This Exhaust is to a gas fireplace. it is underneath a deck. this is a pre-listing inspection. How many things are wrong here?
Attached Thumbnails
any-comments-fireplace-exhuast-mcclusky_edited-3.jpg  



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"


Reply With Quote
  #2  
Old 5/15/08, 10:04 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Any comments on this fireplace exhuast

One would be the notch in the ledger board.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 5/15/08, 10:07 PM
James R. Szczesny's Avatar
James R. Szczesny James R. Szczesny is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Seattle,Wa
Posts: 332
Default Re: Any comments on this fireplace exhuast

its actually not a ledger board,its a left over from a former deck, the newer deck is above it.



J.Szczesny
4 Seasons Home Inspections
Washington State Inspector # 711
800 5th Ave #101-385
Seattle, Wa 98104
(206)391-0285

online @ www.4seasonsinspects.com
email @ info@4seasonsinspects.com
toll free cal @ 866-512-9972

"For the best protection,
get the right inspection"


Reply With Quote
  #4  
Old 5/16/08, 4:58 PM
jhugenroth jhugenroth is offline
Active Poster
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any comments on this fireplace exhuast

Well, I would say that the words "HOT" (stamped on the front of the exhaust) and "WOOD" don't go together unless you're barbecuing.
Reply With Quote
  #5  
Old 5/16/08, 5:14 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any comments on this fireplace exhuast

Quote:
Originally Posted by jhugenroth
Well, I would say that the words "HOT" (stamped on the front of the exhaust) and "WOOD" don't go together unless you're barbecuing.
well said!
Reply With Quote
  #6  
Old 5/17/08, 11:40 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Any comments on this fireplace exhuast

Quote:
Originally Posted by jszczesny
This Exhaust is to a gas fireplace. it is underneath a deck. this is a pre-listing inspection. How many things are wrong here?
Unless you could get your hands on the manufacturer's venting specifications or you saw scorching or some other evidence of failure or problem, you could recommend that the client check with the manufacturer to confirm compliance with venting specs, otherwise... you could say it looks kind of scary.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #7  
Old 5/18/08, 1:21 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Any comments on this fireplace exhuast

2006 International Residential Code for One and Two Family Dwellings
Part V- Mechanical
Chapter 18 Chimneys and Vents
Section M 1804 Vents
M1804.2.5 Direct vent terminations.
Vent terminals for direct-vent appliances shall be installed in accordance with the manufacturer’s installation instructions.
M1804.2.6 Mechanical draft systems.
Mechanical draft systems shall be installed in accordance with their listing, the manufacturer’s installation instructions and, except for direct vent appliances, the following requirements:
1. The vent terminal shall be located not less than 3 feet (914 mm) above a forced air inlet located within 10 feet (3048 mm).
2. The vent terminal shall be located not less than 4 feet (1219 mm) below, 4 feet (1219 mm) horizontally from, or 1 foot (305 mm) above any door, window or gravity air inlet into a dwelling.
3. The vent termination point shall not be located closer than 3 feet (914 mm) to an interior corner formed by two walls perpendicular to each other.
4. The bottom of the vent terminal shall be located at least 12 inches (305 mm) above finished ground level.
5. The vent termination shall not be mounted directly above or within 3 feet (914 mm) horizontally of an oil tank vent or gas meter.
6. Power exhauster terminations shall be located not less than 10 feet (3048 mm) from lot lines and adjacent buildings.
7. The discharge shall be directed away from the building.
Reply With Quote
  #8  
Old 5/18/08, 1:43 AM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Any comments on this fireplace exhuast

[quote=relliott]
M1804.2.5 Direct vent terminations.
Vent terminals for direct-vent appliances shall be installed in accordance with the manufacturer’s installation instructions.
M1804.2.6 Mechanical draft systems.
Mechanical draft systems shall be installed in accordance with their listing, the manufacturer’s installation instructions and, except for direct vent appliances, the following requirements... [quote]

Since that's a direct vent, the listed requirements don't apply.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #9  
Old 5/18/08, 3:39 PM
cduphily's Avatar
cduphily cduphily is offline
Active Poster
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,486
Please Note: cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any comments on this fireplace exhuast

Direct Vent Clearances
Reply With Quote
  #10  
Old 5/18/08, 4:10 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Any comments on this fireplace exhuast

Quote:
Originally Posted by cduphily

from this PDF...




"...as specified in CGA B149 Installations Codes or ANSI
Z223.1. Note: Local Codes or Regulations may require
different clearances."

I'd like to call it, it looks dangerous, but without mfgr's. specs, I don't see how.













Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940

Last edited by kshepard; 5/18/08 at 4:13 PM..
Reply With Quote
  #11  
Old 5/18/08, 4:32 PM
Charles L. Harper's Avatar
Charles L. Harper Charles L. Harper is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: McDonough, GA
Posts: 351
Default Re: Any comments on this fireplace exhuast

I would call it out as a "keep your eyes on". Also try to find manufacturers instructions to see for sure. It might be a good place for the "dawg" to sleep when its cold.....just above the vent on the deck.....uuummm.
Reply With Quote
  #12  
Old 5/18/08, 6:34 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Any comments on this fireplace exhuast

One thing everyone can agree on...it is not good for the deck.

As home inspectors, referring to the manufacturer's instructions is about all we can actually do.

Since this was obviously a post-construction addition, is there any chance that the jurisdiction would require a permit for this installation?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #13  
Old 5/18/08, 7:34 PM
cduphily's Avatar
cduphily cduphily is offline
Active Poster
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,486
Please Note: cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any comments on this fireplace exhuast

Quote:
Originally Posted by kshepard
from this PDF...




"...as specified in CGA B149 Installations Codes or ANSI
Z223.1. Note: Local Codes or Regulations may require
different clearances."

I'd like to call it, it looks dangerous, but without mfgr's. specs, I don't see how.


Why not? It's a possible fire hazard regardless of codes. Defer to an HVAC Contractor to sign off on it.
Reply With Quote
  #14  
Old 5/18/08, 9:07 PM
jhugenroth jhugenroth is offline
Active Poster
 
Join Date: May 2004
Location: Fresno, CA
Posts: 1,152
Please Note: jhugenroth is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Any comments on this fireplace exhuast

Quote:
Originally Posted by cduphily
Why not? It's a possible fire hazard regardless of codes. Defer to an HVAC Contractor to sign off on it.
I agree. There are times when common sense takes precedence over all.
Reply With Quote
  #15  
Old 5/18/08, 10:29 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Any comments on this fireplace exhuast

Quote:
Originally Posted by cduphily
Why not? It's a possible fire hazard regardless of codes. Defer to an HVAC Contractor to sign off on it.
I agree... tell 'em you don't know, it looks dangerous and recommend a specialist.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
The Rumford Fireplace: Safety vs. Efficiency mbryan Interior Inspections 2 4/28/08 4:38 PM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM
For those in favor of licensing gbeaumont Legislation, Licensing & Legal Issues for Inspectors 70 5/21/07 3:09 PM
Tidbits from the ASHI Message Board jbushart Miscellaneous Discussion for Inspectors 126 4/27/07 11:05 AM


All times are GMT -4. The time now is 6:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts