Default Is there anything wrong with this flex install?




Was told this install was not correct by gas company workers . have no specific things that were wrong just that it was wrong. is it the down turn after the trap before the flex pipe?
Attached Thumbnails
there-anything-wrong-flex-install-p1010687.jpg  
Reply With Quote
  #2  
Old 10/16/08, 8:38 PM
rshuey rshuey is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Mar 2007
Posts: 198
Please Note: rshuey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is there anything wrong with this flex install?

Ron,

I loved all your movies.
Reply With Quote
  #3  
Old 10/16/08, 11:02 PM
Jeff Merritt Jeff Merritt is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Chicago, IL
Posts: 1,162
Default Re: Is there anything wrong with this flex install?

Flex line can not go thru a steel cabinet. Its hard to see in the photo
Reply With Quote
  #4  
Old 10/16/08, 11:07 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,338
Send a message via Yahoo to jfunderburk
Default Re: Is there anything wrong with this flex install?

I don't see the problem. But use the correct terminology: "appliance connector".



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 10/16/08, 11:20 PM
Ron Jeremy Ron Jeremy is offline
New User
 
Join Date: Oct 2008
Posts: 4
Please Note: Ron Jeremy is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is there anything wrong with this flex install?

Sorry about terminology. appliance connector does not go through cabinet it connects right outside cabinet. Going to get rid of bend and hope it makes them happy.Has anyone came accross utility works that are just old fashioned and just dont like flexable piping instead of ridged?
Reply With Quote
  #6  
Old 10/16/08, 11:35 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Is there anything wrong with this flex install?

Make sure the appliance connector is 36" or less also. I agree that getting rid of the 90 degree down bend by rotating it would probably be wise. Also, be sure the gas piping is supported properly. Personally, I'd be more concerned about whatever that is that was used on the W/H TPRV discharge piping. Make sure that's an approved material.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #7  
Old 10/17/08, 1:00 AM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 1,122
Send a message via Yahoo to gpallotta
Default Re: Is there anything wrong with this flex install?

Hi Ron
The flex line has to be connectted to a tee. The elbow there is against code.

6.11.4 Where an appliance is connected to a flexible piping or tubing system connection to the appliance shall be outside the cabinet and into a tee fitting containing a drip pocket and rigid piping that extends to the appliance gas valve.

Hope this helps.
Reply With Quote
  #8  
Old 10/17/08, 1:12 AM
dbucknavich dbucknavich is offline
Active Poster
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 653
Please Note: dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is there anything wrong with this flex install?

Quote:
Originally Posted by gpallotta View Post
Hi Ron
The flex line has to be connectted to a tee. The elbow there is against code.

6.11.4 Where an appliance is connected to a flexible piping or tubing system connection to the appliance shall be outside the cabinet and into a tee fitting containing a drip pocket and rigid piping that extends to the appliance gas valve.

Hope this helps.
Very nice Gerry
Reply With Quote
  #9  
Old 10/17/08, 1:25 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,903
Default Re: Is there anything wrong with this flex install?

Quote:
Originally Posted by Ron Jeremy View Post



Was told this install was not correct by gas company workers . have no specific things that were wrong just that it was wrong. is it the down turn after the trap before the flex pipe?
Sorry I hated your movies, as all that back hair just ruined the mood .

Ron , the drip leg needs to protect the gas valve and it is down stream in this picture.

(sorry , I just saw this thread.)

Put that shutoff on the tee!
Reply With Quote
  #10  
Old 10/17/08, 1:43 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Is there anything wrong with this flex install?

Sorry Bob but you are wrong on the placement of the valve. This is the correct positioning. In order to clean out the drip leg, it would have to be after the valve so the gas can be turned off to remove the cap.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #11  
Old 10/17/08, 1:50 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,903
Default Re: Is there anything wrong with this flex install?

Quote:
Originally Posted by sstanczyk View Post
Sorry Bob but you are wrong on the placement of the valve. This is the correct positioning. In order to clean out the drip leg, it would have to be after the valve so the gas can be turned off to remove the cap.
The drip leg is there to protect the valve Steven.

Buzzzzzzzzzzz...wrong answer.
Reply With Quote
  #12  
Old 10/17/08, 1:55 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Is there anything wrong with this flex install?

Quote:
Originally Posted by relliott View Post
The drip leg is there to protect the valve Steven.

Buzzzzzzzzzzz...wrong answer.
Wrong Bob. So how do you propose to clean out the drip leg? Turn off the gas to the whole home?

You aren't protecting the shut off valve, it is either open or shut. You are protecting the burner/orifice of the unit.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #13  
Old 10/17/08, 1:58 AM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,091
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is there anything wrong with this flex install?

Quote:
Originally Posted by gpallotta View Post
Hi Ron
The flex line has to be connectted to a tee. The elbow there is against code.

6.11.4 Where an appliance is connected to a flexible piping or tubing system connection to the appliance shall be outside the cabinet and into a tee fitting containing a drip pocket and rigid piping that extends to the appliance gas valve.

Hope this helps.
What model code is that Gerry? Must be a regional thing. I almost never find tees or drip legs on gas supply lines to any appliances here in california. Older structures ocassionally, last 25 years or so, never....
Reply With Quote
  #14  
Old 10/17/08, 2:02 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,903
Default Re: Is there anything wrong with this flex install?

Quote:
Originally Posted by whandley View Post
What model code is that Gerry? Must be a regional thing. I almost never find tees or drip legs on gas supply lines to any appliances here in california. Older structures ocassionally, last 25 years or so, never....
Drip legs are always required, but darn it Steven got me on the placement issue.

I should have cheated and looked it up first.

First time I ever heard of them not being rquired some where.
You Californians are a bunch of freaks.
Reply With Quote
  #15  
Old 10/17/08, 2:21 AM
Gerry Pallotta's Avatar
Gerry Pallotta Gerry Pallotta is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Mississauga, ON
Posts: 1,122
Send a message via Yahoo to gpallotta
Default Re: Is there anything wrong with this flex install?

Hi Will

It's based on the Canadian Standards Association code B149. Which is our National natural gas and propane code.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to install a water filtration system? dmacy Plumbing Inspections 22 6/30/08 8:16 AM
Free Books And Articles For Electrical jtedesco1 Electrical Inspections 14 1/6/08 6:45 PM
Flex Gas Connector Tab M. Wilcox Plumbing Inspections 4 3/16/06 4:01 PM