Default Procedural Inspection Checklist

for inspecting an electrical panel. The checklist was developed from http://www.nachi.tv/ppv/3.

Every item in the list appears as a defect or comment in the inspection that Nick and Joe T. perform in the video.


INSPECTION PROCEDURAL CHECKLIST
Electrical panel

• Follow InterNACHI Standards of Practice
• Wear personal safety protection, including glasses and gloves
• Report location of the electrical panel
• Check adequate workspace
• Panel must be readily accessible
• Use proper inspection tools, including magnet handle, insulated screwdriver, and flashlight
• Check adequate illumination at workspace
• Inspect cabinet front cover
• Check for incorrect type of screws or missing screws at the cabinet front cover
• Measure height of main disconnect
• Inspect panelboard
• All disconnects must have specific identification
• Check for inspection stickers and dates
• Check for identified filler plates
• Identify all breakers in the “off” position
• Identify main overcurrent device
• Determine size of service
• Safe removal of cabinet front cover
• No foreign objects or contamination inside cabinet
• Check entrance conductors and lugs
• Identification of grounded conductor
• Check clamps, connectors, and bushings
• No open knockouts permitted
• Check for disconnected or loose conductors
• Inspect main bonding jumper
• Inspect main grounding electrode conductor (GEC)
• Check for doubled neutrals
• Check for doubled hot conductors
• Identify any breakers that are not permitted by manufacturer
• No white wires on breakers
• Test GFCIs and AFCIs
• No doorbell transformers inside cabinet
• Check for loose equipment grounding conductor (EGC)
• Check for ampacity or overfusing defects
• No melted conductor insulation
• No rust, corrosion, or water inside cabinet
• No gaps between cabinet and wallboard greater than 1/8 inch
• Check multiple cables in connectors
• Check for damage to wires
• Check for damage to insulation sheathing
• Inspect for exposed live wires
• Check identified handle ties
• Read the label on the cabinet front cover
• Identify product name and type of cabinet from label
• Confirm amps and volts are identified on label
• Inspect the panelboard diagram
• Count maximum number of poles from the diagram
• Confirm location of main bonding jumper
• Identify twin or ฝ breakers
• In the subpanel, confirm that the EGC's (equipment grounding conductors) are on a separate terminal bar that is bonded to the cabinet, and that the grounded conductors (neutrals) are isolated or floating from the cabinet
• Never leave panelboard exposed
• Replace cabinet cover correctly
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Radon Mitigation System Checklist dmacy Ancillary Inspection Services & Additional Topics 5 1/9/09 5:50 PM
inspection procedural checklist bgromicko Electrical Inspections 24 3/2/08 11:00 AM


All times are GMT -4. The time now is 12:31 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts