Default No Main Disconnect

This is a panel in a condo in Chicago. There is no main shut off, there are no other panels in the condo. What do you guys think? I am thinking that the main shutoff is in the electrical closet in the outside hallway, which I did not have access to because there was no staff authorized to allow me access.

Also, the circled area, seems to be the ground wire. Shouldn't that be connected to the neutral bus? Is this a way of bonding?
Attached Thumbnails
no-main-disconnect-p6240111.jpg   no-main-disconnect-p6240114.jpg  



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America)
  #2  
Old 6/25/09, 7:24 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: No Main Disconnect

Michael,

This is a typical (LSE) sub panel. The main SE breaker (shut-off) is located in a mechanical room at the main floor or basement of the building.

Simply note "No access to Main SE panel".

Where are the ground wires?
Reply With Quote
  #3  
Old 6/25/09, 7:30 AM
Joseph T. Burkeson, CMI's Avatar
Joseph T. Burkeson, CMI Joseph T. Burkeson, CMI is offline
InterNACHI Member
 
Join Date: May 2003
Location: Riverview, FL
Posts: 8,399
Default Re: No Main Disconnect

Quote:
Originally Posted by dvalley View Post
Where are the ground wires?
Wired in metal conduit.



"I know of no more encouraging fact than the
unquestioned ability of a man to elevate his
life by conscious endeavor." ~ Henry David Thoreau


Certified Master Inspector (2007)
Member, International Assoc of Certified Home Inspectors (InterNACHI)
Member, International Code Council (ICC) - Certified Residential Combination Inspector
Member, American Society of Home Inspectors (ASHI)
Vice President - Suncoast ASHI

Square-One Inspection "Assurance begins here"

Reply With Quote
  #4  
Old 6/25/09, 7:32 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 7,926
Default Re: No Main Disconnect

Quote:
Originally Posted by jburkeson1 View Post
Wired in metal conduit.
Where do you see BX?
Reply With Quote
  #5  
Old 6/25/09, 9:30 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,592
Default Re: No Main Disconnect

EMT serves as ground



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #6  
Old 6/25/09, 9:35 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Main Disconnect

Never assume Mike ,but I am going to stick out my neck and say your main panel is in the meter room.

I do not know the layout ,but remember to always follow the mast and try to get in to the locked room where it enters the buiding if not in a hall closet.

Small buildings it will be ground floor.

Mike the conduit serves as ground and the green wire is most likely for a spa tub.(guess)Reason is you have gas powered appliances.

How do I know? (only one double) (for HVAC)

Ground wire and the box should be connected but separate from the neutral bar.(look for a green screw or small bracket which bonds the box to the neutral bars which would be incorrect)

I see no problem from the picture.(If this is a new Condo please do call out lack of AFCI for the bedroom)





Will show you the flat head screwdriver trick (just kidding).

Last edited by relliott; 6/25/09 at 9:41 AM..
Reply With Quote
  #7  
Old 6/25/09, 2:24 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 609
Default Re: No Main Disconnect

As stated in my first post, there is an electrical room about 2 doors down from the unit. No one at the building could give me access. I did not see the bond screw, I thought that the circled item in the pic was a type of bonding. I read on the board that sometimes the screws that are used to install the bus bars act as the bond.

No spa tub or whirlpool.

This is an older building, I think it is the Millenium Building. It seems to me that the unit owner should have a way to shut off all electric to the unit.

I did tell the client about AFCI, and since he is going to have an electrician fix some receptacles, I suggested that he ask the electrician about installing AFCI.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #8  
Old 6/25/09, 2:27 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,525
Default Re: No Main Disconnect

Quote:
Originally Posted by mmerino View Post
This is an older building, I think it is the Millenium Building. It seems to me that the unit owner should have a way to shut off all electric to the unit.
I think the idea is that, in an emergency, the power can be shut off to multiple units much quicker than going unit by unit, seeing if people are home.

And they do - they should have access to the electrical room.

Not much different than having the main breaker at the meter.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #9  
Old 6/25/09, 2:39 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 609
Default Re: No Main Disconnect

I am an idiot! Don't everyone agree to quick.

#1 rule-NO bonding in a sub-panel!! No wonder I didn't see it.



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #10  
Old 6/25/09, 2:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 4,961
Default Re: No Main Disconnect

Quote:
Originally Posted by mmerino View Post
I am an idiot! Don't everyone agree to quick.

#1 rule-NO bonding in a sub-panel!! No wonder I didn't see it.
Brush up a little on the definition of bonding. It causes more greif for inspectors than you may know.

There are components of the electrical system that are "bonded" at load-side equipment (i.e. sub panels), such as EGC's, metal conduit, etc. The rule is - no bonding of the neutrals to the panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 6/25/09, 11:30 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 1,208
Default Re: No Main Disconnect

I challenge you
http://www.nachi.org/electrical-pane...-challenge.htm




BEN GROMICKO
Director of InterNACHI Online Education
President of NACHI.TV - Online Training Videos
President of Mountain Warranty Corporation
ben@nachi.tv
(303)862-2611 ben@mountainwarranty.com

IMPROVE YOUR REPORT

Reply With Quote
  #12  
Old 6/26/09, 11:05 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 809
Send a message via Skype™ to pbolliger
Default Re: No Main Disconnect

Mike

The panel has one MAJOR defect.. NO legend!! I am surprised no one pointed that out.. No professional would leave that puppy unlabeled for branch circuit layout .

As for the "main" in this "distribution panel" your going to see the various configurations /types all over the place in Chicago. This is not uncommon but personally I would prefer to see one (main). Call it out... but be prepare to get ripped into. I have seen many and even had Union contractors slam me for it. It follows two different paths of concern. One occupant safety, the other electrical equipment protection. Guess which one this falls under? Your looking at client safety.. "them guys who installed it say you da wrong pal".. AFCI ain't required... We don't installed thems....

As for the closet down the hall. Very common also. Does the building have an engineer on site. Then they are the person responsible for access. Is the building a mega high rise or a three unit condo. Different configuration?

At the next chapter meeting I will have a challenge for you on Chicago electrical installations..
Reply With Quote
  #13  
Old 6/26/09, 11:16 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: No Main Disconnect

Quote:
Originally Posted by pbolliger View Post
The panel has one MAJOR defect.. NO legend!! I am surprised no one pointed that out.. No professional would leave that puppy unlabeled for branch circuit layout .
The "legend" is above the preprinted label on the panel door.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Find an InterNACHI certified North Dakota Home Inspector (and anywhere else in North America)
  #14  
Old 6/26/09, 11:23 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 809
Send a message via Skype™ to pbolliger
Default Re: No Main Disconnect

OOPS

Focus paralysis!!
Reply With Quote
  #15  
Old 6/26/09, 11:28 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,301
Default Re: No Main Disconnect

Patrick, I know you would have seen if if you had been there.

Inspecting from pictures sucks.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main disconnect at meter instead of main panel. OK? kshepard Electrical 14 11/8/06 7:24 PM
Tenant access to main disconnect in apartment bldg? lhoffman Electrical 4 9/1/06 12:54 PM
Disconnect and Main panel srowe Electrical 10 6/13/06 8:49 PM
Main Disconnect Manufactured Home dbreen Electrical 1 3/4/06 1:42 PM


All times are GMT -4. The time now is 9:38 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts