Default Hot Breaker & Moisture Seen With IR

Suprise... Hot breaker found at the bottom of panel (I turned it off after the picture and
told the the owner of the house). It did not feel that warm on the front so I am glad
the IR camera found it. It was a 15 amp breaker with correct wire size.

Did the breaker trip off? No.

So what provides better protection from being sued... the SoP or aggressive inspection
methods and tools?

Now you know why I use the IR camera on ALL inspections. No exceptions.



Looks like a fine fireplace with dry walls? Wrong.
Moisture found above the mantel with IR camera. Your blind without it.





Watch Thermal Imaging Video



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 11/2/07 at 1:52 PM..
Reply With Quote
  #2  
Old 11/2/07, 4:31 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hot Breaker & Moisture Seen With IR

John I also have had my training and I question what you are showing especially on the breaker. You are not giving any specifics such as emissivity settings, reflective, What angle you were standing to the wall with the glass pic. The breaker indicated 272 degrees but you stated it did not feel that hot. 272 degrees you could not touch and their would have been something melted. I can make the camera read that high on a breaker with the wrong emissivity setting. What did your infrared thermometer read on the breaker. What did your moisture meter detect on the wall in relation to what your camera was detecting. Don't take me wrong I believe in these cameras also but I also believe in backing the camera with another test device as they taught in class.
Just as an after thought the fireplace you are indicating moisture within could also have been effected by a circulating ceiling fan or an A/C register pointed toward the wall.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 11/2/07, 4:48 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
So what provides better protection from being sued... the SoP or aggressive inspection methods and tools?
We know that the SOP have withstood the legal litmus tests.
Is there a SOP for home inspections which set the standards for its use and limitations? If not the courts will most likely set one when a peeved client feels some home inspector with a IR camera was negligent in rendering an opinion or omitting a scan or other instance where they feel harmed or suffered a loss.

Is there an SOP for use of IR by the industry?

Cheers,
Reply With Quote
  #4  
Old 11/2/07, 4:53 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot Breaker & Moisture Seen With IR

I always check areas with a moisture meter. And like Charlie said cool air blowing on the surface always appears darker or wet. Corners almost always are cooler and not moist.
Attached Thumbnails
hot-breaker-and-moisture-seen-ir-ir_0035-small-.jpg.jpg
Views:	37
Size:	27.2 KB
ID:	15757   hot-breaker-and-moisture-seen-ir-pa180068-small-.jpg.JPG
Views:	47
Size:	34.5 KB
ID:	15758  
Reply With Quote
  #5  
Old 11/2/07, 5:13 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
Originally Posted by cbottger
John I also have had my training and I question what you are showing especially on the breaker. You are not giving any specifics such as emissivity settings, reflective, What angle you were standing to the wall with the glass pic. The breaker indicated 272 degrees but you stated it did not feel that hot. 272 degrees you could not touch and their would have been something melted. I can make the camera read that high on a breaker with the wrong emissivity setting. What did your infrared thermometer read on the breaker. What did your moisture meter detect on the wall in relation to what your camera was detecting. Don't take me wrong I believe in these cameras also but I also believe in backing the camera with another test device as they taught in class.
Just as an after thought the fireplace you are indicating moisture within could also have been effected by a circulating ceiling fan or an A/C register pointed toward the wall.
Breaker was so hot underneath that I could not touch it.
The front felt a little warm but the heat was coming off
the bottom. The plastic had deformed a little and I turned
if off before any real damage took place.

Wall had tons of moisture showing with moisture meter.

Emissivity settings, and reflective consideration did not matter
on this find, since it was verfied with double and triple methods.

When you say to use other methods to verify, you are preaching
to the choir. All I can say is Amen!



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.


Last edited by jmckenna1; 11/2/07 at 5:31 PM..
Reply With Quote
  #6  
Old 11/2/07, 5:18 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
Originally Posted by rwand1
We know that the SOP have withstood the legal litmus tests.
Is there a SOP for home inspections which set the standards for its use and limitations? If not the courts will most likely set one when a peeved client feels some home inspector with a IR camera was negligent in rendering an opinion or omitting a scan or other instance where they feel harmed or suffered a loss.

Is there an SOP for use of IR by the industry?

Cheers,
I will let the inspectors who get sued for moisture, mold and decay tell you
how much the SoP protected them. I don't want any of my clients to
have their house burn down... so I will try and find all I can.

Others can debate about the legal issues and I will avoid staying out
of court by finding as much as I can. I'm sure there are other inspectors
who are smarter than me, but this is my plan.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #7  
Old 11/2/07, 5:19 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
Originally Posted by ldapkus
I always check areas with a moisture meter. And like Charlie said cool air blowing on the surface always appears darker or wet. Corners almost always are cooler and not moist.
Ditto, but not this time.
It was good old water penetration.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #8  
Old 11/2/07, 5:21 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Breaker & Moisture Seen With IR

Why debate the obvious? Your not building my confidence guys.
The breaker was HOT and the wall was WET. Trust me, I was there.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #9  
Old 11/2/07, 5:44 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot Breaker & Moisture Seen With IR

How did the moisture get behind the wall? Was it sweating?
Reply With Quote
  #10  
Old 11/2/07, 5:49 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
Originally Posted by ldapkus
How did the moisture get behind the wall? Was it sweating?
Chimney flashing leak.
Happens all the time.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #11  
Old 11/2/07, 7:44 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
Originally Posted by jmckenna1
Why debate the obvious? Your not building my confidence guys.
The breaker was HOT and the wall was WET. Trust me, I was there.
Not questioning your ability John but the way your post came across especially to someone not using the camera made it sound like some miracle tool. No by no means was I there but anytime is see glass as in your Pic makes me automatically cautious.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 11/2/07, 8:01 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
Originally Posted by cbottger
Not questioning your ability John but the way your post came across especially to someone not using the camera made it sound like some miracle tool. No by no means was I there but anytime is see glass as in your Pic makes me automatically cautious.
The dark areas around the mirror is the moisture problem.
I never intended to worry about the mirror.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #13  
Old 11/2/07, 8:31 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
Originally Posted by jmckenna1
The dark areas around the mirror is the moisture problem.
I never intended to worry about the mirror.
Your E setting is not displayed in your pic as Linus is do you remember what the setting was. Just curious



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #14  
Old 11/2/07, 8:48 PM
John McKenna's Avatar
John McKenna John McKenna is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Crockett, Tx
Posts: 12,303
Default Re: Hot Breaker & Moisture Seen With IR

Quote:
Originally Posted by cbottger
Your E setting is not displayed in your pic as Linus is do you remember what the setting was. Just curious
The E setting will not affect the image on the display.
Once you find the anomaly in the image then you verify it with
a moisture meter. The E setting of no value in finding and then
verifying a moisture area.

After you try and set your E settings, I can be through the rest
of the house finding more problem areas.



John McKenna, CMI (TREC #4565)
Executive Director - Master Inspector Certification Board
25 Yrs Constr Exp - 13 Yrs Home Inspector Exp
American Home Inspection - East Texas.

Reply With Quote
  #15  
Old 11/2/07, 9:22 PM
ldapkus ldapkus is offline
Active Poster
 
Join Date: Mar 2006
Posts: 5,717
Please Note: ldapkus is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Hot Breaker & Moisture Seen With IR

Here are some papers on emissivity:
http://www.callpie.com/documents/sea...ramation06.pdf
http://www.flirthermography.com/medi...holm_FINAL.pdf
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
IAC2 In new residential construction mcyr IAC2 Indoor Air Forum 0 10/9/07 6:45 PM
Moisture in slabs mcyr Structural Inspections 7 8/20/07 7:33 PM
bbbb mcyr Structural Inspections 1 8/19/07 10:26 PM
Moisture control for slab on grade in protecting floor finishes mcyr General Inspection Discussion 2 8/13/07 7:53 PM