Default Subpanel Unsafe?

I recently inspected a 80 year old house that main electric panel was located in a detached garage ten feet from the house. The main panel was rated for 200 AMP and had a 100 AMP 240-volt feed to a subpanel in the house. The subpanel in the house had no main breaker and required more than six breakers to turn off power to the house. Would you call out the subpanel in the house as unsafe, and recommend a profesessional electrician evaluate the subpanel?

Dover, DE
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/24/10, 11:48 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Subpanel Unsafe?

No. The main panel was where the main shut off was. This is no more "unsafe" than if there were no sub panel, and all the breakers were in the garage.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 10/25/10, 8:58 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Subpanel Unsafe?

1) In my experience, there is a good possibility such a system is improperly bonded/grounded by current standards, and perhaps even by the standards in effect at the time it was installed.

2) This type of installation (for example a disconnect out the pole at the end of the driveway) is more common in rural and outer suburban areas, and AHJs in some more urban areas may not accept a service disconnect for a main structure in a detached auxiliary structure.

3) IMO, reports should explicitly document all situations were an energized panel or circuit my not be obvious to occupants , ex: the attached is from a report last week, where there was no OCPD ahead of a load-side panel:
Attached Thumbnails
subpanel-unsafe-fpe-02.jpg  
Reply With Quote
  #4  
Old 10/25/10, 9:06 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Subpanel Unsafe?

Quote:
The subpanel in the house had no main breaker and required more than six breakers to turn off power to the house.
There is no requirement for a main disconnect in any subpanel, regardless of what it feeds or how many breakers it has.

As far as the post warning of improper grounding or bonding, ensure that the sub is fed with four conductors, with the grounds and neutrals segregated in the sub-panel. Look for the floating neutral bus bar...
Reply With Quote
  #5  
Old 10/25/10, 7:28 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Subpanel Unsafe?

Quote:
Originally Posted by jfarsetta View Post
There is no requirement for a main disconnect in any subpanel, regardless of what it feeds or how many breakers it has.

As far as the post warning of improper grounding or bonding, ensure that the sub is fed with four conductors, with the grounds and neutrals segregated in the sub-panel. Look for the floating neutral bus bar...
Do you mean "3 conductors and a ground"?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
underamped subpanel?? wstafford Electrical Inspections 12 5/13/09 5:08 PM
Neutral/ground bond in subpanel gkeene Electrical Inspections 2 1/23/09 10:14 PM
Discolored service conductor, bonded subpanel dalvares Electrical Inspections 3 11/6/08 9:44 PM
Subpanel Bonding Screw away Electrical Inspections 24 1/9/08 2:46 PM


All times are GMT -4. The time now is 1:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts