Where do I get wire ampacities? Also according to one thread for the breaker sizing of the AC or heat pump, you can breaker for the maximum rating and wire for the minimum rating. Where do I find this information?
|
| Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I have never seen it in writing but about all heating and cooling contractors say that. It is acceptable in my area.
Braun Inspection Consultants Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
|
|
#3
|
||||
|
||||
|
Nick Gromicko, Certified Master Inspector Find a Home Inspector "Just as iron sharpens iron, one man sharpens another." Proverbs 27:17 |
|
#4
|
||||
|
||||
|
General ampacities are outlined in the link posted by Nick. The NEC (or the Canadian version of the same) will give you much greater detail including wiring requirements for motors and such.This info is available on the data-plate of the appliance.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
The wire size is on the data plate? When did they start doing that?
Braun Inspection Consultants Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
|
|
#6
|
||||
|
||||
|
These two links and the code book should get you everything you need to know....
http://ecmweb.com/nec/code_calc_072304/ http://www.nachi.org/forum/f19/12-wi...-circuit-5629/ B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#7
|
||||
|
||||
|
Quote:
For instance, the minimum circuit ampacity may be rated at 28.8 amps, so it should be wired with conductors rated for at least 30 amps. Next to that, it will list the maximum breaker or fuse - let's say it says 45 amps. So in this case, you can have a 45 amp breaker serving 10AWG conductors and the installation would be compliant with both the NEC and the appliance listing. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Okay, thanks!
Braun Inspection Consultants Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Evaluating your home's wiring system | mcyr | Electrical Inspections | 0 | 12/30/09 1:31 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |
| Proper Marr Connectors for Aluminum Pigtails | jskrypka | Canadian Inspectors | 5 | 3/25/07 10:41 PM |