Default Need adive on clearence exit door

Well this is new one , Home inspection today had a new garage added. Problem One of 2 exit doors is partly blocked by Ac Unit, IS the any distance required for this listed If so what would it be I can not find anything about it Yes they had a permit when they built it.need-adive-clearence-exit-door-100_9902.jpg
I have referred it back to local building official
Reply With Quote
Find an InterNACHI certified North Carolina Home Inspector (and anywhere else in North America)
  #2  
Old 5/22/09, 1:58 PM
jcoleman jcoleman is offline
InterNACHI Member
 
Join Date: Feb 2009
Posts: 5
Default Re: Need adive on clearence exit door

I believe there is an egress clearance minimum of 5 ft if this door can be needed as an emergency egress.
Reply With Quote
  #3  
Old 5/22/09, 2:11 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need adive on clearence exit door

AC unit impeeds door from opening fully.
Reply With Quote
  #4  
Old 5/22/09, 2:48 PM
lgreen's Avatar
lgreen lgreen is offline
InterNACHI Member
 
Join Date: Jan 2009
Location: Buckeye, Arizona
Posts: 36
Default Re: Need adive on clearence exit door

The door opens in. Therefore it does not impeed the door from opening.
I believe the minimum landing outside each exit door in the direction of travel is 36".
Reply With Quote
  #5  
Old 5/22/09, 3:13 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need adive on clearence exit door

Quote:
Originally Posted by lgreen View Post
The door opens in. Therefore it does not impeed the door from opening.
I believe the minimum landing outside each exit door in the direction of travel is 36".
- DOH!

Thanks, I stand corrected.

Last edited by rmaday; 5/22/09 at 3:20 PM..
Reply With Quote
  #6  
Old 5/22/09, 6:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Need adive on clearence exit door

Quote:
Originally Posted by lgreen View Post
I believe the minimum landing outside each exit door in the direction of travel is 36".
This is a good rule of thumb, but generally (in residential construction), the required clearance is equal to the width of the door.

Door width requirements will vary depending on the building "occupancy" type - i.e. residential (typical SFR), multi-family (condo, townhouse, apartment, etc.), utility (garage, storage, etc.), etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 5/22/09, 7:10 PM
cmcdonald cmcdonald is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Jaffrey, NH
Posts: 80
Please Note: cmcdonald is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Need adive on clearence exit door

Wayne,
below are some of the NFPA 101 (Life Safety Code) 2009 edition requirements for secondary means of escape in One & Two Family Homes :

24.2.2.3 Secondary Means of Escape:
The secondary means of escape, other than an existing approved means of escape, shall be one of the means specified in 24.2.2.3.1 through 24.2.2.3.3.


24.2.2.3.1:
It shall be a door, stairway, passage, or hall providing a way of unobstructed travel to the outside of the dwelling at street or the finished ground level that is independent of and remote from the primary means of escape.


24.2.2.3.2:
It shall be a passage through an adjacent nonlockable space, independent of and remote from the primary means of escape, to any approved means of escape.


24.2.2.3.3:
It shall be an outside window or door operable from the inside without the use of tools, keys, or special effort and shall provide a clear opening of not less than 5.7 ft2 (0.53 m2). The width shall be not less than 20 in. (510 mm), and the height shall be not less than 24 in. (610 mm). The bottom of the opening shall be not more than 44 in. (1120 mm) above the floor. Such means of escape shall be acceptable where one of the following criteria is met:
(1) The window shall be within 20 ft (6100 mm) of the finished ground level.
(2) The window shall be directly accessible to fire department rescue apparatus as approved by the authority having jurisdiction.
(3) The window or door shall open onto an exterior balcony.
(4) Windows having a sill height below the adjacent finished ground level shall be provided with a window well meeting the following criteria:
(a) The window well shall have horizontal dimensions that allow the window to be fully opened.
(b) The window well shall have an accessible net clear opening of not less than 9 ft
2 (0.82 m2) with a length and width of not less than 36 in. (915 mm).
(c) A window well with a vertical depth of more than 44 in. (1120 mm) shall be equipped with an approved permanently affixed ladder or with steps meeting the following criteria:
i. The ladder or steps shall not encroach more than 6 in. (150 mm) into the required dimensions of the window well.
ii. The ladder or steps shall not be obstructed by the window.

Reply With Quote
  #8  
Old 5/26/09, 2:41 PM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: Need adive on clearence exit door

As I understand it, the requirements are for egress doors. The home has to have 1 egress door which is generally the front door. It can have a secondary egress door but it is not required in residential. I don't think a service door in the garage would be a required egress door.

I would point out that exiting through the door in an emergency would be restricted by the placement of the air conditioner and recommend that they consider moving it.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #9  
Old 5/27/09, 8:28 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,641
Default Re: Need adive on clearence exit door

Thanks guys i wrote the the ac unit was mounted to close to the exit in my opinion and referred it back to local officials ( there was a permit taken out for the garage ). I wasn't to excited because of the second rear exit.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
www.FireDoorInspector.org gromicko Commercial Inspections 108 1/12/09 3:39 PM
Exterior Door Backward dbucknavich Exterior Inspections 22 10/13/08 11:27 AM
Newbie here with a slab "standards" question Robert Young, #3 Structural Inspections 17 4/10/07 11:48 AM


All times are GMT -4. The time now is 3:38 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts