Default Subpanel for new addition?

Hi Guys

I have a thirty year old 1000 SF country house that is having an 1100 SF addition added giving it a total of 2100 SF. The old wiring (125 amp on the main breaker on the outside wall) was owner installed and was barely adequate at the time. I want to have the meter moved to the side rear of the new addition with underground service installed.
Can I install a temporary connection (maybe 40 amp) from the old panel to the new main distribution panel until the power company makes the connection at the new meter location? The new main panel would temporaryly function as a subpanel. After that I can relocate the other circuits from the old to the new panel one at a time. Is this practical or could you point me to a better way?

Thanks.

Stan Kuter

Last edited by Stan Kuter; 11/13/08 at 6:09 PM..
Reply With Quote
  #2  
Old 11/13/08, 6:08 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Subpanel for new addition?

I want through a similar situation this past year when I added 1800 SF. I had to have an engineer from the elect. utility come to my house and meet me and the electrician. Together, we all worked out a plan for temp. power and thought through when and how to do the permanent underground connection. I strongly suggest you get the elect. utility involved with your electrician.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 11/13/08, 8:24 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Subpanel for new addition?

Yes you probably can install the panel temporarily as a sub. Always consult with local authorities.
Even if you only need a 40 amp breaker for now, I would suggest running a large enough feeder to the new panel, eg one that can handle 100 amps or more. That way you can turn your old panel into a sub and leave most of the existing wiring in place. You must be clear on bonding and grounding differences between main panels and sub panels, as you will be changing both when you get the new service installed. Best to hire an electrician and get the benefit of his local knowledge.

John Kogel
www.allsafehome.ca
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Discolored service conductor, bonded subpanel dalvares Electrical Inspections 3 11/6/08 10:44 PM
SubPanel bonded, ? lfoster Electrical Inspections 5 1/9/08 5:08 AM
Addition dlee2 Structural Inspections 1 8/9/07 7:59 PM
Subpanel feeders jschulte Electrical Inspections 9 8/17/06 9:08 PM


All times are GMT -4. The time now is 11:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts