Was soing an inspection for a friend of mine. He, along with his brother and sisters own a very reputable HVAC company. Condo unit in a gut rehabbed building originally built in 1929. Cosmetics were wonderful.

But, here is the fireplace.

Looks like a regular solid fuel modular unit with a log lighter (which I do not like because too many people wind up loosing their eyebrows lighting them.

The problem?

It was a ventless fireplace!!!

Code inspector (Chicago) was there and totally missed it.

That is why I do not put too much stock in local municipal inspections.
Attached Thumbnails
scary-fireplace-dscf4900.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 5/22/09, 8:11 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Scary fireplace

Are ventless fireplaces permitted in your area?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 5/22/09, 8:22 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Scary fireplace

Quote:
Originally Posted by mlarson View Post
Are ventless fireplaces permitted in your area?
Yes. Special gas log units with oxygen sensor and all that. The way this was configured, it should have had one of those, not a freakin' log lighter. Sometimes, the owners just put a couple of ceramic logs in the fireplace and use the log lighter as the flame. This is also not a good idea.

Just goes to show you what non-professional "builders" will do.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #4  
Old 5/22/09, 8:30 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Scary fireplace

Quote:
Originally Posted by wdecker View Post
Yes. Special gas log units with oxygen sensor and all that. The way this was configured, it should have had one of those, not a freakin' log lighter. Sometimes, the owners just put a couple of ceramic logs in the fireplace and use the log lighter as the flame. This is also not a good idea.

Just goes to show you what non-professional "builders" will do.
So it's not really a ventless fireplace but instead a total hack job.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 5/22/09, 8:44 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Scary fireplace

It is a ventless fireplace (because it has no vent) equipped with a log lighter (which should ony be installed in a solid fuel fireplace, which must have a flue.

The client, the HVAC guy (and his Dad, the 35+ year experienced HVAC guy) could not believe it. They tried to take off the inside top plate, looking for a flue. No chimney or metal vent. Seems like the builder went out and got a modular ventless fireplace, then installed it with a log lighter.

The builder (properly licensed by the city, but formed as an LLC) kept asking (in broken English/Polish) what the problem was. He had no idea what he was doing.

But, more to the point, the city inspector didn't even look at this. He was off looking at the lack of humidifier on the furnace. Never mind that the furnace was a cat 4, with no exhaust air vent, installed in a drain pan that was not properly drained. Just that the furnace had no humidifer (which is not required, but he believed it was).

Go figure.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #6  
Old 5/22/09, 8:47 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Scary fireplace

Ease up Will.

A real ventless fireplace will have an O2 depletion sensor.

And yes the inspector should have found it first.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #7  
Old 5/22/09, 8:54 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Scary fireplace

Quote:
Originally Posted by mlarson View Post
Ease up Will.

A real ventless fireplace will have an O2 depletion sensor.

And yes the inspector should have found it first.
I agree. I am just venting because of all the times I am told by the agents and the builders and even the code inspectors that I am wrong and the city code inspectors are right.

I just write it up, explain it to my clients and hope that they listen.

Funny. The three times that I was sued by my clients (none of which succeded) they were all about issues that the agent and the builder said was OK, but that I defected, but they still tried to sue me.

Remember, in Illinois, local code inspectors are immune from lawsuits and liability.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #8  
Old 5/22/09, 10:13 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Scary fireplace

Quote:
Originally Posted by wdecker View Post
I agree. I am just venting because of all the times I am told by the agents and the builders and even the code inspectors that I am wrong and the city code inspectors are right.

I just write it up, explain it to my clients and hope that they listen.

Funny. The three times that I was sued by my clients (none of which succeded) they were all about issues that the agent and the builder said was OK, but that I defected, but they still tried to sue me.

Remember, in Illinois, local code inspectors are immune from lawsuits and liability.
Yep I remember that that 3 fireplace job Joe had and always check plates very close since.
Also had a nice 2000 build with split block today.
Lots of mortar openings and may be missing weeps and moisture barrier at some spots.
Back to the fire place my client asked if he could use those ceramic logs in the manufactured solid fuel model.
( Had log lighter) and metal venting to roof.
Is that permissible as I do not believe so but need to check into why not?
Reply With Quote
  #9  
Old 5/23/09, 10:00 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Scary fireplace

Quote:
Originally Posted by relliott View Post
Back to the fire place my client asked if he could use those ceramic logs in the manufactured solid fuel model.
( Had log lighter) and metal venting to roof.
Is that permissible as I do not believe so but need to check into why not?
Because the log lighter is meant to light logs, not to provide a flame for the ceramic logs. Log lighters (at least around here) have no safety features, no thermocouple, no oxygeb sensor. Just turn that valve and gas comes out. If they want a gas log unit (which is what they are saying) then they should have a proper one put in. Fairly inexpensive retrofit.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 5/23/09, 10:24 AM
Dennis McAuley's Avatar
Dennis McAuley Dennis McAuley is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hoffman Estates, IL
Posts: 812
Default Re: Scary fireplace

Will, great pun: "I agree. I am just venting because of all the times I am told by the agents and the builders and even the code inspectors that I am wrong and the city code inspectors are right."

Good information for all!

Thanks



Priority One Building Inspection Services d/b/a Home Check America

Office: 866-245-4663
Cell: 815-715-6237
Full member InterNACHI: 06010792
IL license: 450.003154
Reply With Quote
  #11  
Old 5/23/09, 1:25 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Scary fireplace

Quote:
Originally Posted by wdecker View Post
Because the log lighter is meant to light logs, not to provide a flame for the ceramic logs. Log lighters (at least around here) have no safety features, no thermocouple, no oxygeb sensor. Just turn that valve and gas comes out. If they want a gas log unit (which is what they are saying) then they should have a proper one put in. Fairly inexpensive retrofit.

Hope this helps;
So the fact it is vented does not decrease the fact it is dangerous to leave lit longer than the short period of time it is used to light a organic log.
I will make the suggestion of looking into a conversion kit.
Reply With Quote
  #12  
Old 5/24/09, 11:25 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: Scary fireplace

Correct, Bob. You have to look at what the fireplace is designed to do. In this case, it is obvious that a log lighter is not meant to burn ceramic logs. Nor is that the case with a vented fireplace, which is designed to burn wood. Sure, there woukld be little safety hazard (maybe the heat would not be enough for a good draft) but a log lighter is designed to light logs.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hearth size??? jcampbell HVAC 32 6/1/08 2:56 PM
The Rumford Fireplace: Safety vs. Efficiency mbryan Interior 2 4/28/08 5:38 PM
Difficult Chimneys thance HVAC 2 1/29/08 9:16 PM


All times are GMT -4. The time now is 9:33 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts