Default 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

http://www.nachi.org/gallery/exterio...-device-3d.jpg

and for more info: www.nachi.org/deck-inspections.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Find an InterNACHI certified Mississippi Home Inspector (and anywhere else in North America)
  #2  
Old 7/21/09, 7:02 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,794
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

Nick,it is my understanding that this would apply for Jurisdictions that have adopted the 2006 IRC.
For those that like to follow up on the Codes that Nick is presenting, it can be found here in PDF format.

http://www.iccsafe.org/cs/codes/2007...ent/IRC07S.pdf Page 35-36

Hope this helps

Thanks Nick.
Reply With Quote
  #3  
Old 7/21/09, 10:38 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

I see some unanswered questions with this change: What about when the joists run parallel to the ledger?... is the bracket installed using blocking? When the joists run perpendicular to the ledger do the deck joists and house joists have to be lined up and have to match O.C. spacing? What about truss joists?... you can't attach a new load to them, even if you could figure a way to do it. When installing a deck to a home with a finished basement the contractor now has to open the ceiling, no? The contractor now has to lift carpeting to install more nails in the home's subfloor? Wow.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #4  
Old 7/22/09, 12:38 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

This is why some jurisdictions adopt portions of the code and reject other portions.
Reply With Quote
  #5  
Old 7/22/09, 2:57 PM
Richard A. Hetzel Richard A. Hetzel is offline
Unmoderated Guest
 
Join Date: Apr 2007
Location: Tobyhanna, Pennsylvania
Posts: 598
Please Note: Richard A. Hetzel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

Why would there be joists running parallel to the ledger?
Reply With Quote
  #6  
Old 7/22/09, 4:09 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

One reason is when you have a tiered deck with but 1 step between tiers. For architectural effect they often like to switch the decking from tier to tier.

Checkerboard decking also has 1/2 the joists running parallel to the ledger.

And the other reason they do this is for safety so that it is easy for the eye to see the steps. This quote from "Building a Deck" by Scott Schuttner: "A change of direction in the decking can visually alert users to steps or other impediments."



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #7  
Old 7/23/09, 3:20 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

As far as the joists running parallel to the ledger, I'd have to see it on some plans. My experience here would have been where joist direction was not perpendicular to ledger, the load path (post/beam) would be designed to accommodate this. Blocking couldn't be used to bear weight where the joist direction changes.

In theory, as most of our decks / balconies are engineered here, I can imagine the plans would call out to simply install additional blocking to accomodate the mention of checkerboarding the decking material. ie blocking every 16/24" oc in the joist bay depending on manu. specs for their decking materials. Many of the trex and similar products would be fine with 16" oc. Other concerns could be raised by this application as well, such as the blocking bearing the weight of live/traffic load and decking.

Interesting find though. I've used simpson straps up and over plating and to studs from decks and covers, that design looks alot like the Strong Wall and Hardi Wall seismic/shear wall panels.

Tim



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770









Last edited by tspargo; 7/23/09 at 3:23 AM..
Reply With Quote
  #8  
Old 7/23/09, 8:57 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

Forgive me if this sounds like a stupid question, but what is the purpose of these tensioners in the first place? I've yet to see one installed, and from the images they don't appear to do anything that lag bolts and proper hangers wouldn't already do. What am I missing?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #9  
Old 7/23/09, 10:44 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

Unlike lag bolts, the hold-down devices attach to the home's floor joists (which is why subflooring nailing is required), not just the home's band joist.

And unlike lag bolts, the hold-down devices attach to the deck's joists, not just the ledger board.

It's a joist-to-joist connector.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #10  
Old 7/23/09, 10:48 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

I can see these things being of some benefit when there is an outer cantilever. The joist hangers at the ledger board are upside-down on a deck with an outer cantilever because the joists are lifting up instead of applying a load down.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 7/23/09 at 10:53 AM..
Reply With Quote
  #11  
Old 7/23/09, 12:44 PM
Patrick Carter's Avatar
Patrick Carter Patrick Carter is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Kansas City Area
Posts: 456
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

Quote:
Originally Posted by mcyr View Post
Nick,it is my understanding that this would apply for Jurisdictions that have adopted the 2006 IRC.
For those that like to follow up on the Codes that Nick is presenting, it can be found here in PDF format.

http://www.iccsafe.org/cs/codes/2007...ent/IRC07S.pdf Page 35-36

Hope this helps

Thanks Nick.
Marcel, thanks for posting the IRC 2007 PDf
Reply With Quote
  #12  
Old 7/23/09, 3:46 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

Reading sections 502.2.2.1.1, 502.2.2.2.2 & 502.2.2.2.3 indicates the tension hold downs are only required when you cannot attach a ledger board by standard methods using specified lags or bolts.




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
  #13  
Old 7/23/09, 10:26 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: 2007 IRC Supplement requires 2 hold-down tension devices per deck now.

Thanks John. Can you post what you see that indicates that to you please?



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Web Site of the Year Award 2007 mcyr General Inspection Discussion 9 10/30/07 7:17 PM
What happened to the daily... klott Miscellaneous Discussion for Inspectors 25 5/21/07 11:44 AM


All times are GMT -4. The time now is 6:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts