This Exhaust is to a gas fireplace. it is underneath a deck. this is a pre-listing inspection. How many things are wrong here?
J.Szczesny 4 Seasons Home Inspections Washington State Inspector # 711 800 5th Ave #101-385 Seattle, Wa 98104 (206)391-0285 online @ www.4seasonsinspects.com email @ info@4seasonsinspects.com toll free cal @ 866-512-9972 "For the best protection, get the right inspection" |
|
#2
|
||||
|
||||
|
One would be the notch in the ledger board.
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#3
|
||||
|
||||
|
its actually not a ledger board,its a left over from a former deck, the newer deck is above it.
J.Szczesny 4 Seasons Home Inspections Washington State Inspector # 711 800 5th Ave #101-385 Seattle, Wa 98104 (206)391-0285 online @ www.4seasonsinspects.com email @ info@4seasonsinspects.com toll free cal @ 866-512-9972 "For the best protection, get the right inspection" |
|
#4
|
|||
|
|||
|
Please Note:
jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Well, I would say that the words "HOT" (stamped on the front of the exhaust) and "WOOD" don't go together unless you're barbecuing.
|
|
#5
|
||||
|
||||
|
Please Note:
rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
||||
|
||||
|
Quote:
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#7
|
||||
|
||||
|
2006 International Residential Code for One and Two Family Dwellings
Part V- Mechanical Chapter 18 Chimneys and Vents Section M 1804 Vents M1804.2.5 Direct vent terminations. Vent terminals for direct-vent appliances shall be installed in accordance with the manufacturer’s installation instructions. M1804.2.6 Mechanical draft systems. Mechanical draft systems shall be installed in accordance with their listing, the manufacturer’s installation instructions and, except for direct vent appliances, the following requirements: 1. The vent terminal shall be located not less than 3 feet (914 mm) above a forced air inlet located within 10 feet (3048 mm). 2. The vent terminal shall be located not less than 4 feet (1219 mm) below, 4 feet (1219 mm) horizontally from, or 1 foot (305 mm) above any door, window or gravity air inlet into a dwelling. 3. The vent termination point shall not be located closer than 3 feet (914 mm) to an interior corner formed by two walls perpendicular to each other. 4. The bottom of the vent terminal shall be located at least 12 inches (305 mm) above finished ground level. 5. The vent termination shall not be mounted directly above or within 3 feet (914 mm) horizontally of an oil tank vent or gas meter. 6. Power exhauster terminations shall be located not less than 10 feet (3048 mm) from lot lines and adjacent buildings. 7. The discharge shall be directed away from the building. |
|
#8
|
||||
|
||||
|
[quote=relliott]
M1804.2.5 Direct vent terminations. Vent terminals for direct-vent appliances shall be installed in accordance with the manufacturer’s installation instructions. M1804.2.6 Mechanical draft systems. Mechanical draft systems shall be installed in accordance with their listing, the manufacturer’s installation instructions and, except for direct vent appliances, the following requirements... [quote] Since that's a direct vent, the listed requirements don't apply. Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
|
#9
|
||||
|
||||
|
Please Note:
cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#10
|
||||
|
||||
|
Quote:
from this PDF... "...as specified in CGA B149 Installations Codes or ANSI Z223.1. Note: Local Codes or Regulations may require different clearances." I'd like to call it, it looks dangerous, but without mfgr's. specs, I don't see how. Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
Last edited by kshepard; 5/18/08 at 4:13 PM.. |
|
#11
|
||||
|
||||
|
I would call it out as a "keep your eyes on". Also try to find manufacturers instructions to see for sure. It might be a good place for the "dawg" to sleep when its cold.....just above the vent on the deck.....uuummm.
|
|
#12
|
||||
|
||||
|
One thing everyone can agree on...it is not good for the deck.
As home inspectors, referring to the manufacturer's instructions is about all we can actually do. Since this was obviously a post-construction addition, is there any chance that the jurisdiction would require a permit for this installation? James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#13
|
||||
|
||||
|
Please Note:
cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#14
|
|||
|
|||
|
Please Note:
jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#15
|
||||
|
||||
|
Quote:
Kenton Shepard, InterNACHI member # 04082383 Certified Master Inspector (CMI) InterNACHI Director of International Development Director of Green Building EXPERT WITNESS SERVICE Conventional and Log homes (303) 717-8940
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| The Rumford Fireplace: Safety vs. Efficiency | mbryan | Interior Inspections | 2 | 4/28/08 4:38 PM |
| Difficult Chimneys | thance | Inspecting HVAC Systems | 2 | 1/29/08 8:16 PM |
| For those in favor of licensing | gbeaumont | Legislation, Licensing & Legal Issues for Inspectors | 70 | 5/21/07 3:09 PM |
| Tidbits from the ASHI Message Board | jbushart | Miscellaneous Discussion for Inspectors | 126 | 4/27/07 11:05 AM |