Default TPR Drain pipe

What do you think about this copper drain pipe. I remember reading something about it not supposed to routed upward?
Attached Thumbnails
tpr-drain-pipe-img_0089.jpg  
Reply With Quote
  #2  
Old 3/6/08, 10:25 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: TPR Drain pipe

You are right....that is wrong !!!



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 3/6/08, 11:27 PM
Richard A. Moran, 2nd Richard A. Moran, 2nd is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Clarksville, MD
Posts: 151
Default Re: TPR Drain pipe

Morgan, check around the NACHI site. There is a TPR on-line course.

Dick



Dick Moran
True Blue Home Inspections
A Div of RAM2, LLC.
Clarksville, MD
240-832-6838
MD Home Inspector License 29927
Reply With Quote
  #4  
Old 3/7/08, 12:11 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: TPR Drain pipe

Absolutely, 100% wrong. The discharge pipe, that is. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 3/7/08, 12:18 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Drain pipe

Quote:
Originally Posted by mwood1
What do you think about this copper drain pipe. I remember reading something about it not supposed to routed upward?
Correct, must drain by gravity into atmosphere (air gap) in the same room as WH, no more than 6" from floor.
Reply With Quote
  #6  
Old 3/7/08, 10:30 PM
mwood1 mwood1 is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Mandeville, La
Posts: 55
Please Note: mwood1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Drain pipe

Thanks guys.
Reply With Quote
  #7  
Old 3/8/08, 1:53 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: TPR Drain pipe

From http://www.nachi.org/plumbingcoursereleased2008.htm

Discharge Pipe on TPR Valve:
The following are thirteen requirements for a discharge pipe serving a TPR valve: 1) The pipe should not be directly connected to the drainage system; 2) The pipe should discharge through an air gap located in the same room as the water heater; 3) The pipe should be constructed of materials tested, rated, and approved for such use; 4) The pipe should not be smaller than the diameter of the outlet of the valve served and should discharge full size to the air gap; 5) The pipe should not have valves or tee fittings installed; 6) The pipe should not have a threaded end; 7) The pipe should serve a single relief device and should not connect to piping serving any other relief device or equipment; 8) The pipe should discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping should be first piped to an indirect waster receptor through an air hap located in a conditioned space; 9) The pipe should not terminate more than 6 inches (152 mm) above the floor or waste receptor; 10) The pipe should discharge in a manner that does not cause personal injury or structural damage; 11) The pipe should be installed so as to flow by gravity; 12) The pipe should discharge to a termination point that is readily observable by the building occupants; and 13) The pipe should not be trapped.

The termination of a relief valve discharge pipe should always be visible and conspicuous. An air gap is necessary to prevent backflow and contamination of the potable water system. The discharge pipe must not be reduced in size, and must not be less than the size of the relief valve outlet. A reduction in size will act as a restriction and would impede the flow rate of the discharge. Relief valves must not be exposed to freezing temperatures. The slow drip of a leaking valve in freezing temperatures would cause ice to form and restrict the discharge and disable the valve.
Reply With Quote
  #8  
Old 3/8/08, 10:30 AM
iniquette's Avatar
iniquette iniquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,795
Send a message via ICQ to iniquette
Default Re: TPR Drain pipe

kind of curious as to who installed that, I wonder if they really thought it was correct.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network
INACHI Awards Portal
Want To Exchange Links?



What we've got here is......failure......to communicate.....
Reply With Quote
  #9  
Old 3/8/08, 12:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: TPR Drain pipe

Quote:
The pipe should not terminate more than 6 inches (152 mm) above the floor or waste receptor;
In CA, it must be more than six inches. CPC requires termination between 6" and 24" from the floor or receptor.

Also, it is not allowed to drain into the water heater overflow pan.

Just food for thought Ben. Also, when you start work on the water heater course, let me know. I'll help with info on the Watts 210 valve and it's requirements. I hear these are a rarity in the East and Mid-West.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 3/8/08, 10:11 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: TPR Drain pipe

Yep. A relief-valve pipe terminating into a water leak catch pan is not permitted, because the pan is not an indirect waste receptor. Most pans have only a ¾ inch-diameter (19 mm) drain outlet, which is not capable of gravity draining the pressurized discharge of the relief valve at full flow. (Section 5.17 InterNACHI Plumbing Course)
Thanks.

"In CA, it must be more than six inches. CPC requires termination between 6" and 24" from the floor or receptor." That's terrible. I've seen TPR valves blow at full flow. The discharge is all over the place at 6 inches from the floor. I can't imagine the damage that can be caused at two feet from the floor.
Reply With Quote
  #11  
Old 3/8/08, 11:24 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: TPR Drain pipe

Quote:
Originally Posted by bgromicko
Yep. A relief-valve pipe terminating into a water leak catch pan is not permitted, because the pan is not an indirect waste receptor.
How is that different from simply terminating 6" from the floor?
Reply With Quote
  #12  
Old 3/9/08, 10:15 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: TPR Drain pipe

If the TPR discharge pipe terminates 6" from the floor (which is good) and into a water leak catch pan that is on the floor (which is not good) - I would "flag it" so to speak.
Reply With Quote
  #13  
Old 3/9/08, 11:14 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: TPR Drain pipe

Quote:
Originally Posted by bgromicko
From http://www.nachi.org/plumbingcoursereleased2008.htm

Discharge Pipe on TPR Valve:
The following are thirteen requirements for a discharge pipe serving a TPR valve: 1) The pipe should not be directly connected to the drainage system; 2) The pipe should discharge through an air gap located in the same room as the water heater; 3) The pipe should be constructed of materials tested, rated, and approved for such use; 4) The pipe should not be smaller than the diameter of the outlet of the valve served and should discharge full size to the air gap; 5) The pipe should not have valves or tee fittings installed; 6) The pipe should not have a threaded end; 7) The pipe should serve a single relief device and should not connect to piping serving any other relief device or equipment; The pipe should discharge to the floor, to an indirect waste receptor or to the outdoors. Where discharging to the outdoors in areas subject to freezing, discharge piping should be first piped to an indirect waster receptor through an air hap located in a conditioned space; 9) The pipe should not terminate more than 6 inches (152 mm) above the floor or waste receptor; 10) The pipe should discharge in a manner that does not cause personal injury or structural damage; 11) The pipe should be installed so as to flow by gravity; 12) The pipe should discharge to a termination point that is readily observable by the building occupants; and 13) The pipe should not be trapped.

The termination of a relief valve discharge pipe should always be visible and conspicuous. An air gap is necessary to prevent backflow and contamination of the potable water system. The discharge pipe must not be reduced in size, and must not be less than the size of the relief valve outlet. A reduction in size will act as a restriction and would impede the flow rate of the discharge. Relief valves must not be exposed to freezing temperatures. The slow drip of a leaking valve in freezing temperatures would cause ice to form and restrict the discharge and disable the valve.
Darn know it alls



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #14  
Old 3/9/08, 11:43 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: TPR Drain pipe

Oh my Goodness! Hardly. I'm the worse source for quick information. I spent weeks of reading and studying and editing my plumbing course. I'm really good at finding something to say and copy-pasting it in the message board. lol

For my next nachi.tv video, which may be about notching defects in conventional lumber, I will probably spend 80 hours reading about it. I'm slow man, slow, like walking through a 2-feet deep pool of honey in winter. slow.
Reply With Quote
  #15  
Old 3/10/08, 1:39 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: TPR Drain pipe

Ben, the bro must be paying some pretty good coin to get you out there.

Maybe I can work for ole Nicky when I retire too : )



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 36 10/27/10 11:21 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 9:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 7:39 PM
Question about mold on the inside of a drain pipe abishop Plumbing Inspections 3 4/11/07 10:35 PM
drain pipe nbhi Plumbing Inspections 6 4/5/06 11:51 PM


All times are GMT -4. The time now is 4:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts