Default Re: No Main Disconnect

Ben - do you use this same logic when making the videos that you sell to Home Inspectors?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #122  
Old 7/3/09, 12:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: No Main Disconnect

Quote:
Originally Posted by bgromicko View Post
I disagree.I shall inspect with total disregard to my client's concerns/needs? No.

Client: "I have a little trouble getting into the bathtub. Do you think I could install a hand hold bar on the tile wall here?"
Inspector: "Absurd. Why are you asking me? You need to consult a medical doctor! I'm an inspector - not a doctor! Now... stop interrupting me while I inspect only those things that are specifically listed in the SOP. You're concerns about safety are of no concern to me, unless they are written in the SOP."

hee hee.
You're beating a dead horse Ben while twisting what I say and intend. Please knock that crap off.

Of course I will respond to specific client requests but that doesn't mean they belong in the report.

If you insist on putting words in my mouth here are some from yours:

I'm Ben Gromicko and I'm the best damn inspector ever. Just ask me.

Code? Those are bare minimums and just don't do the job and were probably written by a bunch on industry shills anyway.

But don't worry I will use my "expertise" in rehabilitaion and geriatric care to make sure I call out all manner of issues that I think you should spend money on to enhance your safety. I know that some of these are prohitively expensive but hey, its not my money.

Afterall, I'm only here to "help" you.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #123  
Old 7/3/09, 12:42 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: No Main Disconnect

Quote:
Originally Posted by jpope View Post
Ben - do you use this same logic when making the videos that you sell to Home Inspectors?
I hope not but I would not be surprised.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #124  
Old 7/3/09, 12:44 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: No Main Disconnect

I've performed many home inspections at condos and townhouses and apartments, where the meters and main disconnects were outside, clumped together around the corner on the side of the building. Inside the panel had no main disconnect, and more than 6 hand movements to shut them all off. To my client, I described what would need to be done to turn off all of the electricity in an emergency. Usually my client would ask, "Why is the main breaker way over there outside and around the corner? Can't I just put one right here next to the panel?"

My clients weren't dumb. I was not preying on their fears or concerns about safety; I have no motive. My point is that inspectors should not totally disregard the expressed concerns and needs of their client - particularly when it comes to safety concerns/needs (whether actual or perceived).

It's been my experience that existing houses that have major problems were once built to code.
Reply With Quote
  #125  
Old 7/3/09, 12:45 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: No Main Disconnect

Quote:
Originally Posted by rmaday View Post
You never got a baseball cleat caught on the shag carpet as a kid then, huh.
Ben always recommends a sign at the front door to warn cleat wearers to remove them before waling into the house for their personal safety.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #126  
Old 7/3/09, 12:46 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: No Main Disconnect

Quote:
Originally Posted by pabernathy View Post
Define the safety concern over the Main Disconnect Switch. I can see falling in the tub, down stairs and carbon monoxides and most of all AFCI's....but those are in many cases a minimum code mandate....I dont see the exception as posted increasing a safety concern unless YOU impose you WILL on the client and bring it up as I am sure they wont so while the other items they would bring up as it directly relates to physical safety......an alarmist will bring up things that provide no basis but makes them feel better....two different beasts.

Personally.....90% or higher homes that have a "sub-panel" within the same dwelling do not have a main breaker....never a problem. Also if that concerned you my friend.....I would get your own panel checked first....lol.....( inside joke )
Paul,

You're wasting your time.
Reply With Quote
  #127  
Old 7/3/09, 12:47 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: No Main Disconnect

Quote:
Originally Posted by bgromicko View Post
I've performed many home inspections at condos and townhouses and apartments, where the meters and main disconnects were outside, clumped together around the corner on the side of the building. Inside the panel had no main disconnect, and more than 6 hand movements to shut them all off. To my client, I described what would need to be done to turn off all of the electricity in an emergency. Usually my client would ask, "Why is the main breaker way over there outside and around the corner? Can't I just put one right here next to the panel?"

My clients weren't dumb. I was not preying on their fears or concerns about safety; I have no motive. My point is that inspectors should not totally disregard the expressed concerns and needs of their client - particularly when it comes to safety concerns/needs (whether actual or perceived).

It's been my experience that existing houses that have major problems were once built to code.
Expressed concerns?

You lead him down the garden path Ben.

Did you demonstrated by using a stop watch and timing how long it would take?



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #128  
Old 7/3/09, 12:48 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: No Main Disconnect

Quote:
Originally Posted by dvalley View Post
Paul,

You're wasting your time.
I am too but I just finished a report and I'm feeling frisky.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #129  
Old 7/3/09, 12:50 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Main Disconnect

Quote:
Originally Posted by bgromicko View Post
To my client, I described what would need to be done to turn off all of the electricity in an emergency.

What kind of emergency would your client be better suited to remain in the house and turn off the breaker rather than simply leave the premisis?


Usually my client would ask, "Why is the main breaker way over there outside and around the corner?

And what was your answer?

Can't I just put one right here next to the panel?"

My clients weren't dumb. I was not preying on their fears or concerns about safety; I have no motive. My point is that inspectors should not totally disregard the expressed concerns and needs of their client - particularly when it comes to safety concerns/needs (whether actual or perceived).
So if you were the alarm tech, you would have installed the sensors on my mothers upper windows?
Reply With Quote
  #130  
Old 7/3/09, 12:51 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Main Disconnect

Quote:
Originally Posted by dvalley View Post
Paul,

You're wasting your time.
Not necessarily.

While I doubt Ben will change his mind, there may be some reading this that can benefit from the discussion.
Reply With Quote
  #131  
Old 7/3/09, 12:52 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,143
Default Re: No Main Disconnect

Quote:
Originally Posted by mlarson View Post
I'm Ben Gromicko and I'm the best damn inspector ever. Just ask me.

Code? Those are bare minimums and just don't do the job and were probably written by a bunch on industry shills anyway.
Oh, I was one of the worst inspectors out there. I was terrible for many years. Did not know a thing. I still am not as good as I want to be, that's why I work so hard trying to learn and understand and help. I'd say Pope is the best knowlegable inspector out there (from what I hear). Decker is excellent, seen him in action, you'll never want him to leave. Krumm is very good and talking and walking and doing an thorough job. Me.... I'm low on the list.

On the contrary, I have a ton of respect for those who write codes. Canadian building codes are fantastically written. I read them often. Alberta Building Codes Vol 1 and 2. Written very concisely. Easy to understand.

But codes change and improve. Why do they change and improve? Because at a certain point in time, a group of well-respected individuals said that they were inadequate in some way and not safe enough.
Reply With Quote
  #132  
Old 7/3/09, 12:53 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: No Main Disconnect

Quote:
Originally Posted by bgromicko View Post
I've performed many home inspections at condos and townhouses and apartments, where the meters and main disconnects were outside, clumped together around the corner on the side of the building. Inside the panel had no main disconnect, and more than 6 hand movements to shut them all off. To my client, I described what would need to be done to turn off all of the electricity in an emergency. Usually my client would ask, "Why is the main breaker way over there outside and around the corner? Can't I just put one right here next to the panel?"

My clients weren't dumb. I was not preying on their fears or concerns about safety; I have no motive. My point is that inspectors should not totally disregard the expressed concerns and needs of their client - particularly when it comes to safety concerns/needs (whether actual or perceived).

It's been my experience that existing houses that have major problems were once built to code.
But as MANY do....you have to compare "Apples to Apples and Oranges to Oranges" without a blanket statement. We have to evolve with each inspection or we are destine to die by them. In the case of the original post, I would demands to have access to the area where the service disconnect is located to complete my report.....but THAT situation is not the same as you paint in the quote above....two different senerios and a good inspector has to learn to roll with each one and not be hog tied into a blanket statement. This is why knowing the code forms a basis for understand beyond our personal feelings. Again, many older people do not even have the strength to turn off a main breaker so that rules older folks out plus the protection is for Overcurrent protection which is overload, short circuit and ground fault protection to kinda round it out and a breaker ahead of it serves the intent.......lets look at it another way...

I have a service disconnect in my garage....and thats all it is a main breaker and it feeds a "remote" panel in the dwelling...no main breaker as is probably the standard all around the country. Is that a concern? I hope not because the idea of turning off the main breaker is not a likely event in most cases as electrocution is not the concern right....you are not that fast my friend....lol.....we rely on branch circuits and GFCI's and so on...

We simply can't group the issues.........but in your example in the post....older systems that do pose a concern are called out with out a doubt but we can't blanket statement the procedure.

Gotta run...good debate.....meeting the wife for lunch..later fella !



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #133  
Old 7/3/09, 12:54 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: No Main Disconnect

Quote:
Originally Posted by rmaday View Post
Not necessarily.

While I doubt Ben will change his mind, there may be some reading this that can benefit from the discussion.
Such as yourself.
Reply With Quote
Find an InterNACHI certified Nevada Home Inspector (and anywhere else in North America)
  #134  
Old 7/3/09, 12:54 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: No Main Disconnect

Quote:
Originally Posted by bgromicko View Post
Oh, I was one of the worst inspectors out there. I was terrible for many years.
Sorry to hear that.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #135  
Old 7/3/09, 12:57 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: No Main Disconnect

Quote:
Originally Posted by bgromicko View Post
My point is that inspectors should not totally disregard the expressed concerns and needs of their client - particularly when it comes to safety concerns/needs (whether actual or perceived).
Client: Mr. Spector, I'm concerned that that skylight in my daughters room is not safe. I am concerned with debris falling from airplanes, sattelites and space, craching through there.

Mr. Spector: I undertsand your concern. I will put it in the report that the skylight is a safety hazard and should be removed.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 7:24 PM
Tenant access to main disconnect in apartment bldg? lhoffman Electrical Inspections 4 9/1/06 12:54 PM
Disconnect and Main panel srowe Electrical Inspections 10 6/13/06 8:49 PM
Main Disconnect Manufactured Home dbreen Electrical Inspections 1 3/4/06 1:42 PM


All times are GMT -4. The time now is 6:51 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts