Default My electrical fire

My wife was drying her hair (1875 watt hair dryer) as I was talking to her. We both smelled that familiar smell and before she could turn off the dryer, flames shot out from the switch. She wasn't hurt, she tried to turn it off but it wouldn't turn off, we pulled the cord out of the GFCI outlet. The dryer also had an inline GFCI plug. There was no smoke, fire, or sparks at the outlet and no damage to the outlet.

Shouldn't the GFCI outlet or the inline GFCI plug have tripped and shut the power off?

I checked the outlet and it trips with my tester and with the test button.
Attached Thumbnails
my-electrical-fire-p3160165.jpg   my-electrical-fire-p3160166.jpg   my-electrical-fire-p3160167.jpg   my-electrical-fire-p3160168.jpg   my-electrical-fire-p3160174.jpg  




Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/16/10, 7:14 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 1,893
Default Re: My electrical fire

I'll take a crack at it:

GFCI monitors for leakage of current. The device can burn up, but if there is no significant disparity (5+ mA) in the amperage being sent through the ungrounded (hot) conductor and what comes back through the grounded (neutral) conductor at the GFCI device it wont trip the GFCI.

If total amperage doesn't exceed the rating of the breaker, it won't trip either.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 3/16/10 at 7:17 PM..
Reply With Quote
  #3  
Old 3/16/10, 7:25 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 757
Default Re: My electrical fire

That is how it works, but I would think that the burning would cause a change in the amperage sufficient enough to trip the GFCI.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #4  
Old 3/16/10, 7:31 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,040
Default Re: My electrical fire

Quote:
Originally Posted by mmerino View Post
That is how it works, but I would think that the burning would cause a change in the amperage sufficient enough to trip the GFCI.
Maybe an AFCI would have tripped.
Reply With Quote
  #5  
Old 3/16/10, 7:40 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 757
Default Re: My electrical fire

Quote:
Originally Posted by jjonas View Post
Maybe an AFCI would have tripped.

AAH! you are probably correct!! But, shouldn't the GFCI have tripped? I looked at the GFCI and it appears OK and operating correctly.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #6  
Old 3/16/10, 7:50 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,040
Default Re: My electrical fire

Have you checked for recalls yet?

Assuming the air intake screen is not clogged with hair, like most are (and women never seem to clean) and you don't find a recall, report the incident anyway to the CPSC. Also, call Sunbeam and report the incident.

Seems like a lot of work for a $20 hairdryer, doesn't it... but if it adds to a growing list of incidents, it may be the one needed to trigger a recall!

Do the right thing, man!!! Save the world from shoddy products!!! Your wife could have been seriously injured (aka... hair catch fire)!!! Think of the "brownie points" and "special favors" you'll earn when she finds out you're taking on the fight!!!
Reply With Quote
  #7  
Old 3/16/10, 8:00 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: My electrical fire

Quote:
Originally Posted by mmerino View Post
AAH! you are probably correct!! But, shouldn't the GFCI have tripped? I looked at the GFCI and it appears OK and operating correctly.
That is unfortunate but normal, the fire was heat dissapation which is wattage, the wattage is driven by the current, if the neutral did not have current you would not have the wattage. The hair dryer would have shut off when the heat from the fire reached the little heat sensor in the air output section or when a wire burned in two. Never leave hair dryers etc plugged in when not using, it can fail in other ways too.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #8  
Old 3/16/10, 8:00 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 757
Default Re: My electrical fire

LOL, she will just laugh at me, like usual



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #9  
Old 3/16/10, 8:21 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 11,734
Default Re: My electrical fire

Just caught this.
I vote for AFCI would have tripped it.

The voltage may have stayed the same while it arced.
1850 amps (damn ,she must have long hair to need that sorta power).
Reply With Quote
  #10  
Old 3/16/10, 8:41 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: My electrical fire

Can you imagine what might have happened, if she would have set it down, and then sprayed on the hair spray just as it ignited? She'd have been doing a Michael Jackson Pepsi commercial. It's awesome that no one was hurt.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #11  
Old 3/16/10, 8:42 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,040
Default Re: My electrical fire

Quote:
Originally Posted by belliott View Post
Just caught this.
I vote for AFCI would have tripped it.

The voltage may have stayed the same while it arced.
1850 amps (damn ,she must have long hair to need that sorta power).
Watts Bob... not Amps!
Reply With Quote
  #12  
Old 3/16/10, 9:04 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 11,734
Default Re: My electrical fire

Quote:
Originally Posted by jjonas View Post
Watts Bob... not Amps!
Watt you talking about ?

The amps on that thing are pretty close to tripping a 20 amp breaker all on it's own by the way.

Thanks as always for your loving correction.

Be sure to spell check me.(thanks)
Reply With Quote
  #13  
Old 3/17/10, 12:42 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 11,040
Default Re: My electrical fire

Quote:
Originally Posted by belliott View Post
Watt you talking about ?

The amps on that thing are pretty close to tripping a 20 amp breaker all on it's own by the way.

Thanks as always for your loving correction.

Be sure to spell check me.(thanks)
WATT-ever !!!
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/17/10, 1:54 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: My electrical fire

Glad she's OK.

Heres some hair dryer info.

http://home.howstuffworks.com/hair-dryer4.htm
Even with this screen in place, you'll need to periodically pick lint off the screen. Too much lint can block the airflow into the dryer, and the hair dryer will overheat with less air carrying away the heat generated by the nichrome coil or other type of heating element. Newer hair dryers have incorporated some technology from the clothes dryer: a removable lint screen that's easier to clean.

http://www.dallasnews.com/sharedcont...s.c810bf8.html
Millions of Americans start their day by blow drying their hair. However, a News 8 investigation discovered hair dryer complaints that included shooting fire, electric shocks and even statements of hair dryers "turning on" by themselves.
Reply With Quote
  #15  
Old 3/17/10, 9:39 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,696
Default Re: My electrical fire

Michael,

I've seen GFI's that looked like that hairdryer; of course they weren't offering the protection any more...



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Coming to Schaumburg, Ill - Electrical Training with The Electrical Guru ksitzes Inspection Education & Training 12 3/17/10 5:19 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 4:58 PM
Electrical Fire Safety jtedesco1 Electrical Inspections 3 2/1/08 10:02 AM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 2:14 PM


All times are GMT -4. The time now is 9:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts