Default Stupid question about CO detectors

Stupid question about CO detectors. I have a few realtors that are fighting me about if the CO2 detector should be permanently installed or if they can just use the ones that plug into the wall.
I just want to make sure sure I was telling them the right thing

Last edited by hcoleman2; 3/3/11 at 5:12 PM..
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/3/11, 6:38 AM
Vince Santos's Avatar
Vince Santos Vince Santos is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Canton, MI - Serving Souteast Michigan
Posts: 1,786
Default Re: Stupid question about CO2 detectors

Why are you worried about carbon dioxide, beer been a little flat lately?

When I report on the lack of carbon monoxide (CO) detectors I just recommend installing. To me it doesn't matter if it's hardwired or a plug in system and I don't know of any requirements for one or the other.



Vince Santos
StepByStep Home Services LC
(734) 748-9584
Providing Home Inspection Services to Southeast Michigan
facebook
ITA Trained and Certified

Reply With Quote
  #3  
Old 3/3/11, 8:41 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Stupid question about CO2 detectors

There is no requirement in the IRC for a CO monitor. Some local ordinances require it, but it's not a national thing.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 3/3/11, 8:48 AM
Vaughn Hill's Avatar
Vaughn Hill Vaughn Hill is offline
InterNACHI Member
 
Join Date: May 2009
Location: Monroe Michigan
Posts: 648
Default Re: Stupid question about CO2 detectors

House builders in Colorado are required to install carbon monoxide detectors in new homes in a bill signed into law in March 2009 by the state legislature.
House Bill 1091 requires installation of the detectors in new and resold homes near bedrooms as well as rented apartments and homes. It took effect on July 1, 2009. The legislation was introduced after the death of Denver investment banker Parker Lofgren and his family. Lofgren, 39; his wife Caroline, 42; and their children, Owen, 10, and Sophie, 8, were found dead in a multimillion-dollar home near Aspen, Colorado on Nov. 27, 2008, victims of carbon-monoxide poisoning.
In New York State, Amanda's Law,” (A6093A/C.367) requires one- and two-family residences which have fuel burning appliances to have at least one carbon monoxide alarm installed on the lowest story having a sleeping area, effective since February 22, 2010. Although homes built before Jan. 1, 2008 are allowed to have battery-powered alarms, homes built after that date need to have hard-wired alarms. In addition, New York State contractors have to install a carbon monoxide detector when replacing a fuel burning water heater or furnace if the home is without an alarm. The law is named for Amanda Hansen, a teenager who died from carbon monoxide poisoning from a defective boiler while at a sleepover at a friend's house.
In July 2011, California will require installation of carbon monoxide detectors in existing single-family homes, with multifamily homes following in 2013.



Monroe Home Inspection
3168 Orchardale st.
Monroe,MI 48162
734-289-2190




Reply With Quote
  #5  
Old 3/3/11, 10:13 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Stupid question about CO2 detectors

CO detectors are required in MN and WI



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #6  
Old 3/3/11, 10:44 AM
dmcauley's Avatar
dmcauley dmcauley is offline
Active Poster
 
Join Date: Jan 2006
Location: Hoffman Estates, IL
Posts: 854
Please Note: dmcauley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid question about CO2 detectors

Illinois has required them since January 1, 2007. Doesn't matter if hard wired or plug ins, as long as they are within 15 feet of sleeping areas.
Reply With Quote
  #7  
Old 3/3/11, 10:46 AM
rspermo rspermo is offline
Active Poster
 
Join Date: Feb 2009
Posts: 155
Please Note: rspermo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Stupid question about CO2 detectors

In these states that require CO detectors, I am wondering at what PPM of CO do they require that they actually go off? Most of the ones I see produce an alarm at 60 - 70 ppm after 1 - 4 hrs. I consdier these UL approved CO detectors to be almost useless.
Reply With Quote
  #8  
Old 3/3/11, 11:33 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Stupid question about CO2 detectors

Quote:
Originally Posted by rspermo View Post
In these states that require CO detectors, I am wondering at what PPM of CO do they require that they actually go off? Most of the ones I see produce an alarm at 60 - 70 ppm after 1 - 4 hrs. I consdier these UL approved CO detectors to be almost useless.
Why?

Quote:
At what level does carbon monoxide become toxic?
For healthy adults, CO becomes toxic when it reaches a level higher than 50 ppm (parts per million) with continuous exposure over an eight hour period.. When the level of CO becomes higher than that, a person will suffer from symptoms of exposure. Mild exposure over a few hours (a CO level between 70 ppm and 100 ppm) include flu-like symptoms such as headaches, sore eyes and a runny nose. Medium exposure (a CO level between 150 ppm to 300 ppm) will produce dizziness, drowsiness and vomiting. Extreme exposure (a CO level of 400 ppm and higher) will result in unconsciousness, brain damage and death.
http://www.carbon-monoxide-poisoning...co-levels.html



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #9  
Old 3/3/11, 12:57 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,172
Default Re: Stupid question about CO2 detectors

http://www.health.state.mn.us/divs/e.../co/index.html

Quote:
Minnesota State Law requires that homes have at least one operational CO alarm within 10 feet of every room legally used for sleeping (see Minnesota Statute, 299F.50). All CO alarms should be certified by a nationally recognized testing laboratory to conform to the latest Underwriters Laboratory (UL) Standards. Follow the manufacturer's instructions for placement of your CO alarm and also note the suggested replacement date. For additional information on CO alarms, call 651-201-7200 or visit www.fire.state.mn.us
Reply With Quote
  #10  
Old 3/3/11, 1:41 PM
David Hays David Hays is offline
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Stupid question about CO2 detectors

A Precise Home Inspections in Colorado Springs has a nice article about the placement of the detectors.

Thanks Lance!

http://aprecisehomeinspection.com/CO2article.html



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #11  
Old 3/3/11, 3:02 PM
Vince Santos's Avatar
Vince Santos Vince Santos is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Canton, MI - Serving Souteast Michigan
Posts: 1,786
Default Re: Stupid question about CO2 detectors

Quote:
Originally Posted by dhays View Post
A Precise Home Inspections in Colorado Springs has a nice article about the placement of the detectors.

Thanks Lance!

http://aprecisehomeinspection.com/CO2article.html
Interesting article. My question is if carbon monoxide is lighter than air and tends to rise what difference would that make? If the furnace is running and forcing air into various room and that air is also being drawn into the returns, wouldn't that circulate the carbon monoxide too?

"High or low in a room; It makes no difference where you put the detector
-- but not because carbon monoxide and air have approximately the same
density. Both are gases and as a result, diffusion alone and the entropy
effect will take care of mixing them. Any convection currents and/or
forced-air turbulence present will also enable the gases to mix and affect
the detector."

http://www.newton.dep.anl.gov/askasc.../chem03364.htm



Vince Santos
StepByStep Home Services LC
(734) 748-9584
Providing Home Inspection Services to Southeast Michigan
facebook
ITA Trained and Certified


Last edited by vsantos; 3/3/11 at 3:07 PM..
Reply With Quote
  #12  
Old 3/3/11, 4:48 PM
Hans Coleman's Avatar
Hans Coleman Hans Coleman is offline
InterNACHI Member
 
Join Date: Jan 2011
Location: Denver
Posts: 34
Default Re: Stupid question about CO detectors

WOW major typo... That why I should not post at 5AM

Last edited by hcoleman2; 3/3/11 at 5:10 PM..
Reply With Quote
  #13  
Old 3/3/11, 6:46 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Stupid question about CO2 detectors

Quote:
Originally Posted by vsantos View Post
Why are you worried about carbon dioxide, beer been a little flat lately?

When I report on the lack of carbon monoxide (CO) detectors I just recommend installing. To me it doesn't matter if it's hardwired or a plug in system and I don't know of any requirements for one or the other.
It should be within six inches of the ceiling corner.
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/3/11, 6:55 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,172
Default Re: Stupid question about CO2 detectors

Quote:
Originally Posted by belliott View Post
It should be within six inches of the ceiling corner.
Is that a Chicago thing? Certainly not a manufactures instruction.
Reply With Quote
  #15  
Old 3/3/11, 7:03 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Stupid question about CO detectors

http://www.cpsc.gov/cpscpub/pubs/466.html

How should I install a CO Alarm?


CO alarms should be installed according to the manufacturer's instructions. CPSC recommends that one CO alarm be installed in the hallway outside the bedrooms in each separate sleeping area of the home. CO alarms may be installed into a plug-in receptacle or high on the wall. Hard wired or plug-in CO alarms should have battery backup. Avoid locations that are near heating vents or that can be covered by furniture or draperies. CPSC does not recommend installing CO alarms in kitchens or above fuel-burning appliances.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Stupid service amperage question jfunderburk Electrical Inspections 14 1/29/09 11:07 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Plumbing vent Routing Question kweiss Plumbing Inspections 7 11/1/06 9:57 PM


All times are GMT -4. The time now is 1:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts