Default Romex protection in attic space

Quote:
They almost got it right.

NM is required to be secured at intervals not to exceed 54", regardless of the access.

If there is a permanent ladder or stairway (a retractable counts as permanent), you need nothing additional.

Without a permanent access, the cable must be shielded or otherwise protected within 6 feet of the access.

I am curius Jeff as to how often you call this violation out.?

I see it in almost every new home and I always call it out , but it never gets fixed unless it is within 3' of the hatch...?

I have yet to get a satisfactory explanation from a Sparky.???

Last edited by tallen; 5/6/07 at 3:24 AM..
Reply With Quote
  #2  
Old 5/6/07, 4:02 AM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex protection in attic space

People will do only as much as the local AHJ makes them do, which in many cases is very little. There's one jurisdiction around here where it has become 'normal' to run the entire bundle of branch circuit wiring in a wad, usually down along the base of the trusses, branching off where necessary with minimal stapling. If the design makes this method impossible, they use the CENTER of the base of the web members. Some will use plastic cable ties and bundle them together. It never gets corrected, but I still protect my legal butt by calling it out.
Reply With Quote
  #3  
Old 5/6/07, 12:29 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Romex protection in attic space

"Click to Enlarge"

Attachment 11355

Last edited by dvalley; 10/7/07 at 5:40 PM..
Reply With Quote
  #4  
Old 5/6/07, 1:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Romex protection in attic space

Quote:
Originally Posted by tallen
I am curius Jeff as to how often you call this violation out.?
If the attic space is accessible, meaning you can get in and inspect it, rather than just viewing it from the hatch, I will call this out.

I see it much less in new construction as compared to older homes and renovations. Newer construction typically has access platforms (cat-walks) for the FAU, which generally provide the required protection.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 5/6/07, 2:42 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Romex protection in attic space


(A) Where Run Across the Top of Floor Joists. Where
run across the top of floor joists, or within 2.1 m (7 ft) of
floor or floor joists across the face of rafters or studding, in
attics and roof spaces that are accessible, the cable shall be
protected by substantial guard strips that are at least as high
as the cable. Where this space is not accessible by permanent
stairs or ladders, protection shall only be required
within 1.8 m (6 ft) of the nearest edge of the scuttle hole or
attic entrance.
(B) Cable Installed Parallel to Framing Members.
Where the cable is installed parallel to the sides of rafters,
studs, or floor joists, neither guard strips nor running boards
shall be required, and the installation shall also comply
with 300.4(D).



Damaged cables due to foot traffic on the cables or improper protection can cause fires...always call it out and let the chips fall where they may.







Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
Attic wall separation from interior living space sglick Interior Inspections 4 5/27/07 9:47 PM
Spray Foam to the Rescue ? mcyr Structural Inspections 3 3/27/07 8:29 PM
Attic Space lmills Interior Inspections 2 10/3/06 4:01 PM
Is Romex in a crawl space a problem? jtedesco1 Electrical Inspections 48 9/30/06 11:53 PM


All times are GMT -4. The time now is 10:36 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts