Default Soffit vents no longer required?

Over the years I have heard all sorts of BS stories from new construction builders about why they did not do one thing, or another. ..It gets really old.

But I will give this guy the benefit of the doubt (for a minute), and accept the fact that I don't always know everything, and some times codes do change.

So has any one heard of a code change that eliminates the requirement for soffit vents (bird block vents)? In this case there are no soffit vents any where, and I could see that a minimal amount of box vents were installed lower on the roof near the soffits instead. The builder stated that new building and fire codes required this installation.

I have researched, but fail to find anything supporting his position.

So what do you guys know about this?



Everett Home Inspector
www.millerhomeinspect.com

Miller Home Inspection
Washington State Licensed Home Inspector #209
Camano Island WA

425-501-2382
Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/29/11, 9:18 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,575
Default Re: Soffit vents no longer required?

Only time I have heard of this is when using foam or Icynene type of insulation



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #3  
Old 6/29/11, 9:23 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,611
Default Re: Soffit vents no longer required?

http://jobsite.buildiq.com/articles/...ted-attic.aspx


http://www.greenhorizon.com/files/JL...ray%20Foam.pdf


http://www.wriapplications.com/atticinsulation.php



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #4  
Old 6/29/11, 9:50 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Soffit vents no longer required?

Call your AHJ and find out.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 6/29/11, 10:53 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Soffit vents no longer required?

Quote:
Originally Posted by hmiller View Post
Over the years I have heard all sorts of BS stories from new construction builders about why they did not do one thing, or another. ..It gets really old.

But I will give this guy the benefit of the doubt (for a minute), and accept the fact that I don't always know everything, and some times codes do change.

So has any one heard of a code change that eliminates the requirement for soffit vents (bird block vents)? In this case there are no soffit vents any where, and I could see that a minimal amount of box vents were installed lower on the roof near the soffits instead. The builder stated that new building and fire codes required this installation.

I have researched, but fail to find anything supporting his position.

So what do you guys know about this?
Could be fire codes.

About 5-6 years ago I was called into some new ~100 units apartment buildings with attic moisture problems that had already been "addressed" by a consulting engineer but the problem still persisted.

A large number of vents had been installed all over the roofs (5-6/12 slopes with regular asphalt shingles). It had a bit of a postive effect but did not solve the problem fully. Building interior ventilation and attic airsealing were both NOT ADDRESSED by the engineer!!

While I was there, I noticed that the over hanging soffit material was solid metal, not perforated as would be expected. Was told by one of the project architects that fire codes on these 3-4 story buildings would not allow the perforated soffits to prevent fire/smoke entry into the attics.

(Note- I don't deal in fire codes for commercial, and other large buildings so this is second hand, hearsay info)
Reply With Quote
  #6  
Old 6/30/11, 1:56 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Soffit vents no longer required?

I'll ask the obvious question: Where does/did the code ever say that soffit vents are required?

See Section R806 for requirements



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #7  
Old 6/30/11, 8:45 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Soffit vents no longer required?

Quote:
Originally Posted by cevans View Post
I'll ask the obvious question: Where does/did the code ever say that soffit vents are required?

See Section R806 for requirements
Not even a requirement for soffits that I am aware of.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 6/30/11, 10:13 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Soffit vents no longer required?

Well, the requirement for soffit vents was established by the architect who drafted the engineered plans, of which a copy was still in this home on the day of the inspection. It read that soffit vents were to be installed 24" O.C.

And R806 states that the ventilation must be balanced. Because you must have a minimum of 1/150 net free ventilation that is balanced, you are going to need just as many box vents along the lower portion as up at the ridge.

I think they new this looked like crap so they have about half as many below.

Funny thing is the insulator baffled the soffits for ventilation, as they normally do.



Everett Home Inspector
www.millerhomeinspect.com

Miller Home Inspection
Washington State Licensed Home Inspector #209
Camano Island WA

425-501-2382
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM
Massachusetts Board of Registration of Home Inspectors jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 0 2/14/06 3:38 AM


All times are GMT -4. The time now is 1:05 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts