This appears to be a bad location for a smoke detector to me. Does this violate any code? I'm writing it up as a safety hazard anyway but just want to know if there is a specific code that it violates.
774 Manor Road Staten Island, NY 10314 718-514-3393 |
| Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Codes are local.
On the practical side may I as what you are worried about? I am trying to understand how it is a safety hazard. |
|
#3
|
|||
|
|||
|
Please Note:
rramsey1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Good location. If fan is running, smoke will be drawn back to the return air
|
|
#4
|
||||
|
||||
|
I agree. I would think that placing it near the return would draw smoke from a wider area and give the alarm a wider range of coverage. I don't see a safety issue.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#5
|
||||
|
||||
|
Quote:
Not to put words in Johns mouth . |
|
#6
|
||||
|
||||
|
Actually, I was thinking that maybe with the fan running the return would draw smoke away from the detector and not allowing it to be activated. Am I over braining this one?
774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#7
|
||||
|
||||
|
I think you might be.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#8
|
||||
|
||||
|
When air supply and/or air return ducts are present in a room
or space, the detector(s) should not be placed in the path of the air flow supply or return (NFPA 72-2007). Placement of detectors near air conditioning or incoming air vents can cause excessive accumulation of dust and dirt on the detectors. This dirt can cause detectors to malfunction and cause unwanted alarms. Detectors should not be located closer than 3 feet from an air supply diffuser or an air return vent. flo lighting can also be a problem, you'll have to read or search on your own http://www.systemsensor.com/pdf/A05-1003.pdf ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#9
|
||||
|
||||
|
Quote:
774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#10
|
||||
|
||||
|
Quote:
ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#11
|
||||
|
||||
|
There is nothing wrong with that installation. common to more than one compartment.As in more commercial type smoke detection in ventilation equipment. Supply duct smoke detector installation should be downstream of fans, filters, chillers, heaters, and humidifiers. Duct smoke detectors in the return air stream should be located at every return air opening within the smoke compartment, or where the air exits each smoke compartment, or in the duct system before air enters the return air system The principals are the same, just a less expensive detection system. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
|
#12
|
||||
|
||||
|
Barry, Gary, tomato, tomoto. LOL.
Sorry bout that. 774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#13
|
||||
|
||||
|
Barry is most likely right due to the fact that residential systems don't have a filtration system that the like of a commercial air system.
LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
| Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
![]() Don't install smoke alarms near windows, doors, or ducts where drafts might interfere with their operation. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#15
|
||||
|
||||
|
http://www.homesecuritytopics.com/wh...detectors.html
Where not to place smoke detectors? One of the major causes of unwanted alarms is improper placement of detectors. The best way to avoid unwanted alarms is not to install detectors in environments that can cause them to malfunction, or to install detectors specially designed for those environments. Examples follow: • Excessively Dusty or Dirty Areas: In excessively dusty or dirty areas consider using the Filtrex™ smoke detector. This detector incorporates a microprocessor-controlled air intake fan and filter that allows the unit to be installed in areas where ordinary detectors cannot be used. Filtrex is an intelligent smoke detector that removes airborne particles before they reach the sensing chamber. It is ideal for textile mills, dusty manufacturing facilities, paper mills, and recycling centers. • Outdoors: Avoid using detectors outdoors, in open storage sheds, or other open structures affected by dust, air currents, or excessive humidity and temperature extremes. • Wet or Excessively Humid Areas: Avoid damp, wet or excessively humid areas, or next to bathrooms with showers. • Elevator Lobbies: Do not place over ashtrays or where people will smoke while waiting for the elevator. • Extreme Cold or Hot Environments: Avoid very cold or very hot environments, or unheated buildings or rooms where the temperature can fall below or exceed the operating temperature range of the detector. At temperatures above or below the operating range of the detector*, its internal components may not function properly. *Manufacturers’ specifications should list acceptable temperatures in these ranges. • Areas with Combustion Particles: Avoid areas where particles of combustion are normally present, such as in kitchens or other areas with ovens and burners; in garages, where particles of combustion are present in vehicle exhausts. When a detector must be located in or adjacent to such an area, a heat detector may be appropriate. • Manufacturing Areas: Avoid manufacturing areas, battery rooms, or other areas where substantial quantities of vapors, gases, or fumes may be present. Strong vapors can make detectors overly sensitive or less sensitive than normal. In very large concentrations, gases heavier than air, such as carbon dioxide, may make detectors more sensitive, while gases lighter than air, such as helium, may make them less sensitive. Aerosol particles may collect on detector chamber surfaces and cause nuisance alarms. • Fluorescent Light Fixtures: Avoid placement near fluorescent light fixtures. Electrical noise generated by fluorescent light fixtures may cause unwanted alarms. Install detectors at least 1 foot (0.3 m) away from such light fixtures. * The guidelines on this page are adapted from Standards published by the National Fire Protection Association, Quincy, Massachusetts, USA. These standards include NFPA 72, National Fire Alarm Code; NFPA 70, “National Electrical Code”, Article 760; and NFPA 90A, “Installation of Air Conditioning and Ventilating Systems”. LEED Green Associates InachiAwardsPortal: Inachi US Member of the Year Award 2009 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Water Damaged surfaces within the HVAC return - do you test? | tspargo | Inspecting HVAC Systems | 6 | 6/7/11 10:27 AM |
| Recall-Counterfeit Smoke Detectors-Atlanta | jjonas | General Inspection Discussion | 0 | 5/27/11 7:55 PM |
| 2 questions | staylor5 | Electrical Inspections | 14 | 12/18/09 2:32 AM |
| Smoke Detector placement | jwicklander | Electrical Inspections | 0 | 9/17/08 6:43 PM |
| HVAC Design - Air Return | jhaynes | Inspecting HVAC Systems | 9 | 9/16/08 7:52 PM |