Shold these joists have been run through the wall and attached to the interior floor joists.
|
|
#2
|
||||
|
||||
|
How is the ledger board attached?
What is the beam bearing on? "Never underestimate the difficulty of changing false beliefs by facts." |
|
#3
|
||||
|
||||
|
No, but the ledger should be lagged to the sill.
|
|
#4
|
||||
|
||||
|
Need to know the footer,are there lag bolts,any bolts thru the post and ledger board ?
Michael Ivie Ivco Inspection Service Cornelia, Georgia 30531 Home Inspections Georgia Certified Inspections Georgia Home Inspections |
|
#5
|
||||
|
||||
|
Unless I'm missing something, this whole thing looks like an accident waiting to happen.
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#6
|
||||
|
||||
|
Quote:
|
|
#7
|
||||
|
||||
|
I did not see any lag bolts in the ledger. The footers in my opinion are to small, less than 16x16. The beam is only nailed.
|
|
#8
|
||||
|
||||
|
I agree with Mr. Larson. That thing is scary. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Please Note:
ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Last edited by ccurrins; 7/1/08 at 2:23 PM.. |
|
#10
|
||||
|
||||
|
Quote:
"Never underestimate the difficulty of changing false beliefs by facts." |
|
#11
|
||||
|
||||
|
I pointed out as many defects as I could and recommend evaluation by a licensed professional.
Many of these retal cabins in the Smoky Mountains are built the same way. Maybe the hills are too steep for the building inspector to make it up there. |
|
#12
|
||||
|
||||
|
Please Note:
ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#13
|
||||
|
||||
|
As far as the ledger... possibly too small an area to see what they did.
Some areas, albeit small allow doubling of the 2x materials and carriage bolting to the post. That looks like a single piece of 2x material. I have seen even recently, permitted decks with a 2x carriage bolted to both sides of a 6x post.. I can't find anything right about that install shown. The ledger tends to bolted every 16" in a staggered pattern in most areas i've seen. I've also used and seen Simpson Strong Drive Screws (SDS) in a 16" on center pattern with 2 sds screws every 16. There may be a nice sized galvy bolt on just either side of the pic.. Hey, give em credit. They DID use some flashing of some type... Tim |
|
#14
|
||||
|
||||
|
I just noticed the picture of the balcony above the other... I'm gonna puke.
What the heck is the upper deck/balcony bearing on.. the one below it... ouch. I like how the posts are offset from one another and bearing on the single piece of 2x (at least it looks like a single piece of 2x) Some guys take shortcuts when they scab a project in. That deck could/will give more than a scab to SOMEBODY. Tim ps I hereby take away any credit I gave them for the flashing. |
|
#15
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
The railings are real nice, and that's what sold the place!
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Sump Pit/Pump Question | Joey D'Adamo | Plumbing | 4 | 11/26/08 2:04 PM |
| Question for all... | Bob Hopton-Jones | General Inspection Discussion | 9 | 4/6/07 8:43 AM |
| Basement Bathroom Venting Question | Sean M. Jeric | Plumbing | 4 | 3/21/07 12:56 AM |