Gas furnice in upstairs encolsed area-fresh air vents go from enclosed area into attic area. Is this OK or should it vent to outside?
Thanks, I need this info ASAP
Reply With Quote
  #2  
Old 2/3/08, 12:14 AM
James Budrow's Avatar
James Budrow James Budrow is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Sacramento, CA
Posts: 26
Default Re: Vent Question

Yes thats ok.



James Budrow
American Pride Home Inspection Service
5714 Folsom Blvd Suite 106
Sacramento CA 95819
1-877-IB4-UBuy(877-424-8289)
http://www.InspectSacto.com
http://www.APInspectionService.com
http://www.SacramentoInspection.com
President-Sacramento Valley Chapter (InterNACHI)
Reply With Quote
  #3  
Old 2/3/08, 6:36 AM
Robert Sole's Avatar
Robert Sole Robert Sole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 360
Default Re: Vent Question

It's OK as long as the attic has proper ventilation. It would have to be changed if the attic were insulated and the vents sealed as they are starting to do in some homes now.



Robert Sole, CMI



407-637-7288


Florida license numbers HI 169 and MRSA 92

Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

Check out my blog orlandohomeinspections.info/
REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #4  
Old 2/3/08, 6:57 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Vent Question

Combustion air...?



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 2/3/08, 6:59 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: Vent Question

Quote:
Originally Posted by rkeith
Gas furnice in upstairs encolsed area-fresh air vents go from enclosed area into attic area. Is this OK or should it vent to outside?
Thanks, I need this info ASAP
What kind/size of enclosed area and how many floors between it and the attic?

This all depends on the size of installed unit, vent sizing, their location should be 2 hi/lo, what other gas appliances are in the proximety...there are supposed to be a manual/instructions present for all gas fired appliances...if they aren't onsite I note as a deficiency and take down as much info (model/serial) about the unit and check it out back at the office...before sending report to client

probably not ASAP as you wanted but more info will be required before answered without this and photos



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #6  
Old 2/3/08, 7:13 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,466
Default Re: Vent Question

Quote:
Originally Posted by lkage
Combustion air...?
The furnace we recently installed in my house enclosed area needed 1 sq. inch of combustion air (split high and low) per 4000 btu input of all gas appliances in that enclosed area if run in vertically. And double that if run in horizontally. We came direct from outside.

Edited:

I checked for my Rheem and the exact wording is:

"Each opening shall communicate directly, or by ducts, to the outdoors or spaces (crawl or attic) that communicate with the outdoors."



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 2/3/08 at 7:23 AM..
Reply With Quote
  #7  
Old 2/3/08, 7:19 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Vent Question

Quote:
Originally Posted by rkeith
Gas furnice in upstairs encolsed area-fresh air vents go from enclosed area into attic area. Is this OK or should it vent to outside?
Thanks, I need this info ASAP
As stated already, the attic is fine for combustion air as long as it's vented properly. Gable end vents are not considered adequate with todays tighter homes.

A properly vented attic is basically....outside.
Reply With Quote
  #8  
Old 2/3/08, 12:26 PM
rkeith rkeith is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: St Augustine, FL
Posts: 44
Default Re: Vent Question

THANKS EVERYONE! It is worth the membership dues to have access to this knowledge base.
Rusty
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 10:17 AM
Has anyone seen this type of vent material? scosta Inspecting HVAC Systems 12 3/9/07 3:30 PM
Bathroon vent bemelander Inspecting HVAC Systems 8 2/3/06 3:40 AM


All times are GMT -4. The time now is 7:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts