Default Slightly uncomfortable....

I took the temp from the attic access, put it in hold mode and snapped a pic. There was one ridge vent and the blown-in insulation was blocking all of the soffit vents. Outisde temp was only about 70-75.
Attached Thumbnails
slightly-uncomfortable-img_0610.jpg  
Reply With Quote
  #2  
Old 6/28/08, 1:26 PM
iniquette's Avatar
iniquette iniquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,795
Send a message via ICQ to iniquette
Default Re: Slightly uncomfortable....

Recommend having a contractor remedy the situation because of improper airflow.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network
INACHI Awards Portal
Want To Exchange Links?



What we've got here is......failure......to communicate.....
Reply With Quote
  #3  
Old 6/28/08, 1:56 PM
kpierce's Avatar
kpierce kpierce is offline
Active Poster
 
Join Date: Jun 2008
Location: Orting, WA
Posts: 4,609
Please Note: kpierce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Slightly uncomfortable....

Yup. That's what I wrote.
Reply With Quote
  #4  
Old 6/28/08, 2:10 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Slightly uncomfortable....

Quote:
Originally Posted by kpierce
Yup. That's what I wrote.
Would be interested if you went back and measured attic temp on a still, clear July/August day with similar outdoor temps after the problem is "corrected".
Reply With Quote
  #5  
Old 6/28/08, 2:40 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: Slightly uncomfortable....

Quote:
Originally Posted by Brian A. MacNeish
Would be interested if you went back and measured attic temp on a still, clear July/August day with similar outdoor temps after the problem is "corrected".
I agree.

According to this study and several others, "average" attic temp is 40 degrees F higher than the ambient temp. Variances to that would come at different times of the day, etc.

I don't see 144 degrees as a defect. The blocked soffit vents, regardless of temperature, would be a defect.

The darker the shingles, the hotter the attic.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 6/28/08 at 2:44 PM..
Reply With Quote
  #6  
Old 6/28/08, 3:31 PM
kpierce's Avatar
kpierce kpierce is offline
Active Poster
 
Join Date: Jun 2008
Location: Orting, WA
Posts: 4,609
Please Note: kpierce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Slightly uncomfortable....

Quote:
Originally Posted by jbushart
I agree.

According to this study and several others, "average" attic temp is 40 degrees F higher than the ambient temp. Variances to that would come at different times of the day, etc.

I don't see 144 degrees as a defect. The blocked soffit vents, regardless of temperature, would be a defect.

The darker the shingles, the hotter the attic.
I didn't state in the inspection or on this forum that I thought 144 degrees was a defect. But to be the devil's advocat, according to your statement, 40 degrees above the ambient temp. would be around 115. The temp. reading was almost 70 degrees above! Also, this inspection was around 2pm.
I only noted the blockage of the soffit vents and the apparent lack of ridge vents in the inspection....and of course advised further investigation by a qualified contractor.
Reply With Quote
  #7  
Old 6/28/08, 4:06 PM
Jeff Orcas Jeff Orcas is offline
New User
 
Join Date: Apr 2008
Posts: 24
Please Note: Jeff Orcas is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Slightly uncomfortable....

Kevin,

the bigger problem in the Pacific NW isn't the high temp, its the mold that will grow on the backside of the roof in the cooler months. Warm moist air from the home will condense of the roofing and you will see dark spots. I tell my clients you can't have too much ventilation in these parts,

Jeff
Reply With Quote
  #8  
Old 6/28/08, 4:16 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Slightly uncomfortable....

Soffit vents being covered is a norm in my area. I find attic ventilation issues in 90% of the homes I inspect.

That gave me no choice but to design a web page on Attic Ventilation.

It's simply amazing to see so many re-roofs and newly constructed homes that have ventilation issues.
Reply With Quote
  #9  
Old 6/29/08, 6:48 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Slightly uncomfortable....

Quote:
Originally Posted by Jeff Orcas
Kevin,

the bigger problem in the Pacific NW isn't the high temp, its the mold that will grow on the backside of the roof in the cooler months. Warm moist air from the home will condense of the roofing and you will see dark spots. I tell my clients you can't have too much ventilation in these parts,

Jeff
HOUSE AIR LEAKAGE- There's the defect......losing heat, that isn't that cheap anymore, and letting moisture into the attic where mould may grow. So in this time of high energy costs, which would you want to do?? (1)Improve the attic venting which will in all likelyhood increase the rate of warm air loss from the home (and in some wet homes may increase the condensation in the attic) .......or (2) airseal at the ceiling level which reduces both heat loss and moisture transport to the cool/cold attic where it condenses and may, over time, rot the roof sheathing!! Your choice!!!

Stopping the moisture transport upwards (doing a good job and not lip service) usually reduces condensation enough so that additional venting is not needed!!
Reply With Quote
  #10  
Old 6/29/08, 6:57 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Slightly uncomfortable....

Quote:
Originally Posted by dvalley
Soffit vents being covered is a norm in my area. I find attic ventilation issues in 90% of the homes I inspect.

That gave me no choice but to design a web page on Attic Ventilation.

It's simply amazing to see so many re-roofs and newly constructed homes that have ventilation issues.
So what do you think about the concept of conditioned attics with no ventilation at all? Is this an issue?

My feeling is that if you are not seeing the attic at the worst time of the year (up north: coldest days in January/February), in most cases, it will be hard to truly make an accurate determination if there is a ventilation issue. I have a check box on my report that tells my clients to check the attic during this period.
Reply With Quote
  #11  
Old 6/29/08, 7:41 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Slightly uncomfortable....

Brian,
I wish there were more coming on board with the conditioned method
Maybe by the end of my career I'll see more than 1-2 a year

Insulation/ventilation



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #12  
Old 6/29/08, 9:51 AM
dplummer dplummer is offline
Active Poster
 
Join Date: Dec 2003
Location: Collingwood, ON
Posts: 236
Please Note: dplummer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Slightly uncomfortable....

Just out of curiosity, what was the indoor temp?

Doug
Reply With Quote
  #13  
Old 6/29/08, 1:05 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Slightly uncomfortable....

Quote:
Originally Posted by badair
Brian,
I wish there were more coming on board with the conditioned method
Maybe by the end of my career I'll see more than 1-2 a year

Insulation/ventilation
Barry:

By coincidence, I have been referring people to that article for 5-6 years now for the very last graphic of how to deal with kneewalls and outer attics in a truly energy efficient and cost effective manner. We were doing that in our insulation company about 1983-84.
Reply With Quote
  #14  
Old 6/29/08, 3:04 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Slightly uncomfortable....

Quote:
Originally Posted by Brian A. MacNeish
So what do you think about the concept of conditioned attics with no ventilation at all? Is this an issue?
Absolutely. Not only is this an issue...It's worse with the conditioned attics. The summer months (w/ hot attic cavities) will deteriorate that roof in less than 10 years.

Here's a roof surface that I inspected which was only 9 years old. Not a single vent was installed in the entire roof surface.
slightly-uncomfortable-shingles_no-vent-1-.jpg.JPG
Views:	45
Size:	248.6 KB
ID:	22336

The Seller ended up calling me and yelling at me for telling my Buyers that the roof shingles needed to be replaced now. She told me that she had those shingles installed nine years ago. I told her to get a roofer in to evaluate her shingles, and if her roofer says that the shingles are fine, I'll buy the new shingles for my Buyers.

She never called back. Hmmmm..I wonder why?
Reply With Quote
  #15  
Old 6/29/08, 5:07 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,932
Default Re: Slightly uncomfortable....

David,

Not fair those look like they were a 5 year shingle to start out with. They almost got twice the life!

Quote:
Originally Posted by Brian A. MacNeish
Barry:
By coincidence, I have been referring people to that article for 5-6 years now for the very last graphic of how to deal with kneewalls and outer attics in a truly energy efficient and cost effective manner. We were doing that in our insulation company about 1983-84.
Brian,
I'm sure you've seen this one that I now use

Energy efficiency and insulation instructions for attics: http://www.southface.org/web/resources&services/publications/factsheets/9atticaccess.pdf

What's your thought on Owens Pink-cap?



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good

Last edited by badair; 6/29/08 at 5:11 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Existing home sales rose slightly in February as prices drop. gromicko Miscellaneous Discussion for Inspectors 0 3/29/08 11:53 PM
Slightly unusual water heater location kweiss Plumbing Inspections 8 12/5/07 9:22 PM
Slightly elevated CO reading that went down -- explanation? fbartlo Inspecting HVAC Systems 8 9/23/06 11:10 AM


All times are GMT -4. The time now is 12:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts