You have a safety issue. |
|
#5
|
||||
|
||||
|
I spoke with John last night. As it turns out, there were only five breakers in the service panel.
No need for a "main" disconnect. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
Quote:
Did he call you? Asked another way (and with no inference of a lack of knowledge on John's part) If I ask a question here and don't get a timely response, can I call you? (is there a 'sheepish' smile on here somewhere!) Seriously, I view you as a hell of a resource (I spoke with several in Orlando who feel the same) Humbly, - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector Last edited by mgault; 3/24/06 at 12:01 PM.. |
|
#7
|
||||
|
||||
|
Quote:
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Jeff,
You're now in my phone as Jeff Pope-Ca (to remind me not to call you at 0900 my time Thanks! - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#9
|
|||
|
|||
|
Jeff
Help me out a little --- if a main disconect is required (over six throws) how accessable does it have to be? I have seen a simular question in reff to condos but what about a normal home? rlb |
|
#10
|
||||
|
||||
|
Quote:
230.70(A)(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors. 230.72(C) Access to Occupants. In a multiple-occupancy building, each occupant shall have access to the occupant’s service disconnecting means. Exception: In a multiple-occupancy building where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the service disconnecting means supplying more than one occupancy shall be permitted to be accessible to authorized management personnel only. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
|||
|
|||
|
Thanks Jeff
I know this has been explained before but for some reason it just did not stick Sort of open for some common sense depending on how the house is built When we spot some of these things and flag them I guess we should remember that there is some gray areas Thanks again and have a good day rlb |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Download the videos here all about physics and electricity | jtedesco1 | Electrical Inspections | 5 | 9/14/08 3:58 PM |
| Handbook for Electrical Safety | pabernathy | Electrical Inspections | 1 | 1/1/07 1:14 PM |
| Electrical Safety Information | jtedesco1 | Electrical Inspections | 0 | 2/19/06 1:48 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |