Default 600 AMP Service. Use CAUTION!

I inspected this home last week with a 600 Amp, single phase incoming service! This could fry you, and your entire high school class-No Romex here! Down stream there were (5) 200 & 100amp panels. There was also a whole-house generator(YES-WHOLE HOUSE).

If you look at the 600amp panel, it makes the 200 amp panel to the left look tiny.

Notice on the exterior shot the bottom access panel has no pad-lock. Anyone can open this panel door making incoming service line completely exposed. Use extreme caution, and if ever unsure how to handle a situation like this...make a phone call- don't guess!
Attached Thumbnails
600-amp-service-use-caution-600amp-service.jpg   600-amp-service-use-caution-picture-014.jpg   600-amp-service-use-caution-picture-071.jpg  



Dan Musielski
Engineer/Inspector
IL Lic # 450.0002229
Assured Home Inspections
"The NEW Standard in Inspecting"

Batavia, IL 60510
Phone 630.745.0573
www.InspectThatHouse.com


See us in the Fox News Channel!
FOX NEWS Shattered Dreams
http://www.foxnews.com/us/2010/10/13/foreclosure-mess-thickens-experts-fear/
Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/25/11, 11:35 PM
clambert2 clambert2 is offline
Active Poster
 
Join Date: Jan 2011
Location: Southern California
Posts: 343
Please Note: clambert2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: 600 AMP Service. Use CAUTION!

On most panels like that one MUST shut the power off (big handle) before one can open the panel to expose service cables
Reply With Quote
  #3  
Old 11/26/11, 12:50 AM
Dan Musielski's Avatar
Dan Musielski Dan Musielski is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Batavia-Fox Valley, IL
Posts: 55
Default Re: 600 AMP Service. Use CAUTION!

True Charles,

However, not on this systems. Actually this had two location where service lines were accessible; the bottom access door at the exterior and an additional access in the garage where service lines tied into the whole-house system.
Attached Thumbnails
600-amp-service-use-caution-picture-046.jpg   600-amp-service-use-caution-picture-079.jpg  



Dan Musielski
Engineer/Inspector
IL Lic # 450.0002229
Assured Home Inspections
"The NEW Standard in Inspecting"

Batavia, IL 60510
Phone 630.745.0573
www.InspectThatHouse.com


See us in the Fox News Channel!
FOX NEWS Shattered Dreams
http://www.foxnews.com/us/2010/10/13/foreclosure-mess-thickens-experts-fear/
Reply With Quote
  #4  
Old 11/26/11, 12:52 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: 600 AMP Service. Use CAUTION!

What are you guys going to do when you get into high voltage?!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 11/26/11, 12:57 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 600 AMP Service. Use CAUTION!

60 amp or 600 amp they all Can kill .

If you are unsure then stay away and get an electrician .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #6  
Old 11/26/11, 1:34 AM
Dan Musielski's Avatar
Dan Musielski Dan Musielski is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Batavia-Fox Valley, IL
Posts: 55
Default Re: 600 AMP Service. Use CAUTION!

But it's the amps that kill you..and it only has to be 1 amp! 20,000 volts can leave you with a little more than a zap without adequate current.

Think of it this way...take a metal vessel (lets say 1 liter in volume), and pressurize it with 500 PSI of air ...you have a bomb which you don't want to be near! Now pressurize the same vessel to 3000 PSI with hydraulic fluid. Relieve a few drops of fluid out of the system, and pressure quickly goes to 0.



Dan Musielski
Engineer/Inspector
IL Lic # 450.0002229
Assured Home Inspections
"The NEW Standard in Inspecting"

Batavia, IL 60510
Phone 630.745.0573
www.InspectThatHouse.com


See us in the Fox News Channel!
FOX NEWS Shattered Dreams
http://www.foxnews.com/us/2010/10/13/foreclosure-mess-thickens-experts-fear/
Reply With Quote
  #7  
Old 11/26/11, 1:36 AM
Dan Musielski's Avatar
Dan Musielski Dan Musielski is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Batavia-Fox Valley, IL
Posts: 55
Default Re: 600 AMP Service. Use CAUTION!

You're absolutely correct Roy!



Dan Musielski
Engineer/Inspector
IL Lic # 450.0002229
Assured Home Inspections
"The NEW Standard in Inspecting"

Batavia, IL 60510
Phone 630.745.0573
www.InspectThatHouse.com


See us in the Fox News Channel!
FOX NEWS Shattered Dreams
http://www.foxnews.com/us/2010/10/13/foreclosure-mess-thickens-experts-fear/
Reply With Quote
  #8  
Old 11/26/11, 2:02 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: 600 AMP Service. Use CAUTION!

So can a screwed up wiring system that we don't want to have checked.

Home Inspectors want everyone to have there houses inspected but won't hire a Pro when they can't explain an obviously screwed up electrical system.

Just come to NACHI and we will tell you whats wrong from here,,,

The hot ground did not go away by replacing a breaker.

If anyone should know better...



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #9  
Old 11/26/11, 4:24 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 600 AMP Service. Use CAUTION!

I find it sad to see some who know so little giving advice to others who know even less .
I try to not give advice to those do not have enough knowledge to absorb what is said..... Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #10  
Old 11/26/11, 5:41 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is offline
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,054
Default Re: 600 AMP Service. Use CAUTION!

Quote:
Originally Posted by rcooke View Post
I find it sad to see some who know so little giving advice to others who know even less .
I try to not give advice to those that do not have enough knowledge to "absorb" what is said..... Roy
That was an elegant remark that more should practice.
The value of personal and public safety is understated by many.
When in doubt "leave it alone" and recommend a professional.
Note it under recommendations and limitations in the report.
RECOMMEND: Licensed electrician evaluate the electrical systems panel.
Do all the branch testing, sockets and switches GFCI,s etc..
LIMITATIONS: High voltage panel. Beyond the scope of --------your company name inspections for a residential building.
JMO.
Honesty is the best policy.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #11  
Old 11/26/11, 10:52 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 600 AMP Service. Use CAUTION!

600 amp services are not uncommon for high-end homes. Even though these larger services will have different equipment associated with them, 600 amp services are no more "dangerous" than 60 amp services. The same caution should be used with either.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 11/26/11, 1:15 PM
Dan Musielski's Avatar
Dan Musielski Dan Musielski is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Batavia-Fox Valley, IL
Posts: 55
Default Re: 600 AMP Service. Use CAUTION!

Yes Jeff... caution needs to be used in 60 or 600 amp. However 600 is more dangerous...just like 60 amp is more dangerous than 20 amp. It's like stepping in front of a moving car, a moving truck, or a train...they all kill you. However, you can't install 60amp services in residential. A wall recepticale will electrocute you.

Just like dealing with "deadly" or "Hot" neturals...you wont typically see this with Romex...but it's "very common" with conduit because of "shared" neutrals on two circuits out of phase...or working with 3-phase 440 or 480V(not typical in residental)...which you better have quality testers for since sparks can "jump" air gaps.

It's not just enough to know how to inspect electrial; but it's best knowing how electrical systems function. I did an inspection after another inspector wrote up a service panel as a SAFTEY HAZZARD when 12 guage wire was used on 15amp breakers...obviously he had no clue what he was looking at.



Dan Musielski
Engineer/Inspector
IL Lic # 450.0002229
Assured Home Inspections
"The NEW Standard in Inspecting"

Batavia, IL 60510
Phone 630.745.0573
www.InspectThatHouse.com


See us in the Fox News Channel!
FOX NEWS Shattered Dreams
http://www.foxnews.com/us/2010/10/13/foreclosure-mess-thickens-experts-fear/

Last edited by dmusielski; 11/26/11 at 1:19 PM..
Reply With Quote
  #13  
Old 11/26/11, 2:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: 600 AMP Service. Use CAUTION!

Quote:
Originally Posted by dmusielski View Post
However 600 is more dangerous...
I don't agree. This is like saying that falling from 500 feet is more deadly than falling from 100 feet.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/26/11, 2:53 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,106
Default Re: 600 AMP Service. Use CAUTION!

Yep! Infact I think 60 Amp systems are the worst because of the the average individual does not understand the danger of Amps thinking there might be less chance to be thrown across a room than 100 Amps which we know is not true.
Plus older system design is not as safe as a new panel with 600 Amps because of the stringent electrical codes involved in the installation of this set up.
It is the lack of knowledge that kills whether it is 600 amps or 6 amps it makes no difference when the heart stops.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #15  
Old 11/26/11, 2:54 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,619
Default Re: 600 AMP Service. Use CAUTION!

Quote:
Originally Posted by dmusielski
However 600 is more dangerous...

Bunk touching with your bare hands ,Your Heart has no idea what the size of the service is less the fraction of an amp kills you .
-----------------------------------------------------------------------------
I don't agree. This is like saying that falling from 500 feet is more deadly than falling from 100 feet.

Right on Jeffery . Many do not know 26 volts can kill .

Please some incorrect information is getting posted .

Do not get complacent with Electricity .If in doubt call it out .

Get in an expert .I let my electrical license drop 10 years ago to help remove me from being an expert .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service size acox Electrical Inspections 6 9/5/09 2:40 PM
Infrared Inspection Service jwarner Thermal Imaging, Infrared Cameras & Energy Audits 25 7/28/09 7:32 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 6:02 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts