Default How many amps and volts is this panel?

http://www.nachi.org/forum/attachmen...1&d=1214928498

Yesterday I came upon this panel, it is larger than I usually come across around here. Could somebody please tell me their opinion. It appears to me to be an 800 amp panel, but that seems large, and why are there 4 conductor lines?
Attached Thumbnails
many-amps-and-volts-panel-cimg6176-800x600-.jpg  
Reply With Quote
  #2  
Old 7/1/08, 12:19 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many amps and volts is this panel?

Quote:
Originally Posted by dkraemer
http://www.nachi.org/forum/attachmen...1&d=1214928498

Yesterday I came upon this panel, it is larger than I usually come across around here. Could somebody please tell me their opinion. It appears to me to be an 800 amp panel, but that seems large, and why are there 4 conductor lines?
If this is the main disconnect means, without having more info such as the SEC size and #, my first guess is a 240 volt, 400 amp service. Check the panel data and see if it is rated for 400 amps.
Reply With Quote
  #3  
Old 7/1/08, 7:22 PM
David K. Kraemer David K. Kraemer is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Lancaster, CA
Posts: 37
Default Re: How many amps and volts is this panel?

Sorry, hope this helps.
Attached Thumbnails
many-amps-and-volts-panel-cimg6173-800x600-.jpg  
Reply With Quote
  #4  
Old 7/1/08, 7:27 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many amps and volts is this panel?

Quote:
Originally Posted by dkraemer
Sorry, hope this helps.
Its a 240 volt meter but.......?? Take this to the electrical section.
Reply With Quote
  #5  
Old 7/1/08, 9:59 PM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is offline
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,548
Default Re: How many amps and volts is this panel?

Quote:
Originally Posted by dkraemer
http://www.nachi.org/forum/attachmen...1&d=1214928498

Yesterday I came upon this panel, it is larger than I usually come across around here. Could somebody please tell me their opinion. It appears to me to be an 800 amp panel, but that seems large, and why are there 4 conductor lines?
It is a 200 Amp 120/240 Volt panel. There are (4) staggered 50A bus bars in this panel.



"A state of war only serves as an excuse for domestic tyranny." ~ Alexander Solzhenitsyn



Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"
Reply With Quote
  #6  
Old 7/1/08, 10:25 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many amps and volts is this panel?

Quote:
Originally Posted by jburkeson1
It is a 200 Amp 120/240 Volt panel. There are (4) staggered 50A bus bars in this panel.
50A at 120 volts?


ODD!! Have never seen anything like that in my neck of the woods!!

Why wouldn't each pair of bus bars (240 volts bar to bar) be protected by 100 amp breakers?

Brand? Reference? Pictures?

PS:
Thanks, James. Got the answers in Electrical.

Last edited by Brian A. MacNeish; 7/1/08 at 10:57 PM..
Reply With Quote
  #7  
Old 7/3/08, 8:18 PM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is offline
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,548
Default Re: How many amps and volts is this panel?

Quote:
Originally Posted by Brian A. MacNeish
50A at 120 volts?


ODD!! Have never seen anything like that in my neck of the woods!!

Why wouldn't each pair of bus bars (240 volts bar to bar) be protected by 100 amp breakers?

Brand? Reference? Pictures?

PS:
Thanks, James. Got the answers in Electrical.
Why... Cause its not, thats why. GE, look it up yourself.



"A state of war only serves as an excuse for domestic tyranny." ~ Alexander Solzhenitsyn



Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"
Reply With Quote
  #8  
Old 7/3/08, 9:43 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many amps and volts is this panel?

Quote:
Originally Posted by jburkeson1

My question: "Why wouldn't each pair of bus bars (240 volts bar to bar) be protected by 100 amp breakers?"



Your answer:
Why... Cause its not, thats why. GE, look it up yourself.


From same topic on electrical thread:

That main breaker is factory installed and part of a UL listed assembly so it's not a issue. FYI that type of breaker was common on ITE*, GE* and some Cutler-Hammer "All in ones" all they are is 2 - 100 A 2 pole breakers paralelled together .

Is this last answer incorrect??



Reply With Quote
  #9  
Old 7/4/08, 12:56 AM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: How many amps and volts is this panel?

[quote=dkraemer]http://www.nachi.org/forum/attachmen...1&d=1214928498

Yesterday I came upon this panel, it is larger than I usually come across around here. Could somebody please tell me their opinion. It appears to me to be an 800 amp panel, but that seems large, and why are there 4 conductor lines?[/quote

David,

It is a 200 Ampere 240v panel. It is probably 3-phase 4-wire. The reason I said it is "probably" 3-phase 4-wire is because there is a very slim possibility of it being 2-phase.

In a perfect World, the fourth wire would not be on a breaker. If it is a corner grounded Delta connection, it ought to be identified. In most parts of the US of A the fourth leg (aka "Hi-leg" or "Wild-leg") would be identified with orange tape.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #10  
Old 7/4/08, 2:27 AM
Joseph Burkeson, CMI's Avatar
Joseph Burkeson, CMI Joseph Burkeson, CMI is offline
InterNACHI Member
 
Join Date: May 2003
Location: Greater Tampa Bay
Posts: 16,548
Default Re: How many amps and volts is this panel?

Quote:
Originally Posted by gwells
It is a 200 Ampere 240v panel. It is probably 3-phase 4-wire. The reason I said it is "probably" 3-phase 4-wire is because there is a very slim possibility of it being 2-phase.
It is not a 3-phase 4-wire panel, repeat NOT. It is a single-phase 200 Amp house panel manufactured by GE. The buss configuration is their design, the CB is simply ganged, the rating is for the entire ganged configuration.

BTW it is doubtful that you have ever seen a 2-phase panel, (2-hot legs & 2-neutrals), it just ain't used anymore because of the cost of transmission, 3-phase power is cheaper to produce & transmit over long distances. If you are seeing 2-phase it is most likely fused and in an old industrial environment somewhere on the east coast of the united states.

240 delta is a three phase configuration, again the panel in the picture ain't 3-phase. In a three phase panel there is 3-hot conductors and possibly a neutral. The picture shown is simply a ganged CB with staggered 120-volt A & B phases.



"A state of war only serves as an excuse for domestic tyranny." ~ Alexander Solzhenitsyn



Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector

Square-One Inspection "Assurance begins here"

Last edited by jburkeson1; 7/4/08 at 2:38 AM..
Reply With Quote
  #11  
Old 7/4/08, 11:29 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: How many amps and volts is this panel?

I agree with Joe (although he will never know it since I'm on his 'Ignore List", but that's OK). Just look at the wiring diagram visible in one photo to see the ganged breakers connected; one set to phase A, the other set to phase B. It is definitely not a 3-phase panel.
http://www.nachi.org/forum/attachmen...5&d=1214955931
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
wire size for these 60 amps? rwashington Electrical Inspections 12 6/4/08 11:10 PM
Service Panel Quiz? hmcclard Electrical Inspections 5 10/24/07 11:53 PM


All times are GMT -4. The time now is 6:32 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts